Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC 2020 230.67 Sure Protection

User: Jgarzon88, Location: Orlando, Florida

Asked on: Tuesday, November 19, 2024 at 8:32 am EST
Answered on: Thursday, March 6, 2025 at 5:22 am EST

Question: Wanting to get some clarity specifically about the exception in this code230.67-(A) All services supplying dwelling units shall be provided with a surge-protective device(B) Location: Be made an integral part of the service equipment or immediately adjacent theretoException- The SPD shall not be required to be required to be located in the service equipment as required in (B) if located at each next level of distribution equipment downstream toward the load.My question is based on a residential home scenario where I have an outdoor meter main combo that feeds an indoor load center. Does the exception allow for the SPD to be installed in the load center?This scenario is based on the bus bar in the meter main combo being used to capacity (AC condenser units, pool equipment, irrigation clock, solar) in which case the SPD has no space.

Yes, in your scenario, the exception to NEC 230.67(B) does allow the SPD to be installed in the indoor load center.Here's why: The Exception's Language

The exception states the SPD doesn't need to be
immediately adjacent to the service equipment if it's located at each subsequent level of distribution equipment downstream toward the load.

Your Scenario

The meter main combo is the service equipment. The indoor load center is the next level of distribution downstream toward the load.

Practical Application

The exception recognizes situations like yours where space within the service equipment is limited. Placing the SPD in the load center accomplishes the purpose of surge protection for the dwelling unit, even if it's not directly at the service.

Key Considerations and Best Practices



Conductor Length

The conductors from the load center to the SPD should be as short as possible. Longer conductors increase inductance, which can diminish the SPD's effectiveness. Keep the wires neat and avoid unnecessary loops.

Wiring Method

Follow the manufacturer's instructions regarding the proper wiring method for the SPD. This usually involves a dedicated breaker and appropriately sized conductors.


SPD Rating

Ensure the SPD you choose is rated for the service voltage and has a sufficient surge current capacity for your location. Consider your geographical location and susceptibility to lightning strikes.

Coordination

If other SPDs are used (e.g., at appliances), ensure coordination between them. A coordinated system is more effective at diverting surge energy.


Documentation

Keep a record of the SPD's installation and specifications.

Manufacturer Instructions

Always follow the SPD manufacturer's instructions for installation and maintenance. These instructions may provide specific requirements or recommendations relevant to your situation.

AHJ's (Authority Having Jurisdiction) Opinion
Remember that ultimately the AHJ has the final say on interpretations of the NEC, so it is best to consult them.In summary, given your described situation with a full meter main and an indoor load center, the exception to 230.67(B) does permit installing the SPD in the indoor load center, provided you adhere to best practices for conductor length, wiring method, SPD rating, and manufacturer's instructions. Flag for review

Previous Question Next Question