Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Feeders in metal trough

User: Grouch1980, Location: New York, NY

Asked on: Tuesday, November 19, 2024 at 10:52 am EST
Answered on: Thursday, March 6, 2025 at 5:23 am EST

Question: Does anything in the NEC prohibit placing multiple feeders serving apartments in a common trough / wireway? Each apartment is fed by a 120/208 volt, single phase, three wire feeder, and it is being discussed to run all of them in a common trough.

The NEC does not explicitly prohibit placing multiple feeders serving apartments in a common trough/wireway, provided certain conditions are met. You're on the right track to consider this carefully. Here's a breakdown of the key considerations and relevant NEC sections

Key Considerations & Relevant NEC Sections:
Ampacity Calculations & Heat Dissipation (314.28(C) & 366.22)

This is probably the
most critical aspect. You need to ensure the wireway/trough is adequately sized to handle the combined ampacity of all the feeders.

The ampacity of the conductors must not exceed the wireway's ampacity.
More importantly, consider: Adjustment Factors (310.15(C) & 310.15(B)(3)(a))

When multiple current-carrying conductors are installed in a raceway or cable tray, the allowable ampacity of each conductor must be reduced according to Table 310.15(C)(1). This derating accounts for the increased heat generated by having so many conductors bundled together. This is crucial for safety and preventing overheating.

Grouping (310.15(B)(3)(a)(2)

The NEC requires that conductors be bundled, stacked, or supported on horizontal runs.


Fill Percentage (366.22)

A wireway must not be filled to more than 75% of its cross-sectional area.

Proper Sizing

The trough/wireway must be sized to handle the physical volume of all the conductors, splices (if any), and maintain the required fill percentage. Remember to factor in the physical size (diameter) of the conductors, including insulation.


Good Engineering Practice

Consider the worst-case scenario where multiple apartments are heavily loaded simultaneously. You might want to factor in a diversity factor, but this should be done carefully and based on sound engineering principles.

Grouping of Conductors (215.12 and 225.30)

NEC addresses the grouping of conductors in relation to identification and disconnecting means. Ensure compliance with conductor marking requirements to clearly identify each feeder circuit. This is especially important for emergency and essential systems.


Physical Protection (366.12)

The wireway/trough must provide adequate physical protection for the conductors.

Suitable for the Environment (366.10)

Ensure the wireway/trough is suitable for the environmental conditions (e.g., wet, damp, corrosive).


Proper Grounding (250)

The wireway/trough must be properly grounded according to Article 250 of the NEC. Bonding is also critical.

Accessibility

Wireways and Troughs MUST be accessible.


Workmanship

The installation must be done in a neat and workmanlike manner (110.12).

Voltage Drop

Ensure that voltage drop is within acceptable limits, especially given the potential length of the feeders.

Specific NEC Sections to Review Closely



Article 310: Conductors for General Wiring
(Especially 310.15 for ampacity calculations). Article 366: Wireways (Covers construction, installation, and use requirements). Article 215: Feeders (General requirements for feeders). Article 225: Outside Branch Circuits and Feeders (If any portion of the feeder is outside). Article 250: Grounding and Bonding Article 314: Junction Boxes, Pull Boxes, and Handhole Enclosures (Especially 314.28(C) for conduit bodies) 110.3(B): Examination, Identification, Installation, and Use of Equipment. Listed or labeled equipment must be installed per its listing instructions.

Why This Requires Careful Planning and Calculation

The main reason to be cautious is heat. Multiple feeders carrying significant current in a confined space (the wireway/trough) will generate a lot of heat. If the wireway and conductors aren't properly sized, the conductors can overheat, potentially leading to insulation damage, fires, and other hazards.

In Conclusion

Running multiple apartment feeders in a common wireway is possible under the NEC, but it requires meticulous calculations and careful adherence to the NEC to ensure safety and compliance. It's highly recommended that a qualified electrical engineer or electrician with experience in this type of installation performs the calculations and design to ensure everything is done correctly.

Recommendation


Consult the local Authority Having Jurisdiction (AHJ)

Discuss your plans with the local electrical inspector before starting the installation. They may have specific requirements or interpretations of the NEC.2.

Perform Thorough Calculations

Accurately calculate the ampacity of the feeders, apply all applicable adjustment and correction factors, and verify that the wireway is sized appropriately.3.

Document Everything

Keep detailed records of your calculations, conductor sizes, wireway specifications, and installation methods for future reference and inspection purposes.4.

Consider Alternatives:
Depending on the number of feeders and the available space, consider if separate conduits/raceways might be a simpler and more cost-effective solution, especially considering the derating factors you would have to apply.By carefully considering these factors and adhering to the NEC, you can ensure a safe and code-compliant installation. Flag for review

Previous Question Next Question