Topic: Type Z purge kit identified for a Class I Div 2 location being supplied with a certified UL 508A panel

User: Matt_from_CA, Location: CA

Asked on: Tuesday, November 19, 2024 at 11:06 am EST
Answered on: Thursday, March 6, 2025 at 5:23 am EST

Question: Say I have a panel coming from a UL508A panel shop and it is certified as UL 508A compliant. But they're also providing a Type Z purge kit pre-installed.Do I need to have the purge kit's final installation field certified?If the AHJ is happy with the purge kit being identified on its own nameplate for Type Z per NFPA 496, and is installed correctly to whatever rigor he may deem necessary (be it visual inspection, asking to confirm the remote alarm, verifying holding pressure), is that equivalent to being suitable/accepted and thus compliant with the law?Does the AHJ have the right to mandate the installation of the purge kit be field certified by an 3rd party inspection service?Code references appreciated. I've heard differing opinions on this.

This is a nuanced question that depends on a few factors and interpretations. Here's a breakdown of the issues, code references, and potential answers

Understanding the Problem
UL 508A Panel

The panel itself is built and certified to UL 508A standards. This covers the general design and safety requirements for industrial control panels.


Type Z Purge Kit

A Type Z purge system (per NFPA 496) is designed to reduce the concentration of flammable gases or vapors within an enclosure to a safe level, allowing the use of non-explosion-proof equipment inside.

Pre-Installed vs. Field Installation

The purge kit is provided
pre-installed in the UL 508A panel. This is important because it affects how the system as a whole is considered.

AHJ (Authority Having Jurisdiction)

The AHJ is the person or body responsible for enforcing electrical codes and safety regulations. Their interpretation and requirements are paramount.

Field Certification

A field certification is an inspection and testing process conducted
after the equipment has been installed in its final location, to verify that it meets applicable codes and standards.

NFPA 496

The standard that governs purge and pressurization systems for electrical enclosures in hazardous locations.

Arguments Against Mandatory Field Certification of the Purge Kit in this Case
1. The Purge Kit is Part of the UL 508A Listed Assembly: If the panel shop integrates the purge kit and lists the entire assembly (panel + purge kit) as a UL 508A panel with a Type Z purge system, the AHJ may be satisfied. This is because UL 508A covers the integration of components. The AHJ might view it like any other component within a listed panel, which wouldn't usually be subject to field certification. UL 508A (Ed. 4) Section 1.1

"These requirements cover industrial control panels intended for general industrial use, operating from a voltage of 1500 V or less." This suggests that UL 508A covers the entire panel, including properly integrated components.2.

Purge Kit Nameplate
: If the purge kit has its
own nameplate indicating compliance with NFPA 496 Type Z requirements, the AHJ may accept this as sufficient, especially if the installation instructions from the purge kit manufacturer have been followed. The AHJ's inspection (visual, testing the alarm, etc.) becomes the verification step. NFPA 496 (2021 Ed.) Section 5.2.1

"Enclosures that are suitable for purging shall be marked to indicate the purge volume of the enclosure in cubic feet (or liters) and the required minimum flow rate and duration for purging the enclosure to provide an atmosphere suitable for the enclosure type and the applicable location." This emphasizes the importance of the nameplate information.

NFPA 70 (NEC) Article 90.7 (Examination of Equipment for Safety)

"...the authority having jurisdiction shall accept labeled or listed equipment or materials. Where no listing or labeling is available, equipment or materials shall be acceptable to the authority having jurisdiction if judged suitable for the particular purpose involved." This provides the AHJ with flexibility to accept equipment even without listing or labeling if they deem it suitable.3.

AHJ's Discretion

The AHJ ultimately has the final say. If they are comfortable with the documentation provided (UL 508A listing, purge kit nameplate, installation records) and their own inspection, they may not require field certification.


NFPA 70 (NEC) Article 90.4 (Enforcement)

"This Code is intended to be suitable for mandatory application by governmental bodies exercising legal jurisdiction over electrical installations..." This reaffirms the AHJ's authority.

Arguments For Mandatory Field Certification
1. AHJ Concerns About Installation

The AHJ may be concerned about the proper installation of the purge kit within the UL 508A panel, even if the panel is listed. They might feel that the panel shop may not have the proper expertise with hazardous location equipment and it might make more sense to have a field certification performed by a qualified 3rd party to assure conformance. They might be concerned that the panel shop didn't properly follow the purge kit manufacturer's instructions or that field wiring changes compromised the integrity of the system.2.

Specific Local Regulations

Some jurisdictions have specific regulations requiring field certification for all equipment used in hazardous locations, regardless of prior listings. These regulations supersede general code requirements.3.

Liability Concerns

The AHJ might require field certification to reduce their own liability in case of an incident.

Code References to Consider
NFPA 70 (National Electrical Code)

While the NEC doesn't
explicitly require field certification in this scenario, it emphasizes the AHJ's role and the requirement for equipment to be suitable.

NFPA 496 (Purged and Pressurized Enclosures for Electrical Equipment)

This standard defines the requirements for Type Z purge systems. Compliance with NFPA 496 is essential.

UL 508A (Standard for Industrial Control Panels)

If the entire assembly (panel + purge kit) is UL 508A listed
as a unit with a purge system, it strengthens the argument against mandatory field certification.

Jurisdictional Regulations

Always check local and state regulations, as they may have specific requirements.

Answering Your Specific Questions
"Do I need to have the purge kit's final installation field certified?" Not necessarily. It depends on the factors outlined above. If the panel is UL 508A listed with the purge kit, the purge kit itself has a nameplate, and the AHJ is satisfied with the documentation and their inspection, field certification may not be required. However, if the AHJ is concerned about the installation or local regulations require it, then field certification is likely necessary. "If the AHJ is happy with the purge kit being identified on its own nameplate for Type Z per NFPA 496, and is installed correctly to whatever rigor he may deem necessary (be it visual inspection, asking to confirm the remote alarm, verifying holding pressure), is that equivalent to being suitable/accepted and thus compliant with the law?" Yes, potentially. If the AHJ is comfortable with their inspection and the documentation provided, that can be considered "suitable" and thus compliant. This is because NFPA 70 Article 90.7 gives the AHJ the authority to accept equipment they deem suitable. "Does the AHJ have the right to mandate the installation of the purge kit be field certified by an 3rd party inspection service?" Yes, absolutely. The AHJ has the authority to enforce the code as they interpret it, and if they believe field certification is necessary to ensure safety and compliance, they can mandate it. This is especially true in hazardous locations.

Recommendations1. Communicate with the AHJ Early

The best approach is to discuss the situation with the AHJ
before* installation. Present the UL 508A listing (if it covers the purge kit integration), the purge kit nameplate, and the panel shop's qualifications. Ask if they will accept this approach or if they require field certification.2.

Provide Detailed Documentation

Be prepared to provide the AHJ with detailed documentation, including the UL 508A report, the purge kit manufacturer's installation instructions, and any test reports from the panel shop.3.

Consider a Pre-Installation Meeting

A pre-installation meeting with the AHJ and the panel shop can help clarify expectations and address any concerns.4.

Budget for Field Certification

If there's any doubt, it's best to budget for field certification to avoid delays and potential non-compliance issues.

In summary, there's no definitive "yes" or "no" answer. It boils down to the specific circumstances, the AHJ's interpretation of the codes, and local regulations. Proactive communication with the AHJ is crucial.