Topic: How to make sure 230.72(C) is code compliant for tenant

User: electricalintern, Location: PA

Asked on: Tuesday, November 19, 2024 at 1:29 pm EST
Answered on: Thursday, March 6, 2025 at 5:24 am EST

Question: The electrical room houses a main service disconnect serving 10 tenants—5 on the lower level and 5 on the upper floor—along with a separate house panel.My tenant is taking over two tenant spaces:Space A has a 400 AMP, 208V, 3-phase service.Space B has a 200 AMP, 208V, 3-phase service.Both panels in the tenant spaces are MLO (Main Lug Only).The base building engineer prefers not to combine the services into a single 600 AMP, 208V, 3-phase service.Is it acceptable for the panels to remain as MLO?Additionally, the 400 AMP service will supply two subpanels, each rated at 125 AMP.

Let's break down the situation and address each question

1. MLO Panels Acceptance

Yes, it is generally acceptable for the panels to remain as MLO (Main Lug Only) in this scenario, provided they meet code requirements and are properly protected by upstream overcurrent devices. Here's why: Code Compliance (NEC)

The NEC (National Electrical Code) allows for MLO panels when they are properly protected by an overcurrent device (like a breaker or fuses) at their point of supply. This means the upstream disconnect (likely in the electrical room) is providing the overcurrent protection.


Existing Installation

Since the existing installation presumably passed inspections and complies with the code at the time of installation, changing to a main breaker panel isn't necessarily required just because the tenant is expanding.

Engineering Preference

The engineer's preference to avoid combining the services likely stems from factors like:


Cost

Combining services involves new conduit runs, potentially larger conductors, and a more substantial disconnect switch, which is expensive.

Disruption

Combining services usually requires an extended outage to the affected tenant spaces, impacting operations.


Capacity

If the existing main service is near its capacity, adding a 600A service might require upgrading the entire service, which is a very costly and disruptive project.

Important Considerations for MLO Panels



Clear Labeling

Absolutely essential! The MLO panels MUST be clearly and permanently labeled to indicate their source of power (the disconnect switch in the electrical room) and the rating of the overcurrent device protecting them. This labeling is critical for safety and future maintenance.


Accessibility of Overcurrent Device

The disconnect switch/breaker that feeds the MLO panel MUST be readily accessible to the tenant. This allows them to safely shut off power to the panel in case of an emergency.

Proper Wiring & Connections

Ensure all connections within the MLO panel are properly torqued and that conductors are appropriately sized and rated for the load.

2. 400A Service Supplying Two 125A Subpanels


This is generally acceptable, but requires careful consideration:
Load Calculation

The most critical factor is whether the actual load connected to the two 125A subpanels combined will exceed 400A. A proper load calculation is mandatory to ensure the 400A service is sufficient. This calculation must account for all connected loads, their demand factors (i.e., how much power they draw simultaneously), and any future expansion plans.

Overcurrent Protection

Each 125A subpanel
must be protected by a 125A breaker or fuses in the 400A panel. This is non-negotiable. This protects the subpanel and the conductors feeding it.

Conductor Sizing

The conductors feeding each 125A subpanel MUST be sized appropriately to carry the 125A load (after derating for temperature, conduit fill, etc.).

Conduit Sizing

The conduit or raceway between the 400A panel and each 125A subpanel must be properly sized to accommodate the conductors.

Summary of Requirements for Your Situation


Clear Labeling

MLO panels MUST be clearly and permanently labeled with the source of power and the overcurrent protection rating.2.

Accessibility

The tenant must have easy access to the disconnect/breaker feeding the MLO panels.3.

Load Calculation

A thorough load calculation is required to ensure the 400A service can handle the two 125A subpanels.4.

Overcurrent Protection

Each 125A subpanel must be protected by a 125A breaker in the 400A panel.5.

Conductor and Conduit Sizing

All conductors and conduits must be properly sized for the loads and in accordance with the NEC.6.

Inspection

This work will require inspection by the local authority having jurisdiction (AHJ). Be sure to obtain all necessary permits and schedule inspections.7.

Documentation

Keep all load calculations, panel schedules, and other relevant documentation on file for future reference and potential inspections.

Recommendations



Engage a Licensed Electrical Contractor

Hire a qualified and licensed electrical contractor to perform the work and ensure it is done safely and to code.

Review with Base Building Engineer

Have the electrical contractor review the plans with the base building engineer to ensure they are comfortable with the proposed solution.


Obtain AHJ Approval:
Before starting any work, obtain the necessary permits and approvals from the local authority having jurisdiction (AHJ). They will be the final arbiter of code compliance.By addressing these considerations, you can ensure a safe and compliant electrical installation for your tenant. Good luck! Flag for review