Question: Does a large steel reinforced Comercial AC equipment pad have to be bonded to the foundation steel / electrode grounding system? The pad is on the side of a new single story building.
The requirement to bond a large steel-reinforced commercial AC equipment pad to the foundation steel/electrode grounding system is a nuanced issue dependent on several factors, primarily the applicable electrical codes (NEC in the US, CEC in Canada, or local equivalents) and interpretations by the local Authority Having Jurisdiction (AHJ).Here's a breakdown of the considerations and potential interpretations
Arguments for Bonding:
Equipotential Plane
The primary argument is to create an equipotential plane around the AC unit. This means minimizing voltage differences between the AC unit's metal parts, the surrounding earth, and other grounded metal components. This reduces the risk of electric shock if a fault occurs.
Ground Fault Current Path
If the AC unit experiences a ground fault, the pad's steel reinforcement can provide a low-impedance path back to the electrical source, facilitating the operation of overcurrent protection devices (circuit breakers or fuses) and quickly clearing the fault.
NEC 250.50/250.52
While not directly mentioning AC pads, these sections of the NEC (National Electrical Code) discuss grounding electrode systems and supplemental electrodes. A steel-reinforced pad could be argued as a supplemental grounding electrode. If it's considered part of the concrete-encased electrode (aka "ufer ground"), bonding becomes more clearly necessary.
Metallic Parts Likely to Become Energized
The pad is supporting equipment with exposed metal parts that are prone to electrical failure. The pad itself may be considered a large exposed conductive part.
Arguments Against Bonding (or Mitigation)
Isolated Equipment
If the AC unit is specifically designed to be electrically isolated from the pad (e.g., mounted on vibration-dampening, non-conductive pads), the need for bonding might be reduced. However, this is rare for large commercial units.
NEC Ambiguity
The NEC doesn't explicitly address AC equipment pads in detail. This leads to interpretation.
Potential for Stray Currents/Corrosion
In some environments (especially with dissimilar metals and moisture), bonding everything together can increase the risk of galvanic corrosion. This is more of a concern in highly corrosive environments.
Effectiveness Questioned
Some argue that a small amount of rebar in a relatively small pad provides negligible grounding benefit compared to the main building grounding electrode system.
Factors Influencing the Decision
Size of the Pad
A very large, heavily reinforced pad is more likely to be considered a significant grounding component.
Local AHJ Interpretation
The most important factor. The local electrical inspector or AHJ has the final say. Contact them for their specific requirements.
Type of AC Unit
Larger, higher-voltage units are more likely to require bonding.
Soil Conditions
Soil resistivity affects grounding effectiveness. High resistivity soils might increase the need for supplemental grounding, including bonding the pad.*
Other Grounding Systems
The overall grounding system of the building is important. A robust grounding system may reduce the need for bonding the pad, while a weak system may increase it.
Recommendations
Consult the AHJ
The most crucial step is to contact the local electrical inspector or the Authority Having Jurisdiction (AHJ). Ask them specifically about their requirements for bonding AC equipment pads. Document their response.2.
Review the Project Specifications
The project specifications might already address this issue.3.
Consider a Grounding Study
For complex projects or in areas with challenging soil conditions, a grounding study by a qualified electrical engineer can provide valuable insights and recommendations.4.
Err on the Side of Caution
If there's uncertainty and the AHJ doesn't provide clear guidance, it's generally safer to bond the pad. This will help ensure safety and reduce potential liability.5.
Use Proper Bonding Techniques
If bonding is required, use approved methods and materials, such as exothermic welding (Cadweld) or listed grounding connectors.
In summary, while the NEC may not explicitly mandate bonding, the spirit of electrical safety, the potential for the pad to become energized, and the recommendations of the AHJ usually point toward bonding. Always consult with the local AHJ for their specific requirements. Flag for review