Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: MC cable firestopping UL interpretation

User: Tainted, Location: New York

Asked on: Tuesday, November 19, 2024 at 9:11 pm EST
Answered on: Thursday, March 6, 2025 at 5:26 am EST

Question: I plan to penetrate a 3 hour fire rated wall with 3/0 - 3 conductor + ground MC cable.I found a firestop submittal (see below and attached) which says this:3. Cable bundle to be a combination of any of the following:G. Maxmimum 3/C copper conductors no. 8 Awg metal clad cableI. Any cables, metal-clad cable or armored cable currently classified under the through penetrating product category.Why does it have 2 seperate conditions for "no. 8 cable" and "cables under the through penetrating products category"?What does "through penetrating products category" mean? Does it mean it needs to be rated for fire rated penetrations?Can I use 3/0 - 3 conductor + ground MC cable even if they say maximum allowed is #8 awg? The 3/0 cable I'm using is classified under the through penetrating products category I believe...

You've asked some very important questions. Let's break down this firestop submittal.

Understanding the Two Conditions

The reason for having two separate conditions (G and I) likely stems from the testing standards and how the firestop system was evaluated. Here's a likely explanation: Condition G (Maximum 3/C copper conductors no. 8 Awg metal clad cable)

This condition probably reflects a very specific test scenario. The firestop manufacturer likely tested the system with
only #8 AWG 3-conductor MC cable, and that test passed the 3-hour fire rating. Therefore, they can confidently state that this specific cable configuration is acceptable.

Condition I (Any cables, metal-clad cable or armored cable currently classified under the through penetrating product category)

This condition opens up the acceptable cable types and sizes beyond just the #8 AWG. It suggests that other cables and cable types have been individually tested with that specific firestop system and are listed in the manufacturer's documentation. It means the manufacture has done due deligence to ensure that the cable itself will not fail and cause the firestop to fail.

"Through Penetrating Products Category"


Yes, "through penetrating products category" does mean that the cable itself needs to be evaluated for fire-rated penetrations and listed as such in the manufacturer's documentation. It essentially means the cable has been tested to ensure that it doesn't contribute to the spread of fire through the penetration.

Can You Use 3/0 - 3 Conductor + Ground MC Cable?Potentially, yes, but you absolutely must verify specific documentation.

Here's the breakdown of how to determine if you can use the 3/0 cable:1. Manufacturer's Documentation is Key

You need to consult the detailed firestop manufacturer's installation instructions and product listings. These documents, beyond just the submittal excerpt you provided, are the only place you'll find the answer.2.

Look for Specific Listing

Look for a specific listing within the firestop manufacturer's documentation that explicitly states that the 3/0 - 3 conductor + ground MC cable is acceptable for use with that firestop system for a 3-hour fire-rated wall. This is critical. The listing will usually include the specific manufacturer and product number of the cable.3.

"Through Penetrating Products Category" Qualification

If the 3/0 MC cable is listed in the manufacturer's documentation, it will be because it has been evaluated and classified under the "through penetrating products category" and has a specific listing number or approval.4.

If No Specific Listing

If you cannot find a specific listing for your 3/0 cable size in the firestop manufacturer's documentation, then you cannot use it. Using it would violate the fire rating and code requirements. The #8 AWG limitation would then apply.

Important Considerations and Next Steps
Code Compliance

Your installation must meet all applicable local building codes and the National Electrical Code (NEC). The NEC has specific requirements for firestopping penetrations (e.g., NEC 300.21, 314.29, etc.)


AHJ Approval

Always consult with your local Authority Having Jurisdiction (AHJ) before installation. They have the final say in what is acceptable. Provide them with the firestop manufacturer's documentation and cable specifications.

Alternative Solutions

If your 3/0 cable isn't listed, consider:
Using a different firestop system that is listed for your cable size. Using a smaller cable size (if feasible for the electrical load). Installing a larger sleeve or opening that is listed for the 3/0 cable with the firestop.*

Documentation

Keep all manufacturer's documentation, product listings, and AHJ approvals on file for future reference.

In summary, you MUST consult the firestop manufacturer's detailed documentation and the cable manufacturer's documentation. If the 3/0 MC cable is not specifically listed with that firestop system for a 3-hour fire-rated wall, you cannot use it.
Flag for review

Previous Question Next Question