Question: Hi All,I have a ductless mini-split type A/C unit. This unit condenser circuit feeds the indoor unit (1 circuit) per manufacturer. My question is how do you typically calculate the voltage drop for something like this and how are they typically connected? For example: The condenser on the roof (above 3rd floor) and indoor unit is in the (1st floor hallway).Distance: (Panel to condensor 50feet) ----- (condensor to indoor unit 50feet) ---- (Panel to indoor 10feet)Assume the panel that is feeding the condenser is also on the first floor. Is the circuit going from the panel location to roof condenser to indoor unit?Or is the circuit in the first floor being split on 1st floor where one is going to condenser (roof) and one is going to indoor unit 1st floor?The voltage drop will be much higher if it is a full loop.Thank you,
Okay, let's break down how mini-split connections typically work and how to calculate voltage drop for your situation.
Understanding Mini-Split Wiring (General Case)
Mini-split wiring is often a point of confusion because it's not the same as wiring a central AC unit. Here's the typical arrangement: Power to the Condenser (Outdoor Unit)
The main power supply (from your panel) always goes to the condenser unit first. The breaker and wiring must be sized to handle the entire load of the system (condenser and indoor unit).
Control/Communication Wires (Indoor to Outdoor)
A separate set of low-voltage wires (typically 14-18 AWG, multi-conductor cable) is used for communication between the condenser and the indoor unit. These wires carry signals for things like fan speed, temperature settings, and on/off control. They do not carry significant power.
Power from Condenser to Indoor (Sometimes)
As you mentioned, some mini-split systems power the indoor unit directly from the condenser. In this case, the conductors from the condenser to the indoor unit will carry the voltage, and will need to be sized accordingly to account for the load and voltage drop.
Determining Your Specific Setup
The critical question is: How is the indoor unit powered?1. Check the Wiring Diagram
The best way to determine this is to consult the wiring diagram that came with your mini-split. This diagram will clearly show how the indoor and outdoor units are connected and powered. It will also show you the load and FLA.2.
Inspect the Wiring
Look closely at the wiring connections at both the condenser and the indoor unit.
Power Wires at the Indoor Unit
If you see line-voltage wires (e.g., 12/2 or 14/2 Romex) connected to the indoor unit's power terminals, it suggests the indoor unit is being powered directly from the condenser.
Only Communication Wires
If you only see low-voltage communication wires at the indoor unit, it almost certainly confirms that the indoor unit is being powered from the condenser.
Based on your comment, here's the most likely scenario (and how to calculate voltage drop)
The main power supply (from the panel) goes to the condenser. The condenser then provides power to the indoor unit. This is the single circuit you mentioned.
Calculating Voltage Drop (Assuming Condenser Powers Indoor Unit)
In this case, you have one continuous circuit from the panel, through the condenser, and then to the indoor unit. You need to treat it as a single, long circuit for voltage drop calculations.1. Total Circuit Length
Panel to Condenser: 50 feet Condenser to Indoor Unit: 50 feet
Total: 100 feet2. Calculate Voltage Drop
Formula
There are several voltage drop calculators available online (search for "voltage drop calculator"). You'll need to input the following:
Voltage
120V or 240V (depending on your unit)
Amperage (Load)
The total amperage draw of the system (condenser + indoor unit). This should be listed on the condenser's nameplate or in the installation manual. Use the Full Load Amps (FLA) rating.
Wire Gauge
The size of the wires you are using for the circuit.
Circuit Length
100 feet (as calculated above)
Conductor Material
Copper or Aluminum
Number of Conductors 2 (for single phase) Acceptable Voltage Drop
For branch circuits (like this), a maximum voltage drop of 3% is generally recommended. Anything higher than 3% could cause issues with the equipment's performance and lifespan.
Example (Illustrative Only)
Let's say: Voltage: 240V Total FLA: 10 Amps Wire Gauge: 12 AWG Copper Circuit Length: 100 feet Conductors: 2Plugging this into a voltage drop calculator might give you a voltage drop of around 5-6 volts, or about 2.5%. This would be acceptable.
Important Considerations
Minimum Wire Size
The wire size must be adequate to carry the load per NEC (National Electrical Code) requirements. Voltage drop calculations are secondary to meeting the minimum ampacity requirements. You can't choose a smaller wire just to reduce voltage drop if it's not rated for the load.
Starting Current
Mini-splits (especially inverter-driven models) can have a significant inrush (starting) current. Your breaker and wiring must be sized to handle this. The manufacturer's specifications will give you guidance on this. A "time delay" breaker is often recommended.
Professional Advice
If you are not comfortable working with electrical wiring, it is highly recommended that you hire a qualified electrician. Mistakes can be dangerous and can damage your equipment.
To Summarize
Confirm the Wiring Diagram
The first step is always to consult the wiring diagram that came with your mini-split system.2.
Identify the Circuit Length
Determine if the indoor unit is powered from the condenser or has its own dedicated circuit. Calculate the total circuit length (panel to condenser to indoor unit).3.
Calculate Voltage Drop
Use a voltage drop calculator, considering the total circuit length, amperage, and wire gauge.4.
Ensure Compliance
Make sure the wire size meets the NEC requirements for the load and that the voltage drop is within acceptable limits.5.
Consult a Professional: If you have any doubts, hire a qualified electrician to handle the wiring.Good luck! Flag for review