Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Hvac wire size

User: number2, Location: Nc

Asked on: Wednesday, November 20, 2024 at 4:38 pm EST
Answered on: Thursday, March 6, 2025 at 5:28 am EST

Question: ResidentialI have a unit with a heat kit strip 41.9/47.4  mca 45/50 mopMy question is what wire size would I need to feed this unit in aluminum?Normally I use copper but it's too expensive and I heard this new aluminum is not so bad type se

Okay, let's figure out the aluminum wire size for your heat kit. Here's a breakdown of the calculations and considerations, along with some important safety advice

1. Understanding the Information You Provided:
41.9/47.4 MCA

MCA stands for Minimum Circuit Ampacity. This means the
minimum current the circuit must be able to handle. You have two values.

Use the higher value: 47.4 Amps
. This number is crucial for wire sizing. 45/50 MOP

MOP stands for Maximum Overcurrent Protection. This is the maximum size breaker or fuse allowed to protect the circuit. Again, you have two values.

Use the higher value: 50 Amps
. This is important for both safety and code compliance. Residential

This tells us we're using the National Electrical Code (NEC) for residential wiring.


Heat Kit Strip

This indicates a resistance-based heating element. These typically have a fairly constant current draw.

Aluminum Type SE

You're considering using Service Entrance (SE) cable with aluminum conductors. This is a common and generally safe practice when done correctly.

2. Calculating Wire Size (Aluminum Conductors)



NEC Table 310.16 (Ampacity of Conductors)

This is the table we need to consult. This table gives the ampacity (current-carrying capacity) of different wire sizes based on the insulation type and temperature rating. Common insulation types are THHN, THW, THWN, XHHW. We also need to know the temperature rating of the terminals, as this will be the limiting factor when choosing the wire size. Terminals are usually rated for either 60°C or 75°C. Check the equipment to determine which rating to use. If the equipment is not marked, assume 60°C.

Applying the MCA

We need to find a wire size that has an ampacity
equal to or greater than the 47.4 MCA.

Common Aluminum Wire Sizes and Ampacities (Based on NEC Table 310.16, 75°C column - adjust as needed based on your specific insulation type and terminal rating)



#6 AWG Aluminum

Typically rated for 50 Amps at 75°C.


#4 AWG Aluminum

Typically rated for 60 Amps at 75°C.

Therefore, at 75C you would need #6 aluminum wire.
At 60C you would need #4 aluminum wire.3. Overcurrent Protection (Breaker/Fuse)

You stated that the maximum overcurrent protection (MOP) is 50 Amps.

This means you MUST use a 50 Amp breaker or fuse.
The wire size you choose must be rated to handle at least the overcurrent protection. In this case, #6 aluminum at 75C would be sufficient.4. Important Considerations and Safety



Aluminum Termination



This is CRITICAL.
Aluminum wire expands and contracts more than copper. This can lead to loose connections over time, which can cause overheating and fire hazards. Use ONLY devices (breakers, receptacles, switches, wire connectors) that are specifically rated for use with aluminum wire. Look for markings like "AL-CU" (Aluminum-Copper) or "CO/ALR" (Copper/Aluminum Revised). Use an anti-oxidant joint compound designed for aluminum connections (e.g., Noalox or Penetrox) when connecting the aluminum wire to the device. This helps prevent oxidation and corrosion. Torque Connections Properly

Use a torque screwdriver or wrench to tighten the connections to the manufacturer's specified torque value. Under-torquing or over-torquing can both lead to problems.


Local Codes

Always check with your local electrical inspector or building department to ensure you are complying with all applicable codes and regulations. Local codes may have stricter requirements than the NEC.

Professional Installation

I
strongly recommend that you have this work performed by a qualified and licensed electrician. Electrical work can be dangerous and requires specific knowledge and skills. Improper wiring can create a fire hazard or electrical shock hazard.

Voltage Drop

For long wire runs, you may need to increase the wire size to account for voltage drop. Voltage drop is the decrease in voltage along a wire due to its resistance. Excessive voltage drop can cause appliances to operate inefficiently or not at all. The NEC recommends limiting voltage drop to 3% for branch circuits.

In summary



Wire Size

#6 AWG Aluminum at 75C terminal rating or #4 AWG Aluminum at 60C terminal rating


Breaker/Fuse

50 Amp

Crucial

Use proper aluminum-rated connectors, anti-oxidant joint compound, and torque connections correctly.


Best Practice

Hire a qualified electrician.

Disclaimer:
This information is for general guidance only and should not be considered a substitute for professional advice. Always consult with a qualified and licensed electrician and refer to the National Electrical Code (NEC) and your local electrical codes for specific requirements. Electrical work can be dangerous, and it's essential to prioritize safety. Flag for review

Previous Question Next Question