Topic: Derating PV conductors on roofs.

User: electrofelon, Location: Cherry Valley NY, Seattle, WA

Asked on: Wednesday, November 20, 2024 at 9:10 pm EST
Answered on: Thursday, March 6, 2025 at 5:28 am EST

Question: Confused. Do I use T 690.31(A) or 310.15(B)(3)(c) (and then 310.15(B)(2)(a))?The quick brown fox jumped over the lazy dogs

Okay, let's break down when to use NEC 690.31(A) versus NEC 310.15(B)(3)(c) and 310.15(B)(2)(a) (and why they might both be relevant in your situation).

The core of the issue is ampacity adjustment factors, and the context is likely Photovoltaic (PV) wiring. NEC 690.31(A) - Single-Conductor Cables. This section deals specifically with single-conductor cable installations for PV systems. It has a specific condition that says these cable assemblies must be in cable trays that provide shielding and the cable assemblies must be identified for use with the cable tray. NEC 310.15(B)(3)(c) - Adjustment Factors. This section, along with 310.15(B)(2)(a), comes into play when you have multiple current-carrying conductors in a raceway, cable, or earth (directly buried). When multiple cables or raceways are installed in close proximity. This section applies to all electrical installations unless specifically changed or modified elsewhere in the code (ex. by article 690).Here's how to decide which one to use, and why they might BOTH be relevant:1. PV System Context

The fact that you're considering 690.31 strongly suggests you're dealing with a PV system. This is important because Article 690 modifies or adds to the general rules of the NEC.
2.


Type of Conductor/Cable



Single-Conductor Cable?
YES

If you are using single-conductor cables in a PV system, AND they are installed in cable trays that meet the requirements of 690.31(A), the requirements of 310.15(B)(3)(c) and 310.15(B)(2)(a) do not need to be applied.

NO

If you are NOT using single-conductor cables in a PV system, continue to 3.3.

Multiple Current-Carrying Conductors



Are you running multiple current-carrying conductors in the same raceway, cable, or directly buried in close proximity?
YES

If so, the adjustment factors in 310.15(B)(3)(c) WILL likely apply.


NO

If you are running only a single circuit (e.g., a single positive and negative conductor from one string of PV modules in its own conduit), then the adjustment factors in 310.15(B)(3)(c) MAY not apply (depending on other factors like ambient temperature correction - see below).
4.


Ambient Temperature

ALWAYS check 310.15(B)(1) for ambient temperature correction factors. This is always the first thing to consider before adjustment factors for multiple conductors. High ambient temperatures require you to further reduce the ampacity of the wire. This applies to all installation methods and conductor types.

In summary



Start with

Ambient temperature correction (310.15(B)(1)) - Always applies.


Then consider

If using single-conductor conductors in cable trays in a PV system, 690.31(A)

THEN consider

The number of current-carrying conductors and proximity of cables/raceways and apply 310.15(B)(3)(c)
in addition to the ambient temperature correction.

Example

Let's say you are running three 3-conductor cables (each with 3 current-carrying conductors, for a total of 9 current-carrying conductors) in the same conduit in an ambient temperature of 40°C.1.

Ambient Temperature

You MUST apply an ambient temperature correction factor from 310.15(B)(1). This will reduce the allowable ampacity.
2.


Multiple Conductors

Since you have 9 current-carrying conductors in a single raceway, you must apply the adjustment factor from 310.15(B)(3)(c).
3.


Final Ampacity

You take the base ampacity of the wire from the appropriate table (e.g., 310.16), multiply it by the ambient temperature correction factor, and
then multiply it by the adjustment factor from 310.15(B)(3)(c). The result is the final, adjusted ampacity you can use for your calculations.

Important Considerations



Derating vs. Adjusting

It's important to understand that the NEC uses the terms "derating" and "adjusting" specifically. In general terms, they both have a similar effect, but the NEC uses "derating" more for equipment ratings and "adjusting" for ampacity adjustment factors.

Article 100 Definitions

Refer to the NEC Article 100 definitions to confirm your understanding of "ampacity," "ambient temperature," "current-carrying conductor," etc. Understanding these terms precisely is crucial.


Tables

Make sure you are using the correct ampacity tables (310.16 and others) and the correct adjustment factor tables.

Engineering Judgment

Ultimately, determining the correct application of these code sections often requires engineering judgment and a thorough understanding of the entire electrical system. If you are unsure, consult a qualified electrical engineer or inspector.


AHJ

Your local Authority Having Jurisdiction (AHJ) has the final say on code interpretation. Always check with them if you have any doubts.To give you the BEST advice, I'd need to know:

Specifically what type of conductor/cable you are using.
How are you installing it (raceway, cable tray, direct burial, etc.)? How many current-carrying conductors will be in each raceway/cable? What is the ambient temperature?

Good luck! Flag for review