Question: Confused. Do I use T 690.31(A) or 310.15(B)(3)(c) (and then 310.15(B)(2)(a))?The quick brown fox jumped over the lazy dogs
Okay, let's break down when to use NEC 690.31(A) versus NEC 310.15(B)(3)(c) and 310.15(B)(2)(a) (and why they might both be relevant in your situation).
The core of the issue is ampacity adjustment factors, and the context is likely Photovoltaic (PV) wiring. NEC 690.31(A) - Single-Conductor Cables. This section deals specifically with single-conductor cable installations for PV systems. It has a specific condition that says these cable assemblies must be in cable trays that provide shielding and the cable assemblies must be identified for use with the cable tray. NEC 310.15(B)(3)(c) - Adjustment Factors. This section, along with 310.15(B)(2)(a), comes into play when you have multiple current-carrying conductors in a raceway, cable, or earth (directly buried). When multiple cables or raceways are installed in close proximity. This section applies to all electrical installations unless specifically changed or modified elsewhere in the code (ex. by article 690).Here's how to decide which one to use, and why they might BOTH be relevant:1. PV System Context
The fact that you're considering 690.31 strongly suggests you're dealing with a PV system. This is important because Article 690 modifies or adds to the general rules of the NEC.
2.
Type of Conductor/Cable
Single-Conductor Cable? YES
If you are using single-conductor cables in a PV system, AND they are installed in cable trays that meet the requirements of 690.31(A), the requirements of 310.15(B)(3)(c) and 310.15(B)(2)(a) do not need to be applied.
NO
If you are NOT using single-conductor cables in a PV system, continue to 3.3.
Multiple Current-Carrying Conductors
Are you running multiple current-carrying conductors in the same raceway, cable, or directly buried in close proximity? YES
If so, the adjustment factors in 310.15(B)(3)(c) WILL likely apply.
NO
If you are running only a single circuit (e.g., a single positive and negative conductor from one string of PV modules in its own conduit), then the adjustment factors in 310.15(B)(3)(c) MAY not apply (depending on other factors like ambient temperature correction - see below).
4.
Ambient Temperature
ALWAYS check 310.15(B)(1) for ambient temperature correction factors. This is always the first thing to consider before adjustment factors for multiple conductors. High ambient temperatures require you to further reduce the ampacity of the wire. This applies to all installation methods and conductor types.
In summary
Start with
Ambient temperature correction (310.15(B)(1)) - Always applies.
Then consider
If using single-conductor conductors in cable trays in a PV system, 690.31(A)
THEN consider
The number of current-carrying conductors and proximity of cables/raceways and apply 310.15(B)(3)(c) in addition to the ambient temperature correction.
Example
Let's say you are running three 3-conductor cables (each with 3 current-carrying conductors, for a total of 9 current-carrying conductors) in the same conduit in an ambient temperature of 40°C.1.
Ambient Temperature
You MUST apply an ambient temperature correction factor from 310.15(B)(1). This will reduce the allowable ampacity.
2.
Multiple Conductors
Since you have 9 current-carrying conductors in a single raceway, you must apply the adjustment factor from 310.15(B)(3)(c).
3.
Final Ampacity
You take the base ampacity of the wire from the appropriate table (e.g., 310.16), multiply it by the ambient temperature correction factor, and then multiply it by the adjustment factor from 310.15(B)(3)(c). The result is the final, adjusted ampacity you can use for your calculations.
Important Considerations
Derating vs. Adjusting
It's important to understand that the NEC uses the terms "derating" and "adjusting" specifically. In general terms, they both have a similar effect, but the NEC uses "derating" more for equipment ratings and "adjusting" for ampacity adjustment factors.
Article 100 Definitions
Refer to the NEC Article 100 definitions to confirm your understanding of "ampacity," "ambient temperature," "current-carrying conductor," etc. Understanding these terms precisely is crucial.
Tables
Make sure you are using the correct ampacity tables (310.16 and others) and the correct adjustment factor tables.
Engineering Judgment
Ultimately, determining the correct application of these code sections often requires engineering judgment and a thorough understanding of the entire electrical system. If you are unsure, consult a qualified electrical engineer or inspector.
AHJ
Your local Authority Having Jurisdiction (AHJ) has the final say on code interpretation. Always check with them if you have any doubts.To give you the BEST advice, I'd need to know:
Specifically what type of conductor/cable you are using. How are you installing it (raceway, cable tray, direct burial, etc.)? How many current-carrying conductors will be in each raceway/cable? What is the ambient temperature?