Topic: How to size service conductors

User: patricknola, Location: new orleans, La, United States

Asked on: Thursday, November 21, 2024 at 7:07 am EST
Answered on: Thursday, March 6, 2025 at 5:29 am EST

Question: Good morning, I'm replacing the panel and meter socket on 1/2 of a duplex. They're getting an upgrade to a 200 amp service, the other half will stay 100 amps. There is a single service mast common to both meters that will have to be replaced. Do I add 200 + 100 and then multiply times .87? What other debating factors could I consider? TIA

Good morning! Replacing a meter socket and upgrading a panel to 200A on a duplex with a shared service mast definitely requires careful planning and calculations. Here's a breakdown of how to approach the load calculation and some crucial factors to consider

Understanding the Load Calculation

Your initial thought of adding the two services and applying a demand factor is on the right track, but let's refine the approach:1. Individual Unit Calculations

First you need to perform separate load calculations for each unit. This is critical.

Unit A (200A Upgrade)

Calculate the load for the 200A unit using the standard method in Article 220 of the National Electrical Code (NEC). This includes:
General lighting and receptacle loads (3VA per square foot) Small appliance branch circuits (2 x 1500VA) Laundry circuit (1500VA) Fixed appliances (ranges, ovens, water heaters, HVAC, etc. – use nameplate ratings). Range demand factors (Table 220.55) can be applied where appropriate. Electric vehicle chargers (if any) - these require a significant dedicated load calculation Any other significant loads.

Unit B (100A Existing)

Do the same load calculation for the 100A unit, using its existing appliance and load information.2.

Demand Factors for a Duplex (Optional, but Often Beneficial)

Once you have the individual unit load calculations, you might be able to apply demand factors from NEC Article 220.

Ranges (Table 220.55)

If both units have electric ranges, you might be able to use the range demand factors. This can significantly reduce the calculated load. Carefully review the table.

Optional Method (Article 220 Part IV)

If you have detailed historical energy consumption data and the utility allows it, you
could potentially use the optional calculation method for dwelling units. This is complex and requires more information, but could lead to a lower calculated load. This is UNLIKELY in a simple duplex upgrade scenario.3.

Combining the Loads and Sizing the Service Mast

This is where your initial thought process comes in.


Add the Calculated Loads

Add the total calculated load (after applying any applicable demand factors) for Unit A and Unit B. This is the total demand on the service.

Service Mast Size

The service mast must be sized to carry this total calculated load
continuously.4.

NEC 310.16 and Ampacity Considerations

Once you know the total calculated load in amps, you must select conductors for the service entrance cable and service mast that are rated to carry that amperage. Consult NEC Table 310.16 to determine the appropriate conductor size based on its insulation type (e.g., THHN, XHHW) and the termination temperature rating of the equipment.

Important

Pay close attention to the
termination temperature rating of the service equipment (meter socket, panel). Many are only rated for 75°C. You must use the 75°C column in Table 310.16 for ampacity if that's the case.

Parallel Conductors

If the required ampacity is very high, you might need to consider running conductors in parallel. This is a more complex installation requiring specific NEC rules.

Debating Factors and Considerations



Future Expansion

Even if the current calculated load is relatively low, consider the
potential for future expansion. Will either unit likely add a hot tub, a larger HVAC system, an EV charger, or other high-demand appliances in the future? It's often wise to oversize the service mast slightly to accommodate future needs. This is much cheaper to do now than to replace it later.

Electric Vehicle (EV) Chargers

If either unit currently has or plans to install an EV charger, this is a major factor. EV chargers can add a significant continuous load (often 30-50 amps or more). The NEC requires that the load calculation include 100% of the EV charger's nameplate rating (or 125% if the charger is considered a continuous load).

Local Utility Requirements

Crucially, check with your local utility company. They often have specific requirements for service size, meter socket types, grounding, and disconnect locations. They may also require an inspection and approval of the upgrade. They may even dictate the size of the service based on their standards, not just the NEC minimum.

Available Space

Consider the physical space available for the new meter socket, panel, and service mast. Ensure you have adequate working clearances as required by the NEC.

Existing Grounding and Bonding

Carefully inspect the existing grounding and bonding system. Ensure it is adequate and meets current NEC requirements. You may need to upgrade the grounding electrode system (e.g., adding ground rods or a concrete-encased electrode).


Disconnect Location

The location of the main disconnect(s) is important. Each unit must have a readily accessible disconnect. The NEC and local codes may dictate the allowable distance from the meter.

Cost

Factor in the cost of the new meter socket, panel, service mast, conductors, grounding materials, and any permits or inspection fees. Get multiple quotes from qualified electricians.


Permits and Inspections

Obtain all necessary permits before starting the work. Schedule inspections at the appropriate stages to ensure compliance with the NEC and local codes.

Professional Expertise

This is a complex electrical upgrade.
Highly recommend hiring a licensed and experienced electrician to perform the work. They will be familiar with the NEC, local codes, and utility requirements. Attempting this yourself without the proper knowledge and experience can be dangerous and could result in code violations, electrical fires, or electrocution.

Coordination with the Tenants

Because you're upgrading only one half of the duplex, coordination with both tenants will be important. Clear communication about the schedule and potential power outages is crucial for minimizing disruption.

Example Scenario (Simplified)

Let's say: Unit A (200A Upgrade): Calculated load = 120 amps (after demand factors) Unit B (100A Existing): Calculated load = 60 ampsTotal Calculated Load = 120 amps + 60 amps = 180 ampsIn this simplified example, you would need to select a service mast and conductors rated for at least 180 amps, considering the termination temperature ratings of the equipment. You would likely use 2/0 or 3/0 AWG copper conductors (check Table 310.16). However, remember this is just a simplified example. The actual calculations will likely be more involved.

In summary:
Don't just apply a percentage to the combined service sizes. Perform individual load calculations, apply appropriate demand factors (if applicable), add the results, and then size the service mast and conductors accordingly, considering NEC ampacity rules and termination temperature ratings. And, most importantly, consult with a qualified electrician and your local utility company. Good luck with your upgrade! Flag for review