User: Seven-Delta-FortyOne, Location: Humboldt
Asked on: Thursday, November 21, 2024 at 7:19 pm EST
Answered on: Thursday, March 6, 2025 at 5:32 am EST
Question: When I install Generac, I usually use the GenCable, which is type TC-ER, and rated for direct burial.When I install other types, usually it gets conduit and THWN-2. But I think that type USE direct burial from the generator to the exterior mounted ATS would be fine, if I was doing a direct burial method.Only restriction I see is if the ATS were mounted inside a building, I would have to transition to SE or some other type of wiring to enter the structure.
You've got a good grasp of the common practices and the basic principles. Let's break down your points with some nuances and considerations
1. GenCable (TC-ER):
Advantages
TC-ER (Tray Cable - Exposed Run) is indeed a popular and convenient choice for generator connections. Its flexibility, durability, and direct burial rating (if specifically designed for that) make it a time-saver. It's also generally easier to pull through tighter spaces than conduit.
Things to Watch
While most GenCable is direct burial rated, always verify the specific cable's markings and specifications. Look for "DIR BUR" or similar direct burial approval on the cable jacket. Also, ensure it's sized correctly for the generator's ampacity and voltage drop over the run. Use a voltage drop calculator to ensure the generator can properly power the loads at the far end of the run.
Support Requirements
Even though TC-ER is permitted for exposed runs, it still needs to be properly supported and secured. Refer to the NEC (National Electrical Code) article 336 for the specifics. Avoid excessive sagging.
2. THWN-2 in Conduit
Advantages
Conduit offers excellent mechanical protection. It's a good choice in areas where the cable is likely to be damaged (e.g., vehicle traffic, landscaping, etc.). THWN-2 is a very common and readily available wire type. It's also a good option if future upgrades are anticipated.
Disadvantages
More labor-intensive. Requires fittings, bending, and potentially trenching a wider path to accommodate the conduit's bending radius. Can be more costly than TC-ER, especially for long runs.
Considerations
Use appropriately rated conduit (PVC, rigid metal, etc.) for the environment (e.g., PVC isn't suitable for direct sunlight in some areas). Properly size the conduit to allow for adequate wire fill (NEC Ch. 9). Ensure the conduit is buried to the correct depth per NEC.
3. USE (Underground Service Entrance) Cable for Direct Burial
Your Understanding is Correct
USE cable is a direct burial rated cable and suitable for direct burial applications from the generator to the exterior ATS, provided it meets the following:
Ampacity and Voltage Drop
As with any conductor, ensure it's sized appropriately for the load and distance to minimize voltage drop.
Termination
Use appropriate connectors rated for USE cable (e.g., compression lugs).
Burial Depth
Bury it at the appropriate depth as required by the NEC and local codes.
Key Advantages
Potentially lower cost than TC-ER in some cases.
Disadvantages
Less flexible than TC-ER, potentially making it more difficult to maneuver in tight spaces or around obstacles. More susceptible to damage during installation if not handled carefully.
4. Transitioning to Inside a Building
Your Understanding is Correct
You cannot simply bring direct burial cable (USE or TC-ER, unless specifically designed for this use case) directly into a building and terminate it. You need to transition to an approved wiring method for interior wiring.
Acceptable Transition Methods
SE (Service Entrance) Cable
A common choice for transitioning from outside to inside at the service entrance of a building.
NM-B (Non-Metallic Sheathed Cable) / Romex
If the wiring is not considered "service entrance" (i.e., is fed from the ATS), you can use NM-B cable after the transition box. However, NM-B must be protected if subject to physical damage.
Conduit and THWN-2
If the ATS is inside, conduit can run directly into the building, and you transition to THWN-2 inside the conduit outside the building.
Transition Box
The transition must be made in an approved junction box that is properly grounded. This box must be accessible. You can't just splice wires buried underground without an enclosure.
Important Considerations and Best Practices
Local Codes and AHJ (Authority Having Jurisdiction)
Always check with your local building department and electrical inspector (AHJ) before starting any electrical work. Local codes may have specific requirements or restrictions that supersede the NEC. Some jurisdictions may prefer or require certain wiring methods.
Generator and ATS Manufacturer's Instructions
Always follow the generator and ATS manufacturer's instructions for wiring recommendations and requirements.
Grounding
Proper grounding is critical for safety. Ground the generator and ATS according to the NEC and manufacturer's instructions. This typically involves grounding electrodes (ground rods) and bonding the equipment to the grounding system.
Overcurrent Protection
Ensure proper overcurrent protection (circuit breakers or fuses) is installed at both the generator and the ATS to protect the wiring and equipment from overloads and short circuits.
Disconnect Switch
Consider installing a disconnect switch near the generator for maintenance or emergency situations.
Labeling
Clearly label all wiring and components to identify their purpose (e.g., "Generator Input," "Load Output").*
Licensed Electrician
This type of work should ideally be performed by a licensed electrician. Electrical work can be dangerous, and improper installation can lead to fire, shock, or equipment damage.
In summary, you have a solid understanding of the basics. Remember to always prioritize safety, consult the NEC, adhere to local codes, and follow the manufacturer's instructions. Good luck with your installations! Flag for review