Topic: Tap Service Conductors with Polaris

User: solarken, Location: Hudson, OH, USA

Asked on: Friday, November 22, 2024 at 1:17 pm EST
Answered on: Thursday, March 6, 2025 at 5:34 am EST

Question: 2023 NEC 230.46 specifies tap devices be listed and marked for SUSE use. I called NSi and asked a sales person if they were labeled for that use and they said yes, but looking at photos form an online distributor I do not see that labeling. Has anyone seen that marking on an IPCS4002?

You're right to be skeptical. The wording in 2023 NEC 230.46 is very specific and requires explicit listing and marking for SUSE (Service-entrance Use, Service Equipment). A general "suitable for grounding" or "suitable for bonding" marking isn't enough.Here's a breakdown of why this is important and what to look for: NEC 230.46's Intent

The intent of 230.46 is to ensure that tap connectors used on service entrance conductors are robust and safe enough for service conditions. This includes factors like fault current withstand and proper insulation.


Listing and Marking

Listing means the product has been tested and certified by a Nationally Recognized Testing Laboratory (NRTL) like UL, CSA, ETL, etc. Marking means the product is physically marked with the NRTL's symbol and specific information about its application.

SUSE is Key

The "SUSE" marking is critical. It tells the inspector that the connector has been specifically evaluated and found suitable for use as a service entrance tap.

Regarding the NSi IPCS4002 and SUSE


Manufacturer is Best Source

Contact NSi
directly, preferably their technical support or engineering department, not just a salesperson. Ask for written confirmation (datasheet, certification document, or email) specifically stating that the IPCS4002 is listed and marked for SUSE. A verbal statement from a salesperson isn't sufficient.2.

Online Photos are Unreliable

Don't rely solely on online photos. They may be outdated, of poor quality, or not show all relevant markings.3.

Check NRTL Website

Once you have the NRTL information from NSi (e.g., "UL Listed" and the UL file number), go to the NRTL's website (e.g., UL's Product iQ database) and search for the product by model number and/or file number. This will give you the official listing information and what it is certified for.4.

Inspect the Product

If you have access to the actual IPCS4002, look closely for the NRTL symbol and the SUSE marking directly on the connector body.5.

Ask your Inspector

If you're still unsure, contact your local electrical inspector. They are the final authority on code compliance and can tell you if they will accept the IPCS4002 for service entrance tap applications.

Important Considerations



UL 486A-486B

Connectors used in service entrance applications are typically tested under UL 486A-486B, which covers wire connectors and soldering lugs. However, passing this standard alone doesn't automatically mean it's listed and marked for SUSE. The connector must have specifically undergone testing and listing for service entrance use.



Documentation is Key

Keep all documentation (manufacturer's spec sheets, NRTL listing information) readily available for the inspector.

In summary:
* Don't take the salesperson's word for it. Verify the SUSE listing and marking with the manufacturer's technical documentation and the NRTL listing. And when in doubt, consult your electrical inspector. Flag for review