Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: EGC size after long, upsized run

User: Electromatic, Location: Virginia

Asked on: Friday, November 22, 2024 at 2:15 pm EST
Answered on: Thursday, March 6, 2025 at 5:34 am EST

Question: I'm trying to confirm the proper EGC size for a service that will be partially temped-in during construction. It's a bit of an oddball, though. There is an existing 200A feeder run a long distance to a pole-mounted disconnect that then continues a short distance to a small pumping building. The temp service will be from the pole disconnect to the building. The long run is using 2 sets of 250kcmil Aluminum in (2)3"RMC conduits with the conduits acting as the EGC.For the new temp from the pole to the building, I think a single run of 250kcmil (205A) will be okay. Can I just base the EGC size on that portion of the run on the 200A OCPD and use #6Cu/#4Al?

Yes, you are correct. Because you are creating a temporary service from the pole disconnect to the pumping building, you only need to size the EGC based on the overcurrent protection device (OCPD) protecting the temporary service conductors.Here's a breakdown of why and how: Service vs. Feeder

The key here is that you're creating a
temporary service, not extending the existing feeder. The long run to the pole disconnect is the feeder, and its EGC sizing is based on the feeder conductors and 250.122. Your temporary service is from the disconnect to the building.

250.24(A)(1)

This section in the NEC is relevant because it addresses the grounding electrode conductor (GEC) at the service. However, it doesn't dictate the size of the EGC run with the service conductors.

250.122

This section provides the requirements for sizing equipment grounding conductors. Table 250.122 directly correlates the OCPD rating to the minimum EGC size.


Your Scenario

Since the temporary service is protected by a 200A OCPD, Table 250.122 specifies a minimum of #6 AWG Copper or #4 AWG Aluminum for the EGC.

Important Considerations and Clarifications



Type of EGC

You'll need to determine what type of EGC you'll be using for the temporary service. If you are running wire it must be insulated, covered, or bare copper. It must also follow the requirements in 250.118 for acceptable types of equipment grounding conductors.


Installation Method

Ensure your EGC is installed properly (e.g., run with the phase conductors) to minimize impedance and voltage drop.

In summary:


You are correct. For the temporary service from the pole disconnect to the building, protected by a 200A OCPD, a #6 AWG copper or #4 AWG aluminum EGC is sufficient, based on Table 250.122 of the NEC. Remember to follow all other applicable NEC requirements for temporary wiring, grounding, and bonding. Flag for review

Previous Question Next Question