User: gene6, Location: NY
Asked on: Friday, November 22, 2024 at 4:33 pm EST
Answered on: Thursday, March 6, 2025 at 5:35 am EST
Question: I was told today that motors 6 amps or more need to be on individual circuits.So say I have two 1/3 HP 120V pump motors and a GFCI to install do they each need a 20A circuit or can they share?Each motor is about 7A nameplate.Where is the article 430 reference on motors 6 Amps or more so I can read up on this?
You're right to question this! The statement "motors 6 amps or more need to be on individual circuits" is an oversimplification and potentially misleading. Here's a breakdown of the rules and how they apply to your situation
Understanding the Rule: Individual Branch Circuits for Motors
The NEC does require individual branch circuits for many motor installations, but not all motors over 6 amps. The requirement isn't solely based on the motor's nameplate current. It's more about protecting the motor, wiring, and other equipment during starting (inrush current) and overload conditions.
Key NEC Sections to Review in Article 430
Article 430, Part III (Overload Protection)
This is crucial. It outlines how to protect motors from overloads. Overload protection is designed to trip at currents somewhat higher than the motor's full-load amps (FLA). The exact percentage allowance depends on the motor's design.
Article 430, Part IV (Motor Branch-Circuit Short-Circuit and Ground-Fault Protection)
This section dictates the size of the branch-circuit protective device (circuit breaker or fuses). This is usually sized much higher than the motor FLA to allow for the inrush current during starting.
430.52 Rating or Setting for Individual Motor Circuit
This is the core section dealing with the branch-circuit short-circuit and ground-fault protection sizing. It provides tables and rules for determining the maximum size of the circuit breaker or fuses.
430.53 Several Motors or Loads on One Branch Circuit
This is the section that specifically addresses whether you can have multiple motors on one circuit. Pay close attention to the conditions that allow multiple motors on a single branch circuit.
Analyzing Your Specific Situation (Two 1/3 HP Pumps at 7A each)1. Nameplate FLA
Each motor is rated at 7A.2.
Overload Protection
You must provide individual overload protection for each motor. This can be done with:
Overload relays
These are common in motor starters (which you likely don't have for small pumps like these).
Internal thermal protection
Some motors have built-in thermal protection that will automatically shut the motor off if it overheats. Check the motor's documentation. If the motor has built-in thermal protection adequate to protect the motor the protection requirements of 430.53 would not apply.
3.
Branch-Circuit Protection (Short-Circuit and Ground-Fault)
This is where it gets more complex. The NEC allows for more than one motor on a single branch circuit
IF certain conditions are met: Each motor must have its own overload protection. (As stated above) The branch-circuit protection device (breaker or fuses) must not exceed the ampacity allowed by 430.53. This is where the calculations come in.
Steps to Determine if You Can Share a Circuit (Simplified)
Individual Overload Protection
Confirm each pump motor has adequate overload protection (either internal or external).2.
Calculate Total Load
7A + 7A = 14A (This is the total continuous load from the motors). You also need to factor in any other loads on the circuit (lights, etc.).3.
Determine if the Circuit Can Handle the Load
A 20A circuit is rated for a continuous load of 16A. (20A 80% = 16A). In some cases it may be allowed to load the circuit more than 80%, for example the circuit breaker might be rated at 100% continuous current.4.
Check 430.53
If each motor has adequate thermal protection the requirements of 430.53 will not apply. If 430.53 applies, it might be easier to run a separate branch circuit to each motor.
5.
GFCI Protection
Yes, if the pumps are used in locations where GFCI protection is required (e.g., bathrooms, kitchens, outdoors), the circuit needs GFCI protection. However, GFCI breakers and receptacles are prone to nuisance tripping with motors due to the inrush current. Using a GFCI breaker at the panel is generally preferable to a GFCI receptacle at the point of use.
Example Calculation (Simplified and Hypothetical)
Let's assume you want to try and put both pumps on a single 20A circuit. Each motor has individual overload protection. Total motor load = 14A. No other loads on the circuit.In this simplified case, the continuous load is less than 80% of the breaker rating (16A), so you could use one 20 amp breaker for both. The actual NEC and local building codes may be more complex and require seperate circuits for the motors.
Important Considerations and Recommendations
Inrush Current
Motors draw significantly more current when starting (inrush current or locked-rotor current). This inrush can be 6-8 times the FLA. This is why the NEC allows for larger breakers than the motor's FLA. GFCI breakers are prone to nuisance tripping if the motors are on the same circuit.
Voltage Drop
Running long circuits can cause voltage drop, which can harm motors. Using a larger wire gauge can mitigate this.
Future Expansion
Consider if you might add any other loads to the circuit in the future.
Local Codes
Always check with your local electrical inspector or building department. They may have stricter requirements than the NEC.
Best Practice (Often)
Even if the NEC allows it, it's often best practice to run individual circuits for each motor, especially if they are critical. This provides better reliability and reduces the risk of one motor problem affecting the other.
In summary, you likely can* put both motors on a single 20A circuit if each has individual overload protection, the total load doesn't exceed the circuit's capacity, and the applicable requirements of NEC 430.53 are met, and GFCI protection is provided. HOWEVER, running individual circuits is often the better and safer approach, and you should always consult with a qualified electrician and local codes to ensure compliance.Disclaimer: I am an AI chatbot and cannot provide electrical advice. This information is for educational purposes only and should not be used as a substitute for consulting with a qualified and licensed electrician. Working with electricity can be dangerous, and improper installations can lead to fire, injury, or death. Always follow the NEC and local codes. Flag for review