Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Listing requirements for low voltage power limited circuits and devices

User: tilden, Location: Chapel Hill, NC, USA

Asked on: Saturday, November 23, 2024 at 3:10 pm EST
Answered on: Thursday, March 6, 2025 at 5:36 am EST

Question: I have an AC/DC power supply that's UL listed and outputs max 60W at 24VDC, so below the 100VA max to I believe be considered Class 2 (NEC 2023 Chap. 9 Table 11(B)). If I put this in an enclosure in a building, or outside, do the conductors I'm connecting this 24VDC output need to be "listed" (UL, ETL, etc) if I run them from the enclosure to another piece of equipment (sensors, cameras, etc)?Same question for the powered devices - if a device outside of the enclosure is being fed by this 24VDC source, does it also need to be listed? My take on PoE is that at least the device would need to be listed per 725.160 since power and data are coming in on the same line, but if power is separate from data would it need to be?

Okay, let's break down the NEC requirements for Class 2 circuits and your specific situation, focusing on conductor listing and the listing of powered devices.

Key Concepts: Class 2 Circuits and Listing Class 2 Circuits

These are low-power, limited-energy circuits designed to reduce fire and shock hazards. The NEC (National Electrical Code) provides specific rules for their installation. The 100VA limit (for 30V or less) is a common threshold.


Listing (UL, ETL, etc.)

"Listed" means that a product has been tested by a recognized testing laboratory and found to comply with specific safety standards. The NEC often requires listing for certain components and equipment. However, that's not a universal requirement.

Your Specific Scenario: 24VDC, 60W Power Supply


You're correct that your 24VDC, 60W power supply likely qualifies as a Class 2 power supply based on its voltage and VA rating (below 100VA at 30V or less, as per NEC 2023 Chapter 9 Table 11(B)).

Conductor Listing (Wires Running from Enclosure)

This is where it gets a bit nuanced. Here's the breakdown:

NEC 725.135(A) Class 2 and Class 3 General

This section generally states that Class 2 and Class 3 circuits shall be installed in accordance with 725.3 (Wiring Methods and Materials on Load Side).


NEC 725.3(A)

"The conductors of Class 2 and Class 3 circuits shall be suitable for the particular application and shall be selected in accordance with 725.135."Here's what this typically means in practice:

Inside the Enclosure

Wiring
inside the enclosure should be appropriately rated for the voltage and current. Since the power supply is UL listed, it generally has appropriate wiring already inside.

Outside the Enclosure (to Devices)

This is the critical area. Here's where you need to be most careful. While it is not explicitly stated in article 725.135 that conductors outside the enclosure must be "listed," the conductors still need to be suitable for the application.

Suitable for the Application

This means several things:


Voltage Rating

The conductors must have a voltage rating equal to or greater than the 24VDC.

Ampacity

The conductors must have an ampacity (current-carrying capacity) sufficient for the load. Calculate the current draw of the devices you're powering and choose conductors accordingly. Err on the side of caution and use a slightly higher gauge wire than minimally required.


Environment

Are the wires exposed to sunlight, moisture, extreme temperatures, or physical damage? Choose wire insulation appropriate for the environment. Outdoor-rated cable (e.g., with a "W" designation like THWN) is essential for outdoor applications.

Installation Method

Are the wires run in conduit, cable trays, or open air? The insulation type must be suitable for the installation method.


Physical Protection

If the wires are exposed to physical damage, consider using conduit or other means of protection.

Practical Advice

While not
required to be "listed," using recognized cable types designed for low-voltage power distribution is generally a good idea. Common options include:

CL2 or CL3 Cable

"Class 2" or "Class 3" rated cables are specifically designed and listed for low-voltage, limited-energy circuits. These cables have insulation and construction that meet specific safety requirements. Using CL2/CL3 cable is highly recommended.



CM Cable

This is rated for general communications use, but is typically not for power distribution.


Other Cables

Depending on the specific application, you might be able to use other cable types (e.g., some types of instrumentation cable). Carefully review the cable's specifications to ensure it's suitable for the voltage, current, environment, and installation method.

NM, UF, or other building wire

May not be suitable in some instances due to the low voltage situation, since some of these wires may need to be run in conduit in wet locations.


My Recommendation for Conductors

Use CL2 or CL3 rated cable. It's designed for this type of application, provides a good level of safety and confidence, and demonstrates due diligence.

Listing of Powered Devices (Sensors, Cameras, etc.)

This is also important.

General Rule

The NEC
does not explicitly require all devices connected to a Class 2 circuit to be "listed." However, there are exceptions and strong recommendations.

PoE Considerations (NEC 725.160)

You are correct that if you are using PoE (Power over Ethernet), NEC 725.160 applies. This section does require the equipment connected to the PoE circuit to be listed. This is because PoE combines power and data on the same cable, increasing the risk of fire or shock if the equipment is not properly designed and tested.

Power Separate from Data

If the power and data are separate (e.g., you're running 24VDC power to a camera and then a separate Ethernet cable for data), the NEC's requirement for listing becomes less strict,
but not non-existent.

Prudent Practice and Authority Having Jurisdiction (AHJ)



AHJ Discretion

The final decision on whether a device needs to be listed rests with the local AHJ (electrical inspector). They have the authority to interpret the code and require listing if they deem it necessary for safety.


Manufacturer's Instructions

Always follow the manufacturer's instructions for the devices you are installing. The manufacturer may specify that the device must be powered by a listed power supply or have other specific requirements.

Reasonable Care

Even if the NEC doesn't explicitly require listing, it's always prudent to use listed devices when available. Using listed equipment demonstrates that you have taken reasonable care to ensure the safety of the installation.


Specific Cases



Outdoor Equipment

For outdoor equipment (cameras, sensors, etc.), using devices specifically designed and listed for outdoor use (e.g., UL Listed for wet locations) is highly recommended and may be required by the AHJ. This is especially true for equipment exposed to rain, snow, or other harsh conditions.


Hazardous Locations

If the devices are installed in a hazardous location (e.g., a place with flammable vapors), listing is almost certainly required.

Life Safety Systems

If the devices are part of a life safety system (e.g., fire alarm, emergency lighting), listing is almost certainly required.


My Recommendation for Powered Devices

Use listed devices whenever possible, especially for outdoor applications, hazardous locations, and life safety systems. This demonstrates due diligence and increases the safety of the installation. Even if not explicitly required, it can help avoid issues during inspection.

In Summary


Conductors

Use CL2 or CL3 rated cable for running power from your enclosure to the powered devices. This is the safest and most compliant approach. Ensure the cable is appropriate for the voltage, current, environment, and installation method.2.

Powered Devices

If you're using PoE, the devices must be listed. If power and data are separate, prioritize using listed devices whenever possible, especially for outdoor and hazardous locations. Be prepared to justify your choices to the AHJ.3.

Always Consult the AHJ

Before starting any electrical work, consult with your local AHJ to ensure that your installation meets all applicable requirements. They have the final say.4.

Follow Manufacturer's Instructions:
Always adhere to the device manufacturer's instructions for power supply requirements.This is a complex area, and the specific requirements can vary depending on your local jurisdiction and the specific application. Consulting with a qualified electrician or electrical engineer is always a good idea to ensure that your installation is safe and compliant with all applicable codes and regulations. Flag for review

Previous Question Next Question