User: sparkybkc, Location: Kansas
Asked on: Sunday, November 24, 2024 at 8:01 am EST
Answered on: Thursday, March 6, 2025 at 5:36 am EST
Question: 2 part question1. What are the names of the ground rods if you drive 2 rodsFor example 1st rod primary and 2nd rod supplemental2nd question no ufer available, plastic water pipe, no building steelAre 2 ground rods considered a complete grounding systemThanks
Here are the answers to your questions:1. Ground Rod Names
There isn't a formally recognized naming convention like "primary" and "supplemental" in electrical codes or standards for ground rods in a two-rod system. They are simply referred to as
grounding electrodes. You can think of them as: First ground rod
The first rod installed.
Second ground rod
The second rod installed to meet the 25-ohm resistance requirement.2.
Ground Rods as a Complete Grounding System
No, two ground rods are not generally considered a complete grounding system on their own under the conditions you describe (no Ufer, plastic water pipe, no building steel). Here's why: NEC Requirements
The National Electrical Code (NEC) specifies a grounding electrode system. This system is intended to provide a low-impedance path to earth for fault current, helping to clear faults quickly and safely. The code prioritizes certain types of grounding electrodes.
Prioritized Electrodes
The NEC lists these grounding electrodes (in a hierarchy/order of preference, though the exact order and allowed combinations can depend on the edition of the NEC and local amendments): Metal underground water pipe in direct contact with the earth for 10 feet or more (meeting specific requirements) Building steel (the metal frame of the building, again meeting specific requirements) Concrete-encased electrode (Ufer ground) Ground ring Rod, pipe, and plate electrodes (your ground rods) Other listed electrodes.
Supplemental Electrode Required
If you don't have any of the better grounding electrodes (metal water pipe, building steel, Ufer),
you MUST supplement your rod, pipe, or plate electrode with an additional electrode as described in NEC 250.53(A). This is very important. The second rod fulfills this supplemental requirement, but it doesn't mean the system is now "complete" in the sense of being ideal or optimal. 25 Ohms or Less
The NEC also states that a single rod, pipe or plate electrode must have a resistance to ground of 25 ohms or less. If you cannot achieve 25 ohms with a single rod, then you drive a second rod. The second rod MUST be separated from the first rod by at least 6 feet (250.53(B)). Even with the second rod, the Code suggests supplementary electrodes if resistance is an issue.
Situation Matters
While two ground rods may meet the minimum requirements of the NEC in your scenario, it's not necessarily the best or safest grounding system. A more robust grounding system might be desired, particularly in areas with poor soil conductivity.
In Summary
Two ground rods can satisfy the minimum requirements when other preferred electrodes are not present. However, they are not necessarily a complete or ideal grounding system, and the overall effectiveness depends heavily on soil conditions. You still need to follow the rules of separation and wire size, and in some areas, more robust grounding may be needed.
Important Considerations
Local Codes
Always check your local electrical codes and ordinances, as they may have stricter requirements than the NEC.*
Qualified Electrician: A qualified electrician should perform the grounding system installation to ensure it meets all applicable codes and standards and is safe and effective. They can also measure the resistance to ground to ensure proper performance. Flag for review