Question: I found and old thread from 2017 on this, but did not have definitive answer. When installing multiple runs of NM Cable in a wall cavity, is there a specific requirement in the 2023 NEC on any max adjacent cables, or min spacing? Whether using staples with multiple cables beneath or the stackers that are available, in certain situations it seems unavoidable to have as many as 3 to 6 cables running up the same 2x in contact with each other in the wall that need to be secured. Article 334.80 specifies derating for two or more cables in contact with each other while in contact with insulation, caulk, or foam, but I don't see anything for derating in the absence of insulation, caulk, or foam. If no hard requirement, what is best practice?

You're correct, the 2017 information might be outdated, and the topic of NM cable bundling and spacing is still frequently discussed. Let's break down the 2023 NEC requirements and best practices.

NEC 2023 Requirements



Article 334.80 Ampacity

This is the core of the issue. As you noted, it specifically addresses the derating of NM cable when:


Two or More Cables in Contact

"Where more than two NM cables containing two or more current-carrying conductors are installed in contact with thermal insulation, caulk, or sealing foam without maintaining spacing between cables, the allowable ampacity of each conductor shall be adjusted in accordance with Table 310.15(C)(1)."

No Requirement for Spacing in Open Air

The NEC
does not mandate a specific spacing between NM cables in open air within a wall cavity, provided they are not in contact with thermal insulation, caulk, or sealing foam. This is a critical point.

Support

NM cables must be supported according to 334.30. This includes: Securing every 4 1/2 feet. Within 12 inches of boxes, cabinets, and fittings. Straps and staples designed not to damage the cable.

Understanding the Nuances



Thermal Insulation, Caulk, and Sealing Foam are Key

The ampacity derating rules only apply when the cables are in contact with those specific materials. The concern is heat buildup due to the insulating properties.

"Bundling" vs. "Contact"

The NEC doesn't specifically use the term "bundling" in this context. The crucial factor is whether the cables are "in contact with thermal insulation, caulk, or sealing foam." If they are, then you apply the derating.

Best Practices (Even Though Not Mandated by Code in Open Air)

While the NEC
doesn't require spacing in open air, common sense and good workmanship dictate the following:1.

Minimize Bundling

As a general rule, avoid unnecessarily tight bundles of NM cables, even in open air. Even without insulation, a large bundle can still retain some heat.2.

Spread Cables Out

If you have multiple runs, try to distribute them as much as practically possible within the wall cavity. Use longer staples, or stackers to accomplish this.3.

Consider the Load

If the cables are carrying heavy loads (e.g., powering multiple high-draw appliances), be even more mindful of potential heat buildup.4.

Avoid Completely Enclosed Spaces

Avoid running multiple NM cables through tightly enclosed spaces within the wall (e.g., small holes drilled through studs) if possible.5.

Derating (If in Doubt)

If you're unsure about whether the cables might come into contact with insulation later (e.g., during future renovations), or if you're running a large number of high-current circuits, it's always safer to err on the side of caution and derate the conductors.6.

Proper Stapling

Use cable staples that are designed for NM cable and do not damage the outer jacket. Don't over-tighten staples, as this can damage the conductors inside. Use stacker staples when running multiple cable.

In your scenario of 3-6 cables secured to a 2x stud

If the cables are running in open air, not touching insulation, caulk, or foam, the NEC does not require derating. However, consider the best practices above. If you're dealing with high loads, distributing the cables more evenly is preferable. Use cable stackers instead of staples to secure the cable.

Example

Let's say you have six 12 AWG NM cables (rated for 30 amps) running through a wall cavity to supply general-purpose lighting and receptacle circuits. The cables are not touching insulation, caulk, or sealing foam.

NEC Requirement

No derating is
required.

Best Practice

You could spread the cables out, but as long as they're in open air and not in contact with insulating materials, it's acceptable.

Important Disclaimer:


Always consult with your local electrical inspector for clarification on specific requirements in your jurisdiction. Local codes can sometimes be more stringent than the NEC.In summary, while the 2023 NEC doesn't mandate spacing between NM cables in open air, applying best practices to minimize bundling and promote airflow is always a good idea, especially with high-current circuits. The derating rules of 334.80 are strictly tied to contact with thermal insulation, caulk, or sealing foam. Flag for review