Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 10' tap or not

User: mannyb, Location: Florida

Asked on: Monday, November 25, 2024 at 7:39 pm EST
Answered on: Thursday, March 6, 2025 at 5:39 am EST

Question: Installing Service rated ATS 277480v. The generator requires a 120v circuit and 240v heater circuit. They want to put xfmr close to ATS for tap and then add a small load center for the 2 breakers supplying gfci and heater. If we install a 15kva XFMR outside, What specific rules do we follow for installing the XFMR? Would I follow 240.21 b5? Or 240.21 B1? I would put breaker on primary side of xfmr and put MLO load center on secondary side? What am I missing?

Okay, let's break down the code requirements for installing a 15kVA transformer to derive 120V and 240V from a 277/480V service, specifically for supplying a generator associated with a service-rated Automatic Transfer Switch (ATS).

Understanding the Situation Service-Rated ATS

This means the ATS is directly connected to the utility service entrance.


277/480V Input

Your primary source is 277/480V.

120V and 240V Output Needed

You need to create 120V for a GFCI receptacle (likely for maintenance or convenience) and 240V for a heater (presumably a generator block heater or similar).


Remote Transformer

The plan is to place a 15kVA transformer near the ATS to step down the voltage and then feed a small load center.

Key NEC Considerations
1. Transformer Location (Outdoor)



Suitable for Outdoor Use

The transformer
must be listed and labeled for outdoor use (NEMA 3R or higher enclosure is typical).

Physical Protection

Consider its location to prevent damage from vehicles, weather, or vandalism. You might need bollards or a protective enclosure.

Working Clearance

Maintain proper working clearances around the transformer for maintenance and inspection (NEC 110.26).


Mounting

Properly mount the transformer according to its listing and the manufacturer's instructions. This usually involves a concrete pad or a secure wall mount.

Accessibility

Ensure the transformer is accessible for inspection and maintenance.2.

Overcurrent Protection



Primary Protection

Required on the primary (480V) side of the transformer. This is usually a circuit breaker. You'll need to calculate the primary full-load amps (FLA) of the transformer and size the breaker accordingly.

Secondary Protection

Required on the secondary (120/240V) side. You'll be using a load center, so the individual branch circuits (GFCI receptacle and heater) will be protected by breakers in that load center.

Transformer Overcurrent Protection (NEC 450.3)

Crucially, the primary and secondary overcurrent devices must comply with NEC 450.3. This section dictates the maximum allowable overcurrent protection based on the transformer's impedance and other factors. Typically, primary overcurrent protection can be up to 125% of the transformer's primary rated current, and secondary protection can be up to 125% of the transformer's secondary rated current. Consult NEC 450.3 directly for specific details, as it's very important to get this right.3.

Wiring Methods



Raceway

Use appropriate raceway (rigid conduit, EMT, etc.) for all wiring to and from the transformer. Outdoor installations require weather-tight fittings.


Conductors

Use conductors with the appropriate ampacity and insulation rating for the voltage and environment (THHN/THWN is common).

Grounding

Proper grounding is essential for safety.


Equipment Grounding Conductor (EGC)

Run an EGC with all circuit conductors to ground the transformer enclosure and the load center enclosure.

Separately Derived System (SDS) Grounding (NEC 250.30)

Because this transformer is stepping down the voltage to supply downstream loads, it is considered a Separately Derived System (SDS). You must establish a grounding electrode system for the secondary side of the transformer. This usually involves connecting the neutral (X0) of the transformer secondary to a grounding electrode (ground rod, building steel, etc.) at the transformer location. NEC 250.30 provides detailed requirements.
4.


Overcurrent Protection Tap Rules (NEC 240.21)



This is where you'll be asking about 240.21 B1 or B5...
NEC 240.21(B) outlines the conditions under which you can tap conductors without overcurrent protection at their point of supply. These rules permit conductor taps of a certain length without OCPD at the tap point. Crucially, the requirements of 240.21(B)(1)-(B)(5) are not required if the OCPD is within sight and is rated less than the ampacity of the conductor. In your scenario, you should be using 240.21(C)(1) because you are feeding a Transformer Secondary. The conductors from the secondary side of the transformer to the panelboard or other equipment must be protected from overcurrent at the termination of the conductors.5. Separately Derived System (SDS)

Since your transformer provides 120V and 240V from a 480V source, it creates a Separately Derived System (SDS). NEC Article 250 covers the grounding and bonding requirements for SDS.

Bonding Jumper (NEC 250.30(A)(1)

A bonding jumper is installed from the transformer secondary neutral point (X0) to the transformer enclosure.

Grounding Electrode Conductor (GEC) (NEC 250.30(A)(2)

A grounding electrode conductor is installed from the transformer enclosure or the neutral bonding point to a suitable grounding electrode (ground rod, building steel, etc.).6.

Calculations



Transformer FLA

Calculate the full-load amps on both the primary (480V) and secondary (120/240V) sides of the transformer. `FLA = kVA / (Voltage x 1.732)` for three-phase (480V) `FLA = kVA / Voltage` for single-phase (120V and 240V). Remember to account for the fact that you have both 120v and 240v loads.

Conductor Ampacity

Select conductors with an ampacity at least equal to 125% of the continuous load, plus the non-continuous load.


Overcurrent Device Sizing

Size the primary and secondary overcurrent devices according to NEC 450.3, but never exceed the conductor ampacity.

Step-by-Step Installation (Simplified)
1. Mount the Transformer

Securely mount the outdoor-rated transformer on a pad or wall, ensuring proper clearances.2.

Primary Wiring (480V)

Run conduit from the ATS enclosure to the transformer. Install a properly sized circuit breaker in the ATS enclosure to protect the transformer primary. Connect the primary conductors (with EGC) from the breaker to the transformer primary terminals.3.

Secondary Wiring (120/240V)

Run conduit from the transformer to the load center. Connect the secondary conductors (with EGC) from the transformer to the load center's main lugs.4.

Grounding

Install the bonding jumper from the transformer secondary neutral (X0) to the transformer enclosure. Install the grounding electrode conductor (GEC) from the transformer enclosure (or the neutral bonding point) to the grounding electrode.5.

Load Center Wiring

Install breakers in the load center for the 120V GFCI receptacle circuit and the 240V heater circuit. Wire the receptacle and heater to their respective breakers.

What You Might Be Missing
Local Codes and Permits

Always check with your local electrical inspector for any specific requirements or interpretations of the NEC in your jurisdiction. Permits are almost certainly required for this type of installation.

Coordination with Generator and ATS Controls

Ensure the transformer and wiring do not interfere with the generator's control circuits or the ATS's operation.


Short-Circuit Current Rating (SCCR)

Ensure the transformer, load center, and all connected equipment have a short-circuit current rating (SCCR) sufficient to withstand the available fault current at the installation location.

Voltage Drop

Calculate voltage drop, especially on the 120V circuit, to ensure adequate voltage at the receptacle.

Important Notes
This is a simplified explanation. Electrical work is dangerous and should only be performed by qualified electricians who are thoroughly familiar with the NEC and local codes. Always consult the manufacturer's installation instructions for all equipment (transformer, ATS, generator, load center). Double-check all calculations and grounding/bonding connections.* Have the installation inspected by a qualified electrical inspector before energizing the system.

This detailed explanation should give you a solid foundation for understanding the code requirements for installing the transformer. However, it is not a substitute for the NEC or the advice of a qualified electrician. Please be careful and stay safe! Flag for review

Previous Question Next Question