User: Ohm2, Location: Washington
Asked on: Tuesday, November 26, 2024 at 3:22 am EST
Answered on: Thursday, March 6, 2025 at 5:40 am EST
Question: Ok this site has two triplex buildings. Both buildings have a ufer (rebar is 1/2in). Building 1 has the service ( 600a) and hits the ufer with a #4cu—then each unit has a #4cu to an accessible ufer. Building 1 serves the detached tri-plex ( building 2) with 1/0 1/0 2Al with a #6 EGC. Building 2 has access to the ufer ( rebar is 1/2 in) in each unit ( same as building 1). What size GEC shall be installed from the non-serviced rated panel to the ufer. Do we use T250.66 based on the largest ungrounded conductor or is it going to be a min number 4cu per 250.52(A)3. Or am I thinking too much
Okay, let's break down the grounding electrode conductor (GEC) requirements for the second triplex (Building 2), considering the scenario you've described.Here's the relevant information and considerations: Building 1 (Service Building)
600A Service Ufer ground connected with #4 CU Individual units also have #4 CU to accessible Ufer (likely local to that unit)
Building 2 (Remote Building)
Fed from Building 1 with 1/0-1/0-2 AL with #6 CU EGC Each unit has access to an Ufer ground (1/2" rebar)
Question
What size GEC is needed from the non-service rated panel in Building 2 to the Ufer ground?
Analysis1. Understanding the Ufer Ground
A Ufer ground (concrete-encased electrode) is a grounding electrode per NEC 250.52(A)(3). Since Building 2 already has a Ufer, it's essential to properly connect the panel to it.2.
Remote Building Considerations
Building 2 is a separate building fed from Building 1. This means we must establish a grounding electrode system at Building 2, as outlined in NEC 250.32. This is because it has its own Ufer grounds. This is true even though Building 1 has its own ufer.
3.
NEC 250.32(A) - Grounding Electrode Required
Since Building 2 is a separate building and contains branch circuits, 250.32(A) mandates a grounding electrode system. A Ufer ground is an acceptable grounding electrode.4.
Sizing the GEC to the Ufer at Building 2 (NEC 250.32(B))
NEC 250.32(B) says that the grounding electrode conductor at the remote building is sized based on 250.66, based on the size of the ungrounded conductors that supply the building. The ungrounded conductors feeding building 2 are the two 1/0 Al conductors. Table 250.66 requires a #6 Cu.
Therefore
The GEC from the non-service rated panel in Building 2 to the Ufer ground needs to be a minimum of #6 CU.Why not #4 CU based on 250.52(A)(3)?
While 250.52(A)(3) does specify a minimum size of #4 CU for the portion of the GEC that is the sole connection to a concrete-encased electrode, this only applies to the electrode itself. 250.32(B) sends us to 250.66 to determine the size of the GEC based on the conductors feeding the building, which in this case is smaller than the minimum dictated in 250.52(A)(3).
Important Considerations and Best Practices
Accessibility
Ensure the connection to the Ufer is accessible for inspection and testing (as much as practically possible).
Local Ufers for Each Unit
The fact that each unit has access to a Ufer is a beneficial design. It likely improves grounding within each unit.
Continuity
Verify the integrity and continuity of the Ufer rebar system during construction.*
Existing #6 ECG to building 2. Is the #6 being used to connect the EGC to the electrode system at the remote building? If so you need to upsize to #6, as per 250.32(B).
In summary, comply with NEC 250.32. Base the GEC sizing to the Ufer at Building 2 on the size of the ungrounded conductors feeding Building 2 using Table 250.
66. Upsize the #6 EGC coming from building 1 to #6 to connect to the electrode system at the remote building. Flag for review