Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Switch / circuit breaker that opens and remains open during loss of power

User: Benihana, Location: Suffolk County, NY

Asked on: Tuesday, November 26, 2024 at 11:06 am EST
Answered on: Thursday, March 6, 2025 at 5:41 am EST

Question: I am working on a project that requires a set of modules of a chiller to be de-energized during a loss of power and remain OFF until it is manually reset. Does anybody know what I could use to accomplish this? (note this set of modules will have it's own source of power)

Okay, this is a common requirement in critical systems to prevent equipment from automatically restarting after a power outage, which could cause safety issues, surges, or process disruptions. You're essentially looking for a latching relay/contactor-based system with undervoltage detection and manual reset. Here's a breakdown of components and how they would work together

Core Components:

1. Undervoltage Relay (UVR) or Undervoltage Release (UV Release)

This is the heart of your system. It monitors the voltage of your incoming power source. When the voltage drops below a pre-set threshold (indicating a power loss), it triggers a change in state.

Key Features for Choosing UVR/UV Release



Adjustable Trip Voltage

You want to be able to set the voltage level at which it trips (e.g., 85% of nominal voltage).

Adjustable Trip Delay (Optional)

A short delay can prevent nuisance tripping from brief voltage sags. Be cautious about adding
too much delay; you want it to react reliably to a true power loss.

Reset Mechanism

This is crucial. You'll need a UVR/UV Release that has a manual reset capability. This means it won't automatically re-energize when power returns.

Contact Rating

The contacts on the UVR need to be able to handle the control voltage/current required by the contactor(s) or relay(s) you'll be using to de-energize your chiller modules.


Voltage Range

Make sure the UVR is compatible with the voltage of your power source.

Mounting

DIN rail mounting is common.2.

Latching Contactor or Latching Relay

This is what actually cuts power to your chiller modules. A standard contactor will drop out when power is lost. A
latching contactor, however, stays in its last state (either ON or OFF) even without power applied to its coil. It requires a separate pulse to either SET (turn ON) or RESET (turn OFF).

Key Features for Choosing Latching Contactor/Relay



Voltage and Current Rating

This MUST be appropriate for the voltage and current requirements of your chiller modules. Oversize it slightly for safety margin.


Contact Configuration

Choose the number of normally open (NO) and normally closed (NC) contacts you need. Typically, you'll use NO contacts in series with the power supply to your modules.

Coil Voltage

The coil voltage must match the voltage of your control circuit (which could be different from the main power voltage).


Latching Type

There are different types of latching contactors. Some require separate SET and RESET coils, while others use a single coil with alternating polarity.

Manual Override (Optional but Recommended)

Some latching contactors have a manual override that allows you to manually switch the contactor on or off for testing or maintenance.3.

Manual Reset Pushbutton

This is how you will re-energize the chiller modules after a power loss. It will be wired into the latching contactor's control circuit to provide the RESET pulse.4.

Control Power Supply (If Needed)

If your UVR and/or latching contactor/relay operate on a different voltage than your main power, you'll need a dedicated control power supply (e.g., 24VDC, 120VAC). This supply should ideally be separate from the chiller module power supply.5.

Enclosure

A suitable enclosure to house all the components, protect them from the environment, and provide safety.6.

Wiring and Connections

Properly sized wiring, terminal blocks, and other connection hardware. Use appropriate wire gauges for the current being carried.

How It Works


Normal Operation

The UVR monitors the incoming power. As long as the voltage is within the acceptable range, its contacts are in the "normal" state. This allows power to flow to the latching contactor's SET coil (either directly or through an interlock/enable circuit). The latching contactor is in the ON state, supplying power to your chiller modules.2.

Power Loss

When a power loss occurs, the voltage drops below the UVR's setpoint. The UVR's contacts change state, interrupting power to the latching contactor's SET coil. Because it's a
latching contactor, it remains in the ON state momentarily (until its internal capacitor discharges, or the reset is triggered), but it is now prevented from automatically re-energizing.3.

Manual Reset

After the power is restored and any necessary safety checks are completed, you press the manual reset pushbutton. This sends a pulse to the latching contactor's RESET coil, switching it to the OFF state and cutting power to the chiller modules.4.

Re-Energizing

To re-energize the chiller modules, you press the manual START/ON button. The UVR is monitoring the source, and if all conditions are correct, it will allow the Latching Contactor to energize and supply the chiller modules.

Wiring Diagram (Conceptual)

+-----------------+|   Power Source  |+--------+--------+
+--------v--------+| Undervoltage
Relay (UVR)
(Normally Open) |+--------+--------+| (Healthy Voltage, UVR Closed)|+--------v--------+| Manual Start
Pushbutton |+--------+--------+| (Start Button Pressed)|+--------v--------+| Latching
Contactor/Relay
(SET Coil) |+--------+--------+|+-------------------------------------+| | (Contactor/Relay Main Contacts)v |+--------+--------+ +--------v--------+| RESET | | | Chiller ||Button +--------+---------->| Modules |+--------+ | (Load) |+-----------------+


Important Considerations and Best Practices



Safety Interlocks

Incorporate additional safety interlocks into the control circuit if needed (e.g., over-temperature sensors, pressure switches, etc.). These should prevent the chiller modules from starting if any unsafe conditions exist.

Emergency Stop

Include an emergency stop (E-Stop) button that, when pressed, immediately de-energizes the latching contactor.


Documentation

Create a clear and detailed wiring diagram. Label all components clearly.

Testing

Thoroughly test the system after installation to ensure it functions as intended. Simulate power outages to verify the UVR and latching contactor operate correctly.


Codes and Standards

Ensure that your design complies with all applicable electrical codes and safety standards (e.g., NEC, IEC).

Professional Installation

Have a qualified electrician install and test the system.


Redundancy

For critical applications, consider redundant UVRs and latching contactors for increased reliability.

Example Components (for Illustration Only - Verify Specs!)



Undervoltage Relay

ABB CM-UFD.11, Eaton UVR series, Schneider Electric RM22TG series.


Latching Contactor

Eaton XTML series, ABB AF series with latching blocks, Schneider Electric TeSys D series with latching blocks.

Important Disclaimer:
I am an AI chatbot and cannot provide professional engineering or electrical design advice. The information above is for general guidance only. Consult with qualified professionals for your specific application. Electrical work can be dangerous, and improper design or installation can lead to serious injury or death. Flag for review

Previous Question Next Question