Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 62.5 hz output from generator.

User: Crash117, Location: Nevada

Asked on: Tuesday, November 26, 2024 at 1:32 pm EST
Answered on: Thursday, March 6, 2025 at 5:42 am EST

Question: I was called to job today to help try and figure out why the customer’s Mitsubishi heat pump ducted system would not run on his 9600 watt generator. He has this connected to a proper transfer switch and under normal utility power it runs perfectly. Recently during a power outage he transferred over to his generator but the unit would heat pump would not run. Upon inspection the generator was giving an output of normal voltage but 62.5 hz according to the display on the generator. This was also confirmed by a surge protector unit he has which has a digital readout on it which showed 62.5 hz from generator. I’m not very familiar with the inner workings of the Mitsubishi units but told him that the frequency variation is most likely the cause of his trouble and to have the generator serviced to see if there are changes that can be to make it proper 60hz. Also recommend that to ensure it doesn’t cause trouble on other items he runs off of generator. Can anyone share any info on the workings of a Mitsubishi heat pump unit and how it could be affected by the frequency difference. TIA!

You're on the right track. The frequency difference is almost certainly the culprit. Here's a breakdown of why, and some additional info for your customer

Why 62.5 Hz Matters to a Mitsubishi Heat Pump (and other sensitive electronics):
Variable Frequency Drives (VFDs)

Modern heat pumps, especially Mitsubishi's, are heavily reliant on VFDs to control the compressor and fan motors. These VFDs are designed to operate within a specific frequency range (very close to 60 Hz in North America). They convert the AC power into DC and then back into AC at a
controlled frequency to precisely manage motor speed.

Frequency Sensitivity

VFDs have built-in protection mechanisms. Operating outside of the acceptable frequency range can trigger these protections.

Damage

Exceeding the acceptable frequency range can lead to component failure within the VFD. Capacitors, semiconductors, and other sensitive components can be stressed or even destroyed.


Harmonic Distortion

A generator operating off-frequency often introduces more harmonic distortion into the power supply. VFDs are sensitive to harmonic distortion, which can also cause them to malfunction or shut down.

Synchronous Motors and Timing

Older or simpler equipment might rely directly on the 60 Hz AC signal for timing. While less likely in a modern heat pump, subtle timing issues could manifest as inefficient operation or control problems.


Control Boards/Microprocessors

The control boards in these units rely on precise timing. A stable frequency is essential for them to function correctly. Even if the VFD could tolerate the higher frequency to some extent, the control board might misinterpret signals or fail to initiate the correct start-up sequence.

Why the Heat Pump Runs Fine on Utility Power (and not the generator)



Stable Frequency

The utility grid is exceptionally stable in terms of frequency. It's maintained within a very tight tolerance of 60 Hz (or 50 Hz in other regions).


Clean Power

Utility power is generally "cleaner" than generator power, meaning it has less harmonic distortion and fewer voltage fluctuations.

Troubleshooting Considerations and Recommendations for Your Customer


Generator Service is Essential

Your initial recommendation is spot-on. The generator must be serviced and adjusted to produce a stable 60 Hz output under load.

Technician Expertise

The service technician needs to understand that the generator is being used for sensitive electronics (like a heat pump). They should use a calibrated frequency meter to verify the output under different load conditions.


Load Testing

The generator should be tested with a load similar to the heat pump's expected power draw. Frequency often drifts as the load changes.2.

Generator Type Matters



Inverter Generators

Inverter generators are
generally better for powering sensitive electronics. They produce DC power and then use an inverter to create clean, stable AC power at the correct frequency, regardless of engine speed. If his current generator is NOT an inverter generator, he might consider upgrading to one.

Conventional Generators

Conventional generators are directly tied to engine speed. Maintaining a stable frequency is more challenging, especially under varying loads.3.

Consider a Power Conditioner/UPS

If, after generator service, the frequency is still not perfectly stable, a high-quality power conditioner or uninterruptible power supply (UPS) could be used between the generator and the heat pump.

Online Double Conversion UPS

This type provides the cleanest power and regulates both voltage and frequency. It's the best option but also the most expensive.4.

Soft Start Kit

A heat pump's compressor requires a large inrush of current when starting. This can further destabilize a generator. Installing a "soft start" kit on the heat pump can reduce the inrush current, making it easier for the generator to handle the load. (Though the frequency is most likely the main problem, this is always a good consideration on generator power.)5.

Check Generator Capacity (Again)

While the generator is rated at 9600 watts, make sure that's
running watts, not just starting watts. A heat pump can have a high starting wattage demand. Confirm that the generator has enough capacity to handle the heat pump's full load plus* any other essential loads he plans to run simultaneously.6.

Voltage Regulation

Have the generator's voltage regulation checked along with the frequency. Unstable voltage can also cause problems with VFDs and other electronics.

In Summary:


The 62.5 Hz output from the generator is very likely the root cause. Focus on getting the generator properly serviced and adjusted to deliver stable 60 Hz power. Consider the other points above to ensure reliable operation in the future. Flag for review

Previous Question Next Question