Topic: Dedicated electrical space

User: Grouch1980, Location: New York, NY

Asked on: Tuesday, November 26, 2024 at 2:37 pm EST
Answered on: Thursday, March 6, 2025 at 5:42 am EST

Question: Dedicated electrical space is required, per 110.26(E), above switchboards, switchgear, panelboards, and motor control centers. I believe the answer is no, but does this apply to meter centers?

You're right to be cautious and double-check, but your initial instinct is generally correct.

No, dedicated electrical space, as defined in 110.26(E), typically does not apply to meter centers.

Here's the breakdown of why: Definition of Equipment Covered by 110.26(E)

110.26(E) is very specific in its language. It applies to

switchboards, switchgear, panelboards, and motor control centers.
A meter center doesn't cleanly fall into any of those categories.
Function of Meter Centers

Meter centers primarily house utility-owned metering equipment. While they do distribute power to individual tenant spaces or units, their primary function is measurement and revenue tracking, not switching, overcurrent protection, or motor control.

Intent of Dedicated Space

The dedicated space requirements in 110.26(E) are intended to ensure:


Accessibility for maintenance and repairs

Electricians and qualified personnel need clear, unobstructed access to the equipment for safe working conditions.

Protection of the equipment

Preventing foreign objects or other systems (e.g., plumbing, HVAC) from interfering with the electrical equipment's operation or posing a safety hazard.


Specific Code sections

If the meter center contains any equipment that is covered in the equipment list of 110.26(E) then that area would need to be covered.

Important Considerations and Caveats



Local Amendments

Always check with the local authority having jurisdiction (AHJ). Some jurisdictions may have amended the NEC or have local codes that apply similar dedicated space requirements to meter centers.


Physical Size and Complexity

A large, complex meter center might de facto require some degree of clear space for practical access and maintenance, even if not strictly dictated by 110.26(E).

Manufacturer's Instructions

The manufacturer of the meter center might specify required clearances in their installation instructions. These should always be followed.


Good Electrical Practice

Even if not strictly required, it's always good practice to provide some reasonable clear space around any electrical equipment to facilitate maintenance and safe operation. Avoid running unrelated piping or ductwork directly in front of or above the meter center if possible.

In summary:
While 110.26(E) as written does not apply to meter centers, always check with your local AHJ and consider practical accessibility and safety when installing them. It's better to err on the side of providing adequate clear space. Flag for review