Question: I just failed an inspection because the inspector did not see the Amps on my labelhere is the label ,(Some context PV system needed to de-rate main breaker in order to comply with 120% rule. Load calc allow it )The new main breaker has the amps , the panel label has the Amps of the old Breaker .It is necessary to write down on the label ........" we de-rate from ___ Amps to _____ Amps?
Yes, you absolutely need to update the label to reflect the change in main breaker amperage due to the PV system. The inspector is correct to fail you on this.Here's why and how to fix it
Why It's Required (and why the inspector failed you):
Safety
The main breaker is the primary overcurrent protection for the entire electrical panel. Knowing its amperage is crucial for anyone working on the system (including future owners, electricians, or inspectors). Incorrect labeling can lead to dangerous assumptions about the panel's capacity.
Code Compliance (NEC 705.12 and 705.12(B)(2)(3)
The National Electrical Code (NEC) Article 705, specifically addresses interconnected power sources, like solar PV. Section 705.12(B)(2)(3) requires clear and permanent labeling of the main breaker derating. This is directly tied to the 120% rule you mentioned.
120% Rule
This rule allows the sum of the breaker feeding the bus bar to be 120% of the bus bar rating if you install a PV system.
What You Need to Write on the Label
The label must clearly and permanently state the following:
"WARNING: INVERTER OUTPUT CONNECTION" (This is a standard header often used) "MAIN BREAKER DERATED FROM [Original Amperage] AMPS TO [New Amperage] AMPS DUE TO SOLAR PV SYSTEM" "(Maximum Backfeed Breaker Size) [Amperage] Amps" Date of Modification Name of the Person/Company performing the ModificationExample
Let's say your original main breaker was 200 amps, and you derated it to 150 amps. And you PV backfeed breaker is 20 Amps. Your label would look something like this:WARNING: INVERTER OUTPUT CONNECTIONMAIN BREAKER DERATED FROM 200 AMPS TO 150 AMPS DUE TO SOLAR PV SYSTEM(Maximum Backfeed Breaker Size) 20 AmpsDATE: 2024-10-27MODIFIED BY: [Your Name/Company Name]
Important Considerations
Permanence
The label needs to be permanent. That means it should be printed on durable material that won't fade, peel, or become illegible over time. Use a proper label maker that prints on suitable material or have a professional electrical supply company create one for you.
Location
The label must be placed in a conspicuous location, usually directly adjacent to the main breaker and readily visible.
Legibility
The text must be clear, easy to read, and of an appropriate size.
Professionalism
A handwritten label is generally not acceptable. It gives the impression of being unprofessional and potentially unreliable.*
Inform inspector first It is important to inform the inspector that you intend to correct it so that you can avoid future delaysIn Summary:
The inspector's concern is valid and necessary. Update the label on your electrical panel with the correct information about the main breaker derating. This ensures the safety and accuracy of your electrical system and complies with the NEC. Flag for review