User: Allegiantelectrical, Location: Menifee
Asked on: Wednesday, November 27, 2024 at 1:00 am EST
Answered on: Thursday, March 6, 2025 at 5:43 am EST
Question: Currently quoting a job installing 8 light poles with (12) 150W light fixtures on each pole.The runs will be fed from two different 480V sources. (4 light poles on one panel and 4 light poles on the other panel)Just wanting to double check my load calc & conduit fill.1. Am I right to assume 150W x 12 = 1800W/ 480V = 3.75A at each light pole? If so that means 15A total current on that circuit.2. With a distance to the furthest pole at 1353’ I should run 4AWG.3. (5) 4AWG in schedule 40 PVC means I should run 1 1/4” conduit?4. With a load of 3.75 A at each pole I could run #12 or #10 up each light pole?Thanks in advance!
Okay, let's break down your calculations and address each point.1. Amperage Calculation
Per Fixture
150W / 480V = 0.3125A per fixture. Your initial calculation of 3.75A is incorrect.
Per Pole
0.3125A/fixture 12 fixtures = 3.75A per pole. This is the 3.75A figure you arrived at.
Total Circuit Load
3.75A/pole 4 poles = 15A per circuit.
This part is correct, your total circuit load will be 15A.2. Wire Size (Voltage Drop and Ampacity)
This is where it gets more complex, and voltage drop becomes very important over that distance.
Ampacity
4 AWG copper is rated for 85A (75°C column - assuming terminations are rated for 75C). 15A is well within the ampacity of 4 AWG.
Voltage Drop
This is the crucial factor. Let's calculate the voltage drop for a 15A load over 1353 feet, using 4 AWG copper. You'll need a voltage drop calculator (easily found online) or the formula:VD = (2 K I D) / CMWhere: VD = Voltage Drop (in volts) K = Copper constant (12.9 for copper) I = Current (15A) D = Distance (one-way, in feet, so 1353 ft) CM = Circular Mils of the conductor (4 AWG is approximately 41,740 CM)VD = (2 12.9 15 1353) / 41740 = 12.54 VoltsPercentage Voltage Drop = (Voltage Drop / Source Voltage) 100Percentage Voltage Drop = (12.54 / 480) 100 = 2.61%Typically, you want to keep voltage drop below 3% for branch circuits and 5% for feeders.
Your voltage drop is acceptable with 4 AWG.3. Conduit Fill
You said (5) 4 AWG wires, but you only need 3 wires. So for (3) 4 AWG you would only need 1" conduit
4. Wiring to Each Light Fixture
Ampacity
#12 AWG is typically rated for 20A, and #10 AWG is rated for 30A (check your local codes and termination temperature ratings). 3.75A is well within the ampacity of either.
Voltage Drop
The distance from the base of the pole to the topmost fixture is likely relatively short. Voltage drop will not be a significant factor here.
Therefore, #12 AWG or #10 AWG is acceptable for wiring up each light pole.Important Considerations & Recommendations
Overcurrent Protection
Make sure your overcurrent protection (circuit breaker) is sized appropriately for the conductor ampacity and the connected load. A 20A breaker would be appropriate for a 15A load using #12 AWG.
Grounding
Ensure proper grounding conductors are installed throughout the system. A separate equipment grounding conductor (EGC) should be run with the circuit conductors. Size the EGC according to the overcurrent protection device.
Local Codes
ALWAYS consult and adhere to all applicable local codes and regulations. The NEC is a guideline, but local jurisdictions may have amendments or specific requirements.
Fixtures
Verify the actual wattage and voltage requirements of the fixtures you are using. Manufacturer specifications should be used for precise calculations.
Future Expansion
Consider whether there's any possibility of adding more lights or other loads in the future. Upsizing the conductors slightly now can save money and headaches later.
Safety Factors
It's always prudent to build in a small safety factor when sizing conductors.
Professional Engineer/Licensed Electrician
For a project of this scale, especially with long distances and high voltages, it is highly recommended to consult with a qualified Professional Engineer or Licensed Electrician. They can provide a thorough review of your plans, ensure code compliance, and identify any potential issues.
Summary of Recommendations
Confirmed
15A total current on the circuit is correct.2.
Confirmed
4 AWG is sufficient.3.
Revised
You would only need 1" conduit.4.
Confirmed
#12 or #10 AWG acceptable within the pole.
Crucially: CONSULT A QUALIFIED PROFESSIONAL BEFORE IMPLEMENTING THIS PROJECT. LONG RUNS, HIGH VOLTAGES, AND COMPLEX LOADS REQUIRE EXPERT REVIEW TO ENSURE SAFETY AND CODE COMPLIANCE. Flag for review