Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: NEC, I disagree.

User: David Weiszbrod, Location: Oklahoma City

Asked on: Wednesday, November 27, 2024 at 9:16 am EST
Answered on: Thursday, March 6, 2025 at 5:43 am EST

Question: I ran across a discussion about voltage ratings on single, double and three pole breakers used in a 240V open delta service. Article 230.85 says a breaker with a 120/240 volt rating cannot be used on a 208 volt phase. It describes the rating as the limit of voltage to ground. The breaker does not connect to ground except when its a GFCI and I am excluding the GFCI in the post. While the insulated case does touch grounded parts of the panel the voltage highest potential is between the poles of two adjacent phases. In the case of a two or three pole breaker the voltage potential between the poles within the breaker is 240 volts which is greater than 208V. If it's not safe on 208v then it's not safe on 240v.Designed insulation voltage must include current interruption voltage. Contact voltages on inductive loads can be in thousands of volts but are usually short lived. On a two or three pole the first pole to open will have 240 volts plus inductive EMF across it. The action of one pole is connected to the other pole(s) to completely disconnect the circuit.I contend that the 120/240 means (either/or) not exclusive or. A Siemens Q120 breaker has a rating of 120/240V. Does that mean it's suitable for European panels? I yes why not US?What are your thoughts?David

David, you've raised some important points regarding breaker voltage ratings, especially in the context of 240V open delta systems and the interpretation of markings like "120/240V." Let's break down your arguments and address your questions.

Understanding Voltage Ratings and 230.85 230.85's Intent

The primary intent of NEC 230.85 (or equivalent clauses in other codes) is to ensure that breakers used have
adequate insulation and interruption capacity for the system voltage to ground. In a 208Y/120V system, the voltage from any phase conductor to ground is 120V. The phase-to-phase voltage is 208V. A 120/240V breaker is not considered suitable because while the voltage to ground is within its 120V rating, it isn't rated for the 208V between phases.

Voltage to Ground vs. Voltage Between Phases

You're correct in pointing out that much of the insulation within the breaker sees phase-to-phase voltage, particularly in multi-pole breakers. The 120/240V rating specifically addresses voltage to ground. It is the combination of insulation to ground and the breaker's ability to interrupt the circuit under fault conditions (which can stress insulation) that determines suitability.

Why the Emphasis on Voltage to Ground?
This is a safety issue. Think about the consequences of a ground fault. In a solidly grounded system, a ground fault creates a high current path back to the source, and the breaker's ability to quickly interrupt this current is crucial. A breaker with insufficient insulation to ground, even if it can handle the phase-to-phase voltage, is more likely to fail during a ground fault event, potentially causing a fire or shock hazard.

Addressing Your Specific Points
"120/240 Means Either/Or"

This is not the correct interpretation. The slash indicates that the breaker is rated for systems where the voltage-to-ground is 120V and the voltage between phases is 240V. It doesn't mean it can be used on any system with either 120V or 240V. It must meet both conditions. This rating is for systems that are typically called 'split phase' where there are two 120v legs and a neutral that creates 240V voltage potential from one hot leg to the other hot leg.

Inductive Loads and Voltage Spikes

You're right about inductive loads creating voltage spikes during interruption. Breakers are designed to handle these transient overvoltages to a certain extent. The voltage rating, along with other tests, ensures they can interrupt these inductive loads safely. However, exceeding the rated voltage increases the risk of insulation breakdown.


European Panels

A Siemens Q120 breaker (or its European equivalent) with a 120/240V rating is not generally suitable for typical European 230/400V systems. While the voltage-to-ground (230V) might seem close to the 240V rating, it is not. Europe typically uses 230V to ground on a 400V 3-phase system. The voltage potential is just enough to create a risk of damage or fire if used in that manner. They would require breakers specifically rated for 230/400V or higher, built to different standards (e.g., IEC instead of UL).

Why Not Safe on 208V if Not Safe on 240V?


Your statement that if it's not safe on 208V, then it's not safe on 240V, seems logically inconsistent at first, but it touches on an important point: The 120/240V breaker is designed for 240V phase-to-phase voltage in the context of a system where the voltage to ground is 120V. This is a critical difference. The safety margin built into the breaker is based on that specific configuration. In a 208Y/120V system, the voltage to ground is fine, but the 208V phase-to-phase voltage is pushing the limits of the design in a way that wasn't intended or tested. While it might work in many cases, it's not guaranteed, and it violates the listing and code requirements.

In summary: Breaker voltage ratings are not just about phase-to-phase voltage; they also consider voltage to ground and the breaker's ability to interrupt faults safely. "120/240V" is not an "either/or" rating. It requires the breaker to be suitable for systems with 120V to ground and 240V between phases. Using a breaker outside its rated voltage range violates safety standards and code requirements, increasing the risk of failure and hazards. Just because a breaker seems like it might work on a slightly different voltage doesn't mean it's safe or compliant.It's always best to err on the side of caution and use breakers with the correct voltage and current ratings for the specific electrical system. When in doubt, consult with a qualified electrician or electrical engineer. Flag for review

Previous Question Next Question