Question: hi everyone , I need some advice on a situation we got a small electrical work shop with a trainking station and we just purchase a new xformer step-up to convert our 120/208v service to 480v, we got everything connected high leg to phase C like the diagram shows, but when I read the voltages with the multimeter on the secondary side (480v) I got , Phase A(280V), B (230V), C (355V) and I don’t know could be happening , any thoughts? , I’m pretty sure you guys will ask for more details on this please let met know what information I can provide to get a better understanding on this, thanks in advance.
Okay, let's troubleshoot this. A couple of things are immediately apparent, and we'll need more info to narrow it down. The voltages you're reading on the secondary (480V) side are way off and completely inconsistent with a properly functioning step-up transformer. These low and uneven readings strongly suggest a problem before the transformer, a problem with the transformer itself, or an incorrect connection.Here's a breakdown of things to consider and what information I need
1. Verify Input Voltage and Wiring (Primary Side - 120/208V):
Accurate Measurements
This is absolutely critical. Use a good quality voltmeter.
Phase-to-Phase Voltages
Measure the voltage between each pair of phases on the primary side: A-B, B-C, C-A. You should be getting around 208V for each.
Phase-to-Neutral Voltages
Measure the voltage between each phase and the neutral: A-N, B-N, C-N. You should be getting approximately 120V for each.
Is the High Leg Identified? Verify which phase is the high leg (typically orange). The phase-to-neutral voltage of the high leg should be about 208V. Wiring Connections
Visual Inspection
Carefully check all connections on the primary side. Are they tight and properly landed on the correct terminals? Double-check the wiring diagram provided with the transformer. Make sure no wires are swapped.
Phase Rotation
While less likely to cause this specific voltage issue, ensure the phase rotation is correct if you have equipment that is sensitive to it on the secondary side. Incorrect phase rotation doesn't usually cause the voltage readings you're seeing, but it's a good check. (Phase rotation meters exist for this.)
2. Transformer Information
Nameplate Data
Provide the exact nameplate information from the transformer. This includes:
kVA Rating
(kilovolt-amperes - power rating)
Primary Voltage
(e.g., 208 Delta)
Secondary Voltage
(e.g., 480Y/277 - that's a wye configuration)
Taps
(If it has taps for voltage adjustment, note the tap setting)
Impedance (%Z)
This is important for fault current calculations but can sometimes provide a clue if something is drastically wrong.
Manufacturer and Model Number
Wiring Diagram
If possible, provide a photograph or scan of the wiring diagram that came with the transformer. This is often crucial for verifying connections.
3. Secondary Side (480V) Configuration
Is it a Wye or Delta Configuration? A "Y" (Wye) connected secondary is typical for 480V systems. If so, there should be a neutral connection. Do you have a Neutral Connection on the Secondary? If so, measure the voltage from each phase to neutral (A-N, B-N, C-N). In a balanced 480Y/277 system, these voltages should be close to 277V. High Leg Placement
You mentioned you connected the high leg to phase C. Double check that you did this and that there is no High Leg on the primary side, only on the secondary. It may be that there is some confusion on the secondary, or if the system is grounded correctly.
4. Meter and Measurement Technique
Meter Accuracy
Are you using a known good voltmeter? Try a different meter if possible.
Measurement Points
Be absolutely sure you are measuring at the correct terminals on the transformer.
True RMS Meter
Make sure your meter is a "True RMS" meter. If you have non-linear loads (like variable frequency drives or some types of LED lighting), a regular (average-responding) meter can give inaccurate readings.
5. Potential Problems
Transformer is Damaged
This is possible, especially if it was purchased used or if it was mishandled during shipping/installation. A damaged winding can cause very strange voltage readings.
Incorrect Transformer
The transformer is the incorrect voltage ratio.
Incorrect Wiring
The most common cause. A single swapped wire can create these kinds of problems.
Overloading
While unlikely to cause such drastically low voltages immediately, overloading the transformer over time can damage it.
Troubleshooting Steps
Start with the Input
Methodically verify the 120/208V supply is correct. Document all voltage readings as described above.2.
Isolate the Transformer
Disconnect all loads from the secondary side of the transformer. Then, repeat the voltage measurements on the secondary side. If the voltages are still incorrect with no load connected, the problem is likely in the transformer or its primary-side wiring.3.
Visual Inspection
Carefully inspect the transformer itself for any signs of damage (burnt smell, bulging, etc.).
Important Safety Notes
De-energize
Always de-energize the circuit breaker feeding the transformer before working on any wiring. Lockout/Tagout procedures are critical.*
Qualified Personnel
This type of work should be performed by a qualified electrician who is familiar with three-phase power systems and transformer installations.
Next Steps:
Provide the requested information above, especially the nameplate data and wiring diagram. Once I have that, I can give you more specific guidance. Good luck! Flag for review