Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 225.39(D) -- again

User: junkhound, Location: Renton, WA

Asked on: Wednesday, November 27, 2024 at 12:17 pm EST
Answered on: Thursday, March 6, 2025 at 5:44 am EST

Question: 120 sq ft outbuilding, separate panel in building one 20A 208 tandem breaker, one 20 A for single LED ceiling lamp, 2 20 V outlets on single 20A breaker.I installed 3 wire 10 AWG thwn in 3/4 RMC with 30A breaker of phase A-B in main panel. Everything in conduit.Local AHJ said 6 AWG and 60A breaker required. I just said 'yes sir' rather than argue, butLots of existing 225.39 threads, but there is one AHJ out there that interprets as a 60A feeder needed. And of course 2 ground rods , etc...

Okay, let's break this down. Your situation highlights a very common point of confusion and potential misinterpretation of the National Electrical Code (NEC), specifically related to outbuilding feeders.

Your Installation (Before AHJ Inspection)



Outbuilding Size

120 sq ft. Small.


Load

One LED ceiling lamp (low wattage), two 120V outlets. Very light load.

Feeder

10 AWG THWN in 3/4" RMC conduit, protected by a 30A 2-pole breaker (208V) in the main panel.


Panel in Outbuilding

One 20A tandem breaker, one 20A single-pole breaker (for the light), and one 20A single-pole breaker (for the two outlets).

AHJ's Requirement

6 AWG conductors. 60A breaker. Two ground rods.

The Core of the Disagreement

The key issue here is the interpretation of NEC 225.39 (2023 NEC) and related sections. Many electricians and inspectors debate the proper sizing of a feeder to an outbuilding with a subpanel.


Your Interpretation (Likely)

You sized the feeder based on the calculated load of the outbuilding. Given the minimal lighting and just two outlets, a 30A feeder using 10 AWG was likely more than adequate for the expected load. You were thinking practically.

AHJ's Interpretation

The AHJ is likely interpreting NEC 225.39(D) (which refers to 230.42(B)) as mandating a
minimum feeder size based on the ampacity of the panelboard in the outbuilding. Even though the actual load is small, the AHJ might be taking a conservative stance of not feeding a panelboard at less than its rated amperage.

Why the AHJ Might Be Saying 6 AWG and 60A



Panelboard Ampacity

The panelboard in your outbuilding has the potential to supply 40A worth of 120V (based on its breakers). The AHJ might be arguing that you can't feed a panelboard with a feeder that has less ampacity than the panelboard's total breaker capacity. If your panelboard is rated for 60 amps or higher (which is not uncommon), then he may be using 225.39(D) which refers to 230.42(B).

Future Expansion

The AHJ might be considering potential future loads. Even if your current load is minimal, they might be thinking about what happens if you add a heater, air conditioner, or other high-draw appliances in the future.


Local Amendments

Some jurisdictions have local amendments to the NEC that are more restrictive than the national code. It's possible the AHJ is enforcing a local rule you're not aware of.

Misunderstanding

It's
possible, though less likely, that the AHJ simply misunderstood the installation or assumed you planned to add more circuits later.

NEC Sections to Consider



225.30 Number of Supplies

Generally, you're only allowed one feeder to an outbuilding. This reinforces the AHJ's concern about the feeder needing to be adequately sized for all present and future needs.

225.39 Feeder or Branch Circuit Capacity

This is the critical section. It states that feeder conductors must have an ampacity
not less than the calculated load and not less than the rating of the overcurrent protective device. Subsection (D) is what the AHJ likely thinks applies here. If you cannot determine the load with a calculation, then you have to have an ampacity not less than the rating of the overcurrent device that protects the feeder conductors.

225.32 Disconnecting Means

The disconnecting means for the outbuilding must have a rating not less than the load to be carried, which reinforces the AHJ's argument about potential future loads.

250.32 Grounding and Bonding at Separate Buildings or Structures

This section
definitely requires a grounding electrode system (ground rods) at the outbuilding. Two ground rods spaced at least 6 feet apart are generally required. The AHJ is correct on this point.

What You Should Do


Politely Ask for Clarification

Go back to the AHJ and,
without being confrontational, ask for a detailed explanation of the code section(s) they are using to justify the 6 AWG/60A requirement. Ask about the panelboard rating. A polite, respectful tone is crucial.2.

Review Local Amendments

Check with your local building department to see if there are any local amendments to the NEC that might apply. These could be on their website or available by asking at the counter.3.

Perform a Load Calculation

Even though your current load is small, create a
documented load calculation based on the NEC methods. Include any potential future loads. This calculation will give you a concrete basis for your argument. Documenting this is CRITICAL.4.

Consider a Panel Upgrade

If the AHJ is adamant about the 60A requirement, and you can't sway them with a load calculation, you might have to:


Upgrade the Feeder

Install the 6 AWG conductors and a 60A breaker as requested.

Upgrade the Panelboard (Possibly)

The AHJ may require you to install a panel board rated for 60A.5.

Appeal the Decision (Last Resort)

If you strongly believe the AHJ is incorrect and you've exhausted all other options, you might have the right to appeal their decision to a higher authority within the building department. However, this should be a last resort, as it can damage your relationship with the inspectors.

Important Considerations



Safety First

The AHJ's primary concern is safety. While you might disagree with their interpretation, their goal is to ensure the installation is safe and code-compliant.

AHJ's Discretion

Inspectors have some discretion in interpreting the code. Their decisions are based on their experience, knowledge of local conditions, and interpretation of the NEC.


Documentation

Keep meticulous records of all calculations, conversations, and inspections. This documentation can be invaluable if you need to appeal a decision.

In Summary:


While your initial installation was likely sufficient for the current load, the AHJ's concern about the panelboard's potential ampacity and future expansion is understandable. The best approach is to politely and respectfully seek clarification, document your load calculations, and be prepared to compromise, or upgrade your installation if necessary. Good luck! Flag for review

Previous Question Next Question