User: timm333, Location: Minneapolis, MN
Asked on: Thursday, November 28, 2024 at 11:54 am EST
Answered on: Thursday, March 6, 2025 at 5:45 am EST
Question: We have 4/O AWG direct buried bare copper conductor used as ground ring electrode. Another 4/O AWG bare copper grounding conductor (about 10 feet long) is stubbed up from this ring and is used for grounding the skid. (One end of this stub up grounding conductor is connected underground to the ring, and the other end is connected aboveground to the skid.) A piece of rigid PVC conduit is used to protect this grounding conductor at the point where it emerges from the ground.Do NEC 300.5(D)(1) [direct buried cables/conductors emerging from grade] and 352.12(A) [PVC conduit not permitted in hazardous locations] apply to this bare copper grounding conductor? Or do NEC 300.5(D)(1) and 352.12(A) apply only to power cables? Thanks
Let's break down the application of these NEC sections to your specific scenario
NEC 300.5(D)(1) - Emerging from Grade
Does it apply? YES, likely. NEC 300.5(D)(1) states: "Direct-buried cables or conductors emerging from grade shall be protected by enclosures or raceways extending from the minimum cover distance required by 300.5(A) below grade to a point at least 8 ft (2.44 m) above finished grade. In lieu of an enclosure or raceway, direct-buried conductors emerging from grade shall be installed in accordance with 300.5(D)(2)." The key phrase is "Direct-buried cables or conductors." This is broad and doesn't explicitly limit it to power conductors. A bare copper grounding conductor certainly falls under the definition of a direct-buried conductor. The intent of 300.5(D)(1) is to protect the conductors from physical damage where they emerge from the ground, where they are most vulnerable to mechanical stress, landscaping equipment, or accidental contact. Therefore, a bare copper grounding conductor emerging from the earth is subject to the protection requirements of 300.5(D)(1).
NEC 352.12(A) - Use Not Permitted: Hazardous (Classified) Locations Does it apply? Potentially, depending on location. NEC 352.12(A) says that PVC conduit is not permitted in hazardous locations unless otherwise permitted in Chapters 5, 6, and 7. The critical question is whether the location where this grounding conductor emerges and connects to the skid is classified as a hazardous (classified) location. This requires determining if flammable gases, vapors, dust, or fibers are present in sufficient quantities to create an explosion or fire hazard. If the location is not classified as hazardous, then 352.12(A) does not apply, and the use of PVC conduit is acceptable (assuming all other PVC conduit requirements are met). If the location is classified as hazardous (e.g., Class I, Division 1 or 2, or Class II, Division 1 or 2, etc.), then 352.12(A) does apply, and you cannot use PVC conduit unless an exception in Chapters 5, 6 or 7 specifically allows it for that hazardous classification. You would need to use an approved raceway method for the hazardous location (e.g., rigid metal conduit, intermediate metal conduit, etc.).
Summary & Recommendations
Comply with 300.5(D)(1)
The bare copper grounding conductor emerging from the ground must be protected. The PVC conduit is attempting to satisfy this requirement.2.
Hazardous Location Assessment
Determine if the area where the grounding conductor emerges is classified as a hazardous location. This is critical.
If NOT a hazardous location
The PVC conduit is likely acceptable for physical protection, assuming it is installed properly, and other articles of the NEC are followed. Consider using a more robust method of protection like RMC or IMC.
If it IS a hazardous location
PVC conduit cannot be used unless specifically permitted by an exception in Chapters 5, 6, or 7. You must use a raceway method approved for the specific hazardous location classification. This would typically be rigid metal conduit (RMC) or intermediate metal conduit (IMC) with appropriate fittings, and proper sealing.3.
Best Practice
Even if not strictly required by code, consider using a more robust raceway, like RMC or IMC, instead of PVC for this grounding conductor protection. It provides better mechanical protection and is less susceptible to damage. The cost difference is often minimal compared to the potential consequences of a damaged grounding conductor.
Important Considerations
Local Amendments
Always check with your local electrical inspector for any local amendments to the NEC. Local jurisdictions may have stricter requirements.
Engineering Judgment
The final decision on the appropriate protection method should be based on sound engineering judgment, considering the specific site conditions and potential hazards.
In conclusion, while 300.5(D)(1) applies to your situation, the acceptability of the PVC conduit depends entirely on whether the location is classified as hazardous. Always err on the side of caution and consult with a qualified electrical inspector or engineer. Flag for review