Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Ground size question

User: jcerm, Location: Davis, CA

Asked on: Thursday, November 28, 2024 at 6:33 pm EST
Answered on: Thursday, March 6, 2025 at 5:46 am EST

Question: I’m installing an e23T-3 kiln (48A, 240V, 1 phase) using its existing power cord (6 AWG 2-conductor + 8 AWG ground, rated at 105°C). My plan is:Hard wire the power cord to a 60A, 250V fused disconnect switch (60A fuses) - which is recommended by the manufacturer.Run MC 6/2 cable with a 10 AWG ground from the switch to a 60A 2-pole circuit breaker.NEC 250.122 states the ground size is based on the upstream overcurrent device, which here is the 60A fuses. Per the table, 10 AWG copper is sufficient.My question: Is there any issue with the disconnect to breaker ground being 10 AWG, while the kiln’s power cord uses an 8 AWG ground?Thanks in advance for your insight!

You are on the right track with your reasoning regarding NEC 250.122. However, there are a couple of things to consider for a safe and compliant installation.

Analysis of Your Plan



Kiln Cord

You've identified the kiln cord as 6 AWG conductors and an 8 AWG ground, rated at 105°C. This is essential information.


Fused Disconnect

A 60A, 250V fused disconnect switch with 60A fuses is a good choice for a disconnect. The manufacturer's recommendation is a good indicator.

MC Cable

MC 6/2 cable with a 10 AWG ground from the disconnect to the breaker is where the question arises.


60A 2-Pole Breaker

This is the correct type of breaker for a 240V load.

NEC 250.122 Application

Your understanding of NEC 250.122 is correct in that the grounding conductor size is based on the overcurrent protection device.

Addressing Your Question



The Key Consideration: Equipment Grounding vs. Bonding
Your concern about different sizes of grounding conductors is relevant, but the specific application of the NEC (National Electrical Code) needs to be considered. NEC Article 250 covers grounding and bonding. Grounding refers to connecting to earth, while bonding refers to connecting metallic parts to create an electrically conductive path and ensure electrical continuity. In your case, you are primarily dealing with equipment grounding, providing a low-impedance fault path. Upstream vs. Downstream Grounding

The Code states in 250.122(A) that the equipment grounding conductor size is based on the rating of the

overcurrent protective device
protecting the circuit. You correctly identified this to be the 60A fuses in the disconnect switch. The 10 AWG ground in your MC cable meets this requirement, so it is code compliant. Grounding at the Kiln The #8 ground wire in the kiln cord is sufficient for the kiln itself. By installing the 60A disconnect switch and MC cable appropriately, the equipment grounding path is continuous from the kiln, through the disconnect switch, to the breaker.

Summary and Recommendation1. Your proposed plan is likely code-compliant. A 10 AWG grounding conductor is sufficient for a 60A overcurrent protective device per NEC 250.122. However, there are other factors to consider and verify.
2. Verify Local Codes and AHJ Always consult with the local Authority Having Jurisdiction (AHJ), usually a local electrical inspector. They have the final say on code compliance and may have local amendments that differ from the NEC.3. Consider these additional points

Ensure proper termination of the grounding conductors at the disconnect and at the breaker panel. Use appropriately sized lugs and terminals to create secure and reliable connections. The equipment grounding path (from the kiln's frame, through the cord, through the disconnect switch, and back to the breaker panel) must be continuous and low impedance to effectively clear faults.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Always consult with a qualified and licensed electrician for any electrical work to ensure safety and code compliance.* Flag for review

Previous Question Next Question