User: Jimmy7, Location: Boston, MA
Asked on: Friday, November 29, 2024 at 8:45 am EST
Answered on: Thursday, March 6, 2025 at 5:46 am EST
Question: We installed one of those Arlington fixture siding blocks. The cu in of the block appears to be 6.8. We only have one 14-2 going to the fixture. The owner wants to now install a RAB Gotcha all in one (Pre-assembled two lights and one motion) in that location. On the inside of the RAB cover it states CU4, it appears that is the model number of the cover and not the cubic inch unfortunately. I tried to call RAB to confirm but have been unsuccessful. I know there is an exception in the code in regards to fixture wires that originate within a canopy under #14. I was planning to connect the to the black and white from the canopy. I was also planning on running a #14 to a green screw on the cover to the ground of the 14-2 romex. What about the pre-assembled factory connections of the motion sensor? Do I need to count the pre-assembled connection that terminate in the cover?
Okay, let's break this down to ensure a compliant and safe installation. It's a good practice to over-think these things a bit to be sure.
Key Issues and Code Considerations
Box Fill
The central issue is whether the 6.8 cu in box is large enough to legally contain all the conductors, devices, and connections per NEC 314.
16.
Fixture Wires Exception
NEC 314.16(B)(1) does allow an exception for fixture wires that originate within the canopy or enclosure, provided certain conditions are met (covered in detail below).
Device Fill
Devices (like the motion sensor) within the box have to be accounted for in the box fill calculation (NEC 314.16(B)(4)).
Grounding
Proper grounding is essential (NEC 250).
RAB Documentation
The lack of clear cubic inch information from RAB is a hurdle. You're doing the right thing trying to confirm.
Detailed Analysis and Recommendations
Confirm RAB Enclosure Volume
Keep Trying to Contact RAB
Seriously, keep trying to get the actual cubic inch volume of the RAB enclosure from the manufacturer. This is the most direct way to know if it's compliant. Document your attempts (date, time, person contacted, response) in case you need to demonstrate due diligence.
Look for Other Markings
Examine the RAB cover and any other part of the assembly extremely carefully for any other markings that might indicate the cubic inch volume. Sometimes these markings are faint or in an unexpected place.
Measure (Carefully!)
If you absolutely cannot get the volume from RAB, you could attempt to measure the internal volume of the RAB enclosure. This is tricky because of irregular shapes, but you can try to estimate it by: Creating a scale drawing of the inside of the enclosure, calculating the area, and then multiplying by the depth. Filling the enclosure with sand or beads, then pouring those into a measuring cup or graduated cylinder.
Important
Be very conservative in your measurement. Round down significantly. Your estimate must be accurate in order to comply with code.2.
Box Fill Calculation (Assuming 6.8 cu in Box)
Conductors
(2) 14 AWG current-carrying conductors (black, white from the 14-2). Count each as 1.5 cu. in. (NEC 314.16(B)(1)). 2 x 1.5 = 3 cu. in. (1) 14 AWG grounding conductor. Count this as 1.5 cu. in. (NEC 314.16(B)(5)).
Total conductor volume
3 + 1.5 = 4.5 cu. in.
Device
You need to know the exact size of the device. For instance, if you had one single gang device you would need to count it as an additional 3 cu. in. (double the conductors). However, we would need the RAB dimensions to determine if this is needed.3.
Applying the Fixture Wire Exception (NEC 314.16(B)(1))
This is where things get tricky, and RAB's documentation is critical. The exception might apply to the wires within the RAB fixture itself.
Conditions for the Exception to Apply
#18 AWG or Smaller
The wires must be #18 AWG or smaller. Verify this by looking at the wire insulation markings inside the RAB fixture.
Total Length
The total length of these #18 AWG (or smaller) wires must not exceed 6 inches.
Termination
The #18 AWG wires must terminate in the canopy or within the RAB enclosure itself. They cannot extend out to a separate box without being counted.
Markings
The fixture must be listed for connection to branch circuit conductors. This is generally not a problem for a fixture like the RAB Gotcha, but verify it on the fixture's label.
If the Exception Applies
If all of the above conditions are met, you do not have to include the fixture wires in your box fill calculation.
If the Exception Does Not Apply
If any of the conditions are not met (e.g., the wires are #14 AWG, or longer than 6 inches), then you must include these wires in your box fill calculation. Assume each wire is 1.5 cu. in. for #14. This would likely make the box overfilled!4.
Grounding
Important
The RAB fixture must be properly grounded.
Your Plan
Running a #14 AWG wire from the ground of the 14-2 romex to a green grounding screw on the RAB cover is a good plan. Make sure the connection is tight and secure. Use a proper wire connector (wire nut with grounding hole, or similar).
Continuity
Verify the grounding path is continuous from the service panel to the RAB fixture.5.
Factory Connections of the Motion Sensor
This is a key question. If the motion sensor's connections are truly factory-sealed (potted or similar), then you might be able to argue that they don't contribute to the box fill.
Important
I would lean very heavily toward including them in the box fill unless you have definitive documentation from RAB stating that they are sealed and do not contribute. The safer approach is to count them. Assume each pigtail is 1.5 cu. in.
6.
The "CU4" Marking
You are almost certainly correct that "CU4" is a model number and not a cubic inch volume.
Bottom Line and Action Plan
Get the RAB Volume
This is the absolute priority. Keep calling and emailing RAB. Document everything.2.
Inspect the RAB Wires
Carefully examine the wires within the RAB fixture. Are they #18 AWG or smaller? Are they longer than 6 inches?3.
Calculate Box Fill
Based on the known conductors and the (hopefully obtained) RAB internal volume, calculate the box fill.4.
If Overfilled
Option 1 (Best)
Change to a larger box. This is the safest and most code-compliant solution. Use a deeper Arlington fixture siding box, or a box extender.
Option 2 (Potentially Problematic)
If the RAB fixture's internal wiring definitely meets the exception requirements, and the RAB enclosure volume is just barely compliant after carefully accounting for everything else (including the motion sensor connections), you might be able to proceed. However, this is risky, and could easily be challenged by an inspector.
Important Considerations
Local Codes
Always check with your local electrical inspector or authority having jurisdiction (AHJ) for any specific requirements in your area. They have the final say.
Safety First
When in doubt, err on the side of caution and use a larger box. Overfilling boxes can lead to overheating, loose connections, and potential fire hazards.
Documentation:* Keep detailed records of your calculations, RAB information (or lack thereof), and any communications with inspectors.This is a complex situation, and getting the correct cubic inch volume for the RAB fixture is critical. Good luck! Flag for review