Topic: Utility pole to meter conductor type

User: KnoxvilleGains, Location: Knoxville, TN

Asked on: Friday, November 29, 2024 at 9:37 am EST
Answered on: Thursday, March 6, 2025 at 5:47 am EST

Question: I was provided this Utility Drawing by my local utility. I'm having the pole transformer moved to another pole and running underground to a new disconnect/meter on the side of the home during a re-truss of the home which requires removal of the existing overhead.The utility requires conduit due to the rocky soil (confirmed rocky during trenching, terrible). This is creating issues for me in specifying a proper conductor type for the run. It's 4/0-4/0-2/0 Al but the issue here is my loop from the weatherhead to the pole transformer. Everyone has suggested URD (specifically Southwire Sweetbriar 55418406) but the exposed loop concerns me. I can't find anything stating this is UV rated and the jacketing is cross linked polyethylene. That's the same material as PEX which is certainly not rated for UV exposure.Anybody had a similar application? What did you ultimately go with? This is a 2" conduit run of about 160' with two vertical 90s, one horizontal 90 and two horizontal 45s.

Okay, you've got a common but tricky situation. Let's break down the issue and potential solutions. You're right to be concerned about the UV exposure on the loop if you use standard URD.

Understanding the Problem URD and UV

Yes, standard URD cable is generally
not designed for prolonged, direct UV exposure. While the XLPE insulation itself offers some UV resistance, it's not nearly as good as a specifically UV-rated jacket. Over time, UV can degrade the XLPE, making it brittle and potentially leading to cracking and eventual failure.

Code Considerations

While there isn't a specific code section prohibiting URD for a short exposed loop, the general requirement for suitability for the environment (110.3(B)) kicks in. If the cable is going to degrade and fail prematurely due to UV, it's arguably not "suitable."

Rocky Soil

The rocky soil mandates conduit, which makes sense. This is good for mechanical protection but also limits your conductor choices to those suitable for conduit.


Conduit Fill

With 4/0-4/0-2/0 Aluminum, conduit fill is important, especially with multiple bends. 2" is likely necessary, and you need to double-check your calculations (using Chapter 9, Table 5A in the NEC).

Possible Solutions (Ranked from Most Recommended to Least)
1. Use RHW-2 or XHHW-2 Conductors for the Entire Run



Description

This is often the
best solution. Use individual RHW-2 or XHHW-2 conductors for the entire run, including the loop to the transformer. These are widely available, cost-effective, and are rated for wet locations and direct burial in conduit. They have much better UV resistance than URD jacketing.

Pros

UV Rated: RHW-2 and XHHW-2 are designed for wet locations and can handle some UV exposure (though it's still best to minimize direct sun). Code Compliant: Clearly meets code requirements. Readily Available: Easy to find at electrical supply houses. Standard Installation Practices: Electricians are familiar with working with these conductors.

Cons

Slightly More Labor: Pulling individual conductors can be a bit more labor-intensive than pulling a bundled URD cable (though for a relatively short run like yours, it's not a huge difference). May require additional neutral. XHHW-2 does not make for a good neutral and in most cases you will need to pull a separate green ground wire.2.

Use a UV-Resistant Coating on the URD Cable



Description

If you really want to use URD, you could apply a UV-resistant coating or paint specifically designed for electrical cables.

Pros

Potentially Easier Pull: URD is easier to pull as it's all bundled together.

Cons

Uncertainty: The effectiveness of these coatings varies. You need to find a product specifically rated for XLPE and verify its long-term performance. You'll also need to re-apply it periodically. Potential Warranty Issues: Using an aftermarket coating might void the cable manufacturer's warranty. Check with Southwire. Still Not Ideal: This is really just a "band-aid" solution. Hard to apply on existing installations.3.

Consider USE-2 Cable (If Permitted by Utility and AHJ)



Description

USE-2 (Underground Service Entrance Cable) is designed for direct burial and does have a UV-resistant jacket. However, it's often a single-conductor cable and may not be the configuration you need. Also, some utilities specifically prohibit its use for the service drop to the transformer.

Pros

UV Rated: Specifically designed for direct burial and UV exposure.

Cons

Utility Approval Needed: Check with the utility first to see if they allow it for this application. May Not Be the Right Configuration: USE-2 is often a single conductor, so you'd need to pull multiple conductors. Availability: Can be harder to find in larger sizes.4.

RMC Conduit and Conductors for the Riser



Description

Use rigid metal conduit (RMC) for the vertical section from the weatherhead to the trench, and transition to PVC below ground. This would provide maximum mechanical and UV protection for the conductors in the exposed portion.


Pros

Excellent Mechanical and UV Protection: RMC is extremely durable. Clear Code Compliance: No questions about suitability for the environment.

Cons

Cost: RMC is more expensive than PVC. More Labor: RMC is heavier and more difficult to work with than PVC. Still Requires Proper Conductors: You'd still need to use RHW-2 or XHHW-2 inside the RMC.

Recommendations


Start with RHW-2 or XHHW-2 conductors

This is the most straightforward, reliable, and code-compliant solution. Talk to your electrician about pulling these individual conductors in the conduit.2.

Confirm with the Utility

Before making any decisions, call the utility. Specifically ask them: "What type of conductors do you recommend for the loop between the weatherhead and the pole transformer, considering it will be exposed to sunlight?" "Do you have any specific requirements or restrictions on the conductors or installation methods in this situation?" "Would you permit the use of USE-2 cable?"3.

Consult with Your Local Electrical Inspector (AHJ)

Run your proposed solution by the local electrical inspector before you start work. They have the final say on code compliance.4.

Consider a Sun Shield

As a supplementary measure, regardless of the conductor you choose, consider adding a simple sun shield or "hood" over the loop to provide some additional protection from direct sunlight. This could be fabricated from aluminum or a UV-resistant plastic.

Important Considerations



Neutral Conductor

The 2/0 neutral is smaller than the phase conductors. Ensure this is sufficient for your load calculations and meets the requirements of NEC 220.61 (Feeder or Service Neutral Load). You might need to upsize it.

Grounding

Pay close attention to grounding requirements. You'll need a proper grounding electrode system (ground rods, etc.) at the service disconnect, and the grounding conductor must be sized appropriately.


Professional Installation:
This is not a DIY project. Hire a licensed electrician who is experienced with service entrance installations and understands local codes and utility requirements.By following these steps, you'll be able to select the right conductors and ensure a safe and reliable service entrance for your home. Good luck! Flag for review