Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Help deciding on wire exiting sub-panel

User: jktaylor2020, Location: Tuscaloosa

Asked on: Monday, December 2, 2024 at 12:00 am EST
Answered on: Thursday, March 6, 2025 at 5:49 am EST

Question: Hello all,I need help deciding on what conductor to use.Currently have a small-sub panel being fed by 10/3 w ground, from 30 amps 2-pole. When exiting the sub panel, what type/ size of wire should I use.Outdoor pavilion(no inspection required)Plan on using 3/4 EMT(already have some)Load will be 4 can lights, one TV, two outdoor receptacles,(possibly one cool vintage coke machine)Thanks in advance. I am a distribution lineman for the local utility, this is not my normal operation..Thanks!

Okay, let's break down the conductor sizing for your outdoor pavilion. Since you're a lineman, you already understand the core concepts, but let's make sure we're on the same page for residential wiring and the NEC (National Electrical Code). While you said no inspection, it's always best to follow code for safety.1. Calculate the Load



Can Lights

Assume each is 75W LED equivalent. 4 lights
75W = 300W

TV

Assume 200W (modern LED TV).


Outdoor Receptacles

Each receptacle is considered 180VA (Volt-Amps) for general use. 2 receptacles 180VA = 360VA

Coke Machine (Unknown)

This is the big wild card. A vintage coke machine could draw a significant amount of power, especially on startup. You must find the nameplate rating (Voltage and Amps) on the machine to accurately calculate its load. For now, let's make a conservative estimate of 600VA, but

this is just a placeholder
. You must replace this with the actual value. A compressor and lights can draw some current. Total Estimated Load (Without Coke Machine)

300W + 200W + 360VA = 860 VA


Total Estimated Load (With Coke Machine Estimate)

860VA + 600VA = 1460VA

2. Calculate the Current

Use the formula: Current (Amps) = Power (VA) / Voltage (Volts) Assume Voltage is 120V (standard for most of your loads)

Current (Without Coke Machine)

860VA / 120V = 7.17 Amps


Current (With Coke Machine Estimate)

1460VA / 120V = 12.17 Amps

3. Conductor Sizing (Based on Ampacity)

NEC Table 310.16 (Ampacities of Insulated Conductors) is the key. We need to select a wire size with an ampacity at least equal to the current you calculated, and account for termination temperature. Most common residential wiring uses THHN/THWN-2 insulation, which is rated for 90°C. However, you are limited by the termination temperature rating of your breakers and devices (usually 75°C). So, you must use the 75°C column in Table 310.16.

Without Coke Machine (7.17 Amps)

You could theoretically use #14 AWG copper (which is rated for 20 amps at 75 degrees)


With Coke Machine Estimate (12.17 Amps)

You could theoretically use #14 AWG copper (which is rated for 20 amps at 75 degrees)

4. Considerations and Recommendations



Voltage Drop

Even though the ampacity requirements might allow for smaller wire, voltage drop can be a problem, especially over longer distances. Voltage drop causes lights to dim, motors to run less efficiently, and can damage sensitive electronics. Since you're using a sub-panel, the distance from the sub-panel to your furthest device is the important factor. If the run is over 50 feet, I would go to the larger size.


Future Expansion

It's always a good idea to plan for the future. Do you anticipate adding more lights, speakers, or other devices to the pavilion later? Upsizing the wire now is cheap insurance.

Receptacle Load

Don't forget that the outdoor receptacle load of 180VA is just for general purpose. If someone were to plug in a power tool or something else with higher consumption this will cause an overload if you barely meet the amperage.

Recommendation

Given your current load, possible expansion, and the unknown coke machine, I would recommend

#12 AWG copper conductors
. This gives you a 20 Amp rating, enough to handle all the loads Easier wire to work withRegarding EMT Conduit

3/4" EMT is a good choice for physical protection of the conductors. You can generally fit several conductors in 3/4" EMT, but make sure you don't exceed the fill capacity (NEC Chapter 9). #12 AWG is no problem for a few conductors. Make sure all conduit connections are properly tightened and grounded.

Important Reminders



Grounding

Ensure a proper grounding electrode system is in place at the sub-panel (ground rod(s) or connection to the building's grounding system). A dedicated grounding conductor (green wire) must run with the circuit conductors.


GFCI Protection

All outdoor receptacles must be GFCI protected (Ground Fault Circuit Interrupter). You can use a GFCI breaker in the sub-panel or GFCI receptacles.

Wet Location Fixtures

Use outdoor-rated (wet location) can lights and receptacles.


Licensed Electrician

While you may be knowledgeable, if you are uncomfortable with any part of this project, consider consulting with a licensed electrician to ensure everything is installed safely and to code.*

LOCAL CODES

Local codes may have requirements in addition to the NEC.

Disclaimer:
I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Consult with a licensed electrician for your specific situation. Flag for review

Previous Question Next Question