Topic: Bonding duct work.

User: nizak, Location: Henrico County, VA

Asked on: Monday, December 2, 2024 at 2:01 am EST
Answered on: Thursday, March 6, 2025 at 5:49 am EST

Question: Inspector is requiring ductwork and metal gas pipe in crawl space to be bonded.In past jobs I have never been required to do this since the EGC from the furnace circuit sufficed.He is saying that it could become energized and that the #14 EGC is undersized.Is it acceptable to just bug onto the GEC conductor and hit both the black iron pipe and the sheet metal?Thanks

The inspector is likely referencing NEC 250.104(B), which covers bonding of metal gas piping systems. It states:"Other Metal Piping. Other metal piping systems, including gas piping, that are likely to become energized shall be bonded to the service equipment enclosure, the grounded conductor at the service, the grounding electrode conductor where of sufficient size, or to the one or more grounding electrodes used. The bonding conductor(s) shall be sized in accordance with Table 250.122, based on the rating of the circuit that is likely to energize the piping system(s)."Let's break down the situation and address the inspector's concerns: "Likely to become energized": This is the key phrase. The inspector is concerned that the metal gas pipe and/or ductwork could become energized through some fault condition. While the EGC in the furnace circuit is intended to provide a low-impedance path back to the source in case of a fault, the inspector is essentially saying that it might not be sufficient for all possible scenarios, or that other fault paths could exist. #14 EGC "undersized": The inspector's concern isn't necessarily that the #14 EGC is undersized for the furnace circuit itself (though that should be verified against the circuit breaker rating according to Table 250.122). The concern is that it might be undersized for clearing a fault involving a larger circuit that could potentially energize the gas pipe or ductwork. Bonding to the GEC: This is a possible solution, but needs careful consideration. NEC 250.104(B) specifically allows bonding to "the grounding electrode conductor where of sufficient size."Here's what you need to do to ensure compliance and safety


Determine the Size of the Bonding Conductor
: This is the most crucial step. You
cannot simply use any random wire size. Refer to NEC Table 250.122. The size of the bonding conductor is based on the rating of the circuit that is likely to energize the piping system(s).

Important: This isn't necessarily just the furnace circuit. It's any circuit that, if a fault occurred, could energize the gas pipe or ductwork. This might be a larger branch circuit feeding an appliance near the gas line, or even the service equipment.


Example: If a 20-amp circuit is the most likely to energize the gas pipe, then you'd need at least a #12 AWG copper conductor for bonding. If a 30 amp circuit is the most likely to energize the gas pipe, then you'd need at least a #10 AWG copper conductor for bonding, and so on.2.

Verify GEC Adequacy: If you're going to bond to the Grounding Electrode Conductor (GEC), the GEC must be "of sufficient size." This means it needs to be large enough to handle the fault current it might carry in addition to its regular grounding duties. This is highly dependent on the service size and electrode configuration. In many residential situations with smaller services (100-200A) it is not sufficient.3.

Alternative Bonding Points: Instead of the GEC, consider bonding to:

Service Equipment Enclosure: This is often the easiest and best solution. A properly sized bonding conductor from the gas pipe and ductwork to the service panel enclosure is a common and effective method.


Grounded Conductor at the Service: This is generally avoided as it can lead to objectionable current flow.

Grounding Electrode System: Bonding to a grounding electrode, such as a ground rod, is also acceptable, but ensure proper connections and the electrode's integrity.4.

Proper Connections: Use appropriate connectors for bonding. Approved clamps and connectors are essential for ensuring a good, low-impedance connection. Do not use wire nuts for grounding/bonding connections.5.

Continuity: Verify the continuity of your bonding connections with a multimeter. You should have a very low resistance reading between the bonded items and the grounding point.6.

What to do if you cannot determine the circuit likely to energize the gas piping systemIf it is not practical to apply the sizing criteria of NEC 250.104(B) based on the rating of the circuit likely to energize the gas piping system, the bonding jumper shall be sized in accordance with Table 250.
66.


In summary

The inspector's request is likely based on a reasonable interpretation of the NEC. You

cannot
simply "bug" onto the GEC with an undersized wire without verifying its adequacy and conductor size. Determine the proper bonding conductor size based on the potential fault current, not just the furnace circuit. Consider alternative bonding points like the service equipment enclosure. Use appropriate connectors and verify continuity.* If unsure, consult a qualified electrical engineer.Ignoring the inspector's concerns could lead to a dangerous situation in the event of a fault. It's best to address the issue correctly and safely. Consult with a licensed electrical contractor if you need further assistance. Flag for review