Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: 120v circuit

User: mannyb, Location: Florida

Asked on: Monday, December 2, 2024 at 7:58 pm EST
Answered on: Thursday, March 6, 2025 at 5:49 am EST

Question: when installing a 120v circuit could I use the gen feed wire from generator using the neutral and ground for battery charger and installing a single wire to for power?

No, you cannot directly use the neutral and ground from a generator feed wire as your neutral and ground for a separate 120V circuit. Here's why, and what you need to do

Why it's Wrong and Dangerous
Bonding Issues

When you're using a generator
as a separately derived system (i.e., it's not connected to the regular utility power), it has to have a specific bonding configuration. Typically, the generator's neutral is bonded to its frame (which is also connected to the grounding electrode conductor). Connecting this neutral/ground to a new circuit without proper isolation and overcurrent protection can create several problems:

Ground Loops

These can lead to circulating currents in the grounding system, causing noise, interference, and even tripping of breakers.

Incorrect Fault Current Path

If a fault occurs on the new 120V circuit, the return current path may not be reliable or low-impedance enough to trip the breaker quickly. This creates a shock hazard and fire risk.


Overloading the Neutral/Ground

The original generator circuit's neutral and ground wires were sized for that circuit's load. Adding a separate circuit will require the the neutral conductor to be sized appropiately.

Code Violations

The National Electrical Code (NEC) has very specific rules about how separately derived systems (like generators) must be wired. Incorrectly connecting circuits violates these rules.

How to Do It Safely and Correctly
1. Evaluate Your Needs

How much power (amps) does the battery charger need? How often will you be using the charger? Is this a temporary setup, or a permanent installation?2.

Options (depending on your situation)



Dedicated Circuit from the Generator

Run a completely separate 120V circuit from the generator's output, with its own hot (black), neutral (white), and ground (green) wires. The neutral and ground conductors must be sized appropriately for the new circuit's load. This circuit should have its own overcurrent protection (breaker) in the generator's distribution panel or in a separate junction box. Ensure the generator's neutral is properly bonded to the generator's frame (usually done internally by the generator). This is the safest and most reliable option.

Power from the Home's Panel (If Applicable)

If the generator is transferring power to your home's main electrical panel during a power outage, you should install the battery charger on a regular circuit within your home's panel. The generator is acting as the power source for the entire panel, and the house's existing wiring is already properly grounded and bonded.

Small Inverter

For a small battery charger, a small, portable inverter might be sufficient. These plug into the generator and provide a clean 120V output. Make sure the inverter is rated for the charger's power requirements.

Important Considerations
Grounding Electrode System

If the generator is used as a separately derived system, it may need its own grounding electrode system (ground rod or connection to the building's grounding electrode). Consult the NEC and your local electrical inspector for specific requirements.

Licensed Electrician

Electrical work can be dangerous. If you are not comfortable working with electricity, hire a licensed electrician to install the circuit. They can ensure it is done safely and according to code.


Generator Documentation

Always refer to your generator's owner's manual for specific wiring instructions and safety information.

In summary, do not simply tap into the neutral and ground of an existing generator feed for a separate circuit. It's dangerous and likely a code violation. Always use proper wiring methods, overcurrent protection, and grounding techniques.
Flag for review

Previous Question Next Question