Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: E-rated fuses and Table 450.3(A)

User: chuckd83, Location: Wisconsin

Asked on: Tuesday, December 3, 2024 at 8:53 am EST
Answered on: Thursday, March 6, 2025 at 5:51 am EST

Question: I'm looking at a single phase 50 kVA, 13.8/0.24 kV transformer that is protected by a 10E fuse. The primary FLA is 3.6 A. This is a station service transformer and the fuse is its only protection.When I plot the fuse and transformer on a TCC, it becomes obvious that the transformer damage curve is not fully protected. This is because by NEMA standard, it takes up to 5 minutes for an E-rated fuse to operate for currents 200-240% of its rating. i.e. the 10E fuse will never operate for currents less than 20 A.Given this, I'm inclined to replace it with a 5E or 7E fuse. I'm also curious if the current installation meets the requirements of NEC Table 450.3(A) which stipulates the maximum fuse rating must be 300% FLA (10.8 A in my case). The fuse rating is 10E, or 20 - 24 A.

You've identified a common issue with E-rated fuse selection for transformer protection. Here's a breakdown of your situation, analysis, and recommendations

Understanding the Problem
Transformer Damage Curve

Transformers have a short-time overload capability. Exceeding this capability for too long leads to insulation degradation and eventual failure. The transformer damage curve represents the time/current limit beyond which damage occurs.


E-Rated Fuse Characteristics

E-rated fuses are designed for transformer protection. They have a time-delay characteristic that allows them to ride through inrush currents, but as you noted, this same characteristic means they can take a long time to clear overloads.

Inrush Current

The transformer inrush current is a very large, but very short duration current when the transformer is energized, typically 8-12x the full load current.


Coordination

The goal is to choose a fuse that can withstand the inrush and other temporary overloads, but still protect the transformer against sustained overloads and faults.

NEC 450.3(A) and Exceptions

NEC 450.3(A) provides guidance on transformer overcurrent protection. The basic rule is a maximum primary overcurrent device rating of 125% to 300% of the transformer primary current. Exceptions permit higher values if necessary to allow the transformer to start and operate, but still provide protection.

Analysis of Your Situation
1. The 10E Fuse is Problematic

You correctly point out the key issue. A 10E fuse, with its long clearing time in the 200-240% range, will
not protect the transformer against moderate overloads. The transformer can be operating above its thermal damage curve for a prolonged period before the fuse ever blows.2.

NEC Compliance

NEC Table 450.3(A) is a key consideration. Your transformer's primary FLA is 3.6 A.
300% FLA = 10.8A. The 10E fuse (20-24A rating) clearly violates the 300% FLA rule. The exception in 450.3(A) allows for a higher overcurrent device rating ONLY if the lower rating does not allow the transformer to start and operate. Given your small transformer rating, it is likely that a smaller fuse rating can be used.
3.


Transformer Size

The transformer is only 50 kVA, so overloads can easily happen if loads on the secondary are not monitored and controlled.4.

Fuse as Sole Protection

Since the fuse is the only overcurrent protection, it has to protect against both faults and overloads.

Recommendations
1. Reduce Fuse Size – Strongly Recommended



Target Fuse Size

I strongly recommend replacing the 10E fuse with a smaller one, likely a

5E or 7E
. The key is to plot the TCC curve for those fuses along with the transformer damage curve, and the system load. A 5E fuse has a rating of 10-12A. A 7E fuse has a rating of 14-16.8A. TCC Plot Verification (Crucial)

Before making a final decision,
absolutely plot the Time-Current Curves (TCC) for the 5E or 7E (or both) fuses against the transformer damage curve. Make sure the fuse clears below the transformer damage curve for all overload conditions. A TCC plot is non-negotiable.

Coordination with Secondary Protection (If Applicable)

If there is secondary protection (e.g., a circuit breaker on the secondary side), you'll also need to consider coordination between the primary fuse and the secondary protection. However, based on your message, the primary fuse is the only protection.

Important Considerations
Inrush Current

Select a fuse that can withstand the inrush current. A typical transformer inrush can be 8-12 times the full-load current (FLA) for the first few cycles. Time-delay fuses like E-rated fuses are designed to handle this. If you go too small on the fuse, you'll get nuisance tripping during energization.


Voltage Rating

Ensure the replacement fuse has the correct voltage rating (13.8 kV in your case).

Interrupting Rating

The fuse must have an adequate interrupting rating for the potential fault current at the primary location.


Documentation

Keep records of the fuse size you select and the rationale for your choice.

Steps to Take


Gather Data

Transformer nameplate data (kVA, voltages, impedance). Fuse TCC curves for the 5E, 7E fuses. Transformer damage curve (may be available from the manufacturer or based on industry standards). Calculate primary fault current (maximum available fault current at the primary terminals).2.

Plot TCC

Plot the transformer damage curve, the existing 10E fuse curve, and the proposed 5E or 7E fuse curves on the same graph.3.

Analyze

Verify the proposed fuse is below the transformer damage curve for all overload conditions. Verify that the fault current rating of the proposed fuse is adequate.4.

Make a Decision

Choose the smallest fuse size that provides adequate transformer protection without causing nuisance tripping due to inrush current.5.

Document:
Record the fuse size and the reason for your choice.By following these steps, you can select a fuse that provides adequate protection for your transformer while complying with the NEC. Remember that using a fuse that's too large can lead to transformer damage and potential safety hazards. Flag for review

Previous Question Next Question