Topic: test signals coming from a PLC to a AOH motor starter switch without physical connection (no power wires) to the motor

User: oscarfb07, Location: USA

Asked on: Wednesday, December 4, 2024 at 8:51 am EST
Answered on: Thursday, March 6, 2025 at 5:53 am EST

Question: I need to test a AOH switch from a motor starter, but I do not have the power wires yet connected to the motor, so how can I test the signal coming from the PLC AUTO, START and STOP? plus is a local disconnect/starter, and power cables feeding the disconnect are coming from a electrical panel but the power cables going out to the motor are not there yet, so how can I test the I/O coming from the PLC.

Okay, let's break down how you can test the AOH (Auto-Off-Hand) switch and the PLC I/O without the motor power cables connected. This is a common scenario during commissioning.

Understanding the Setup AOH Switch

This switch typically has three positions:


Auto

The motor is controlled by the PLC.

Off

The motor is forced OFF, regardless of PLC commands.


Hand (or Manual)

The motor is controlled by a local start/stop push button (usually bypassing the PLC).

PLC

The Programmable Logic Controller is sending signals (AUTO, START, STOP) to control the motor starter.


Motor Starter

This device contains the contactor that actually switches the motor power. It also likely has overload protection.

Local Disconnect/Starter

This combines a disconnect switch (for safety) and the motor starter in one unit.


Wiring Situation

You have power into the disconnect/starter from the electrical panel. You do not have power cables connected from the disconnect/starter to the motor.

Testing Procedure (Without Motor Cables)


The key here is to simulate the presence of the motor starter contacts being closed without actually energizing a motor. You'll be focusing on verifying the signal path from the PLC through the AOH switch to the motor starter's control circuit.1. Safety First! Lockout/Tagout (LOTO)

Even though the motor power cables aren't connected, ensure the main power supply to the disconnect/starter is de-energized, locked out, and tagged out before doing any wiring or testing. This is critical.


Verify Power is Off

Double-check with a voltmeter that there's no voltage present on the incoming power terminals of the disconnect/starter.

2. Understanding the Control Circuit
Schematic is Essential

You MUST have a wiring diagram or schematic of the motor starter control circuit. This will show you how the AOH switch, PLC signals, start/stop pushbuttons (if present), and the motor starter coil are interconnected. Pay close attention to the voltage used in the control circuit (usually 24VDC, 120VAC, or 240VAC).


Identify the Starter Coil

Locate the motor starter coil (often labeled "A1" and "A2" on the contactor). This is what actually pulls in the contactor to energize the motor. This is the "load" you're trying to control.

3. Simulating the Motor Starter (for Testing Only)


Since you don't have the motor connected, you need to simulate the motor starter's contacts closing. Instead of trying to power the motor, you'll focus on confirming the control circuit works as expected.Here's the common approach: Temporary Test Load

Instead of the motor, connect a small, appropriate load to the output of the motor starter. This can be:


A low-voltage indicator light (LED)

Choose one with a voltage rating that matches the control circuit voltage (e.g., 24VDC or 120VAC). Connect this in series with the motor starter coil.

A small resistor (e.g. a 10k 1/4 watt)

This is only for testing the circuit integrity, not to power anything.

4. Testing the AOH Switch and PLC I/O
1. Restore Power (Carefully)

Once you've verified the wiring and added your test load, temporarily restore power to the disconnect/starter. Be prepared to immediately shut it off if anything seems wrong.2.

AOH Switch Testing



Hand (Manual) Position

With the switch in the "Hand" position, use the local start/stop pushbuttons (if present) to try to energize the motor starter (which will now just light up your indicator light or pass current through your resistor). Verify that the "Start" button energizes the starter coil and the "Stop" button de-energizes it. If there are no start/stop pushbuttons in the HAND position, you'll need to simulate them by momentarily jumpering the appropriate terminals in the control circuit.

Off Position

In the "Off" position, the starter should
not energize, regardless of the PLC signals or local pushbuttons.

Auto Position

Now, switch to the "Auto" position. The motor starter should now be solely controlled by the PLC.3.

PLC I/O Testing (Auto Position)



Force/Override PLC Outputs

Use the PLC programming software to
force the AUTO output ON (if it isn't already). Then, force the START output ON. The motor starter should energize (the indicator light should come on or you can test the resistor for voltage.)

Verify the STOP Input

Force the STOP output ON (or release the START output). The motor starter should de-energize.

Verify the AUTO Input

if the AOH switch is in "Off" or "Hand", the PLC should not be able to start the motor. The PLC's "Start" signal should be ignored.4.

Troubleshooting

If the motor starter doesn't respond as expected, double-check your wiring against the schematic. Use a multimeter to trace the voltage in the control circuit and identify where the signal is being interrupted. Verify that the PLC outputs are actually switching as commanded. Check for blown fuses in the control circuit.

Important Considerations



PLC Programming

Ensure the PLC logic is correct for controlling the motor in Auto mode.

Interlocks

Many motor starter circuits have interlocks (e.g., overload relay contacts). Make sure these are closed (or bypassed for testing purposes only, and then re-enabled) so they don't prevent the starter from energizing.


Overload Protection

This testing procedure is for FUNCTIONAL testing, not for verifying overload protection. That requires a separate test with a motor load.

Control Voltage

Be extremely careful to use the correct control voltage for your indicator light or resistor. Using the wrong voltage can damage the components or create a safety hazard.


Professional Help

If you are not comfortable working with electrical wiring, seek the assistance of a qualified electrician or automation technician.

Example Scenario (24VDC Control Circuit)


Let's say you have a 24VDC control circuit.1. You would connect a 24VDC indicator light in series with the motor starter coil (A1 and A2 terminals).
2. With the AOH in "Hand", you'd press the "Start" pushbutton. If the wiring is correct, 24VDC would flow through the start button, through the indicator light, through the starter coil, and back to the 24VDC power supply return. The indicator light would turn on.3. With the AOH in "Auto", you'd use the PLC software to force the AUTO output and START output ON. If the wiring is correct, 24VDC would flow from the power supply, through the AUTO contacts in the AOH switch, through the PLC START output, through the indicator light, through the starter coil, and back to the 24VDC power supply return. The indicator light would turn on.

Final Steps



Document Everything

Record your test results. This is essential for troubleshooting and future maintenance.


Remove Temporary Load

Once you've completed the testing, remove the indicator light or resistor.

Reinstall Covers

Make sure all covers and safety guards are properly reinstalled.


Energize Motor Cables:
Once you're confident in the control circuit, you can connect the motor power cables and perform a final test with the motor running (under supervision).Remember to prioritize safety throughout the testing process. Good luck! Flag for review