Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Load Analysis for PV Panel

User: Prototype1, Location: Kansas City

Asked on: Wednesday, December 4, 2024 at 9:09 am EST
Answered on: Thursday, March 6, 2025 at 5:53 am EST

Question: Can you please help and review this? I am the only EE at my job and not sure If I am doing it right. This is my first time sizing a PV panels.Load Analysis for PV Panels:Load analysis for the public latrine in the park, calculate the total electrical load of the building. Calculate the load of each device:GFCI Two duplex receptacles (men's and women's restrooms): 2 x 2 x 120V x 20A = 960W (assuming 20A per receptacle)LED lights: assume 10-15 LED lights, each consuming 10W = 100-150W (let's use 125W)Blow hair dryers: assume 2 hair dryers, each consuming 1500W = 3000W (let's use 3000W)Exhaust fans (2 x 50 CFM): assume 2 fans, each consuming 50W = 100W (let's use 100W)Small boiler: assume a small boiler consuming 2000W = 2000W (let's use 2000W)Calculate the total load:Total load = 960W (receptacles) + 125W (LED lights) + 3000W (hair dryers) + 100W (exhaust fans) + 2000W (boiler) = 6185WDetermine the load factor:Load factor is the ratio of the average load to the peak load. For a public latrine, a load factor of 0.5-0.7 is reasonable. Let's use 0.6.Adjusted load = Total load x Load factor = 6185W x 0.6 = 3711WDetermine the required PV array size:To determine the required PV array size, we'll need to calculate the total energy consumption per day.Assume the public latrine operates for 12 hours a day (8am-8pm).Total energy consumption per day = Adjusted load x Operating hours = 3711W x 12h = 44532 Wh or 44.53 kWhDetermine the PV array size:To calculate the required PV array size, we'll need to know the peak sun hours (PSH) available at the site. Assume an average PSH of 5 hours per day.Required PV array size = Total energy consumption per day / PSH = 44.53 kWh / 5h = 8.91 kWSelect the PV panel size:Let's assume we'll use a standard PV panel size of 300W.Number of PV panels required = Required PV array size / PV panel size = 8.91 kW / 0.3 kW = 29.7 panelsTo account for efficiency losses and other factors, let's round up to the nearest whole number. We'll need approximately 30 PV panels.PV Panel Configuration:30 PV panels x 300W each = 9 kW total capacityArray configuration: 5 rows x 6 columns (30 panels total)Inverter size: 9 kW or larger to accommodate the total PV array capacity

Okay, let's review your PV panel sizing calculations. Overall, your approach is logical, and you've considered the key factors. However, there are a few areas where we can refine the assumptions and improve accuracy.

Here's a breakdown of your calculations with suggestions



1. Load Analysis



GFCI Receptacles

`2 x 2 x 120V x 20A = 960W` This is where you'll want to be careful. While each receptacle
could draw 20A (assuming a 20A breaker protects them), it's very unlikely they will constantly draw that much. Using the full breaker rating for continuous load is overly conservative and will significantly inflate your PV system size.

Recommendation

Instead of assuming 20A per receptacle, consider the actual expected load. What will people realistically be plugging in? Hair dryers are a known high-load item. Other items might be phone chargers, small appliances, or cleaning equipment. A more realistic assumption would be to allocate a certain amount of power for each receptacles. `2x2x120Vx 5A =2400W` Use a maximum value.

Code considerations

Follow NEC, CEC, or local electric codes.


LED Lights

`assume 10-15 LED lights, each consuming 10W = 100-150W (let's use 125W)` This seems reasonable.

Blow Hair Dryers

`assume 2 hair dryers, each consuming 1500W = 3000W (let's use 3000W)` This is likely a correct estimation for a high power device like a dryer.


Exhaust Fans

`assume 2 fans, each consuming 50W = 100W (let's use 100W)` This is also likely correct.

Small Boiler

`assume a small boiler consuming 2000W = 2000W (let's use 2000W)` This seems reasonable.

2. Total Load

You correctly sum the individual loads. However, it's important to revisit the receptacle load calculation above.

Recommendation

Re-calculate your total load once you've adjusted the receptacle load.

3. Load Factor

`Load factor is the ratio of the average load to the peak load. For a public latrine, a load factor of 0.5-0.7 is reasonable. Let's use 0.
6.` This is a good approach. The load factor accounts for the fact that not everything will be running at full power all the time. 0.6 is a reasonable starting point.


Improvement

Consider
when the latrine will be busiest. Are there specific peak usage times (e.g., weekends, after events in the park)? This knowledge can help you refine your load factor estimate.

4. Total Energy Consumption

`Assume the public latrine operates for 12 hours a day (8am-8pm).` Okay, but is this accurate? Does it operate even if the park is closed? `Total energy consumption per day = Adjusted load x Operating hours = 3711W x 12h = 44532 Wh or 44.53 kWh` Correct math, but this is highly dependent on the adjusted load, which, in turn, depends on the realistic receptacle load.

Improvement

Consider seasonal variations. Are there days when the latrine is used more or less (e.g., colder weather, events)?

5. PV Array Sizing

`To calculate the required PV array size, we'll need to know the peak sun hours (PSH) available at the site. Assume an average PSH of 5 hours per day.` This is a critical assumption. 5 PSH is a good starting point, but you must get accurate solar irradiance data for the specific location. You can use resources like:

PVWatts Calculator (NREL)

This free online tool allows you to input location data (latitude, longitude), tilt angle, and azimuth angle to get a more accurate estimate of PSH.

SolarGIS

A commercial service with more detailed solar irradiance data.
`Required PV array size = Total energy consumption per day / PSH = 44.53 kWh / 5h = 8.91 kW` Math is correct, but this is very dependent on the PSH and the energy consumption.

Important Considerations



System Losses

You have not accounted for system losses due to wiring, inverter inefficiency, temperature effects on PV panels, and shading. A typical system loss factor is 15-25%. You need to add this to the load calculation.

Battery Storage (If Applicable)

If you're planning battery storage, you need to factor in battery efficiency (charge/discharge losses) and the depth of discharge (DoD) you're willing to allow to prolong battery life.


Equation with Losses Included

To account for system losses, you can use a more complete formula:`Required PV array size = (Total Energy Consumption per Day) / (PSH System Efficiency)`Where: Total Energy Consumption per Day is in kWh. PSH is the peak sun hours. System Efficiency is between 0.75 and 0.85 (representing 75% to 85% efficiency). Use 0.75 for a more conservative estimate.

6. PV Panel Selection

`Let's assume we'll use a standard PV panel size of 300W.` Good starting point. Consider the actual panel you plan to use (make and model) and its voltage and current characteristics for the inverter selection. `Number of PV panels required = Required PV array size / PV panel size = 8.91 kW / 0.3 kW = 29.7 panels` Correct math. `To account for efficiency losses and other factors, let's round up to the nearest whole number. We'll need approximately 30 PV panels.` Rounding up is good practice.

7. PV Panel Configuration

`30 PV panels x 300W each = 9 kW total capacity` Correct. `Array configuration: 5 rows x 6 columns (30 panels total)` This is fine for a simple example, but the actual configuration (series/parallel connections) will be dictated by the voltage requirements of your chosen inverter.

Important

Panel configurations are constrained by the inverter maximum input DC voltage, and MPPT voltage range.

8. Inverter Sizing

`Inverter size: 9 kW or larger to accommodate the total PV array capacity` Correct in principle.

Important

The inverter must be compatible with the PV panel configuration (voltage and current) and the grid voltage (if grid-tied). Also, consider future expansion. Oversizing the inverter slightly can provide headroom for adding more panels later.

Recommendation

Research available inverter sizes and their voltage and current limits.


Safety Considerations

Ensure the inverter is appropriately rated for outdoor use (if applicable) and has the necessary safety certifications.

Summary and Recommendations


Refine Receptacle Load

This is the biggest area for improvement. Use more realistic power consumption values for the receptacles based on the likely appliances to be plugged in.2.

Get Accurate PSH Data

Use PVWatts or similar tools to get location-specific peak sun hours.3.

Incorporate System Losses

Add a system loss factor (15-25%) into your calculations.4.

Validate Operating Hours

Confirm the latrine's actual operating hours and consider seasonal variations.5.

Panel and Inverter Compatibility

Carefully select PV panels and inverters, paying attention to voltage and current requirements and safety ratings.6.

Consult Local Codes and Regulations

Ensure your design meets all applicable electrical codes and regulations.7.

Consider Future Expansion

Think about whether you might want to add more panels or battery storage in the future.8.

Professional Review:
If possible, have your design reviewed by a qualified solar installer or engineer before implementation.By addressing these points, you'll have a more accurate and reliable PV system design for the public latrine. Good luck! Flag for review

Previous Question Next Question