Question: Hello,I have a Horn/Strobe that is rated 15/75 cd. It is 15 cd per UL 1971 and 75 cd per UL 1638. It is not selectable, its rating is just different based on which listing is governing.My question is regarding the change from UL 1971 to UL 1638. Looking through the editions of NFPA 72 UL 1971 seemed to be the go to until the 2019 or so edition when UL 1638 seems to have started to take over regarding requirements for Visual indication. Now at the 2025 edition, UL 1971 is only mentioned in 1 place which is for tactile requirements, everything else is UL 1638.I need a 60cd strobe, I assume since the code has drifted toward the UL 1638 requirements, my horn/strobe listed for 75cd per UL 1638 is fine.
You've accurately observed the shift in NFPA 72 toward UL 1638 for visual signaling device requirements. Let's break down your understanding and the implications for your 15/75 cd horn/strobe: UL 1971 vs. UL 1638
You're correct. NFPA 72 has increasingly favored UL 1638 for visual notification appliances. UL 1971 primarily covers notification appliances for the hearing impaired, focusing on temporal patterns and tactile notification. UL 1638 focuses on visual appliances.
Your 15/75 cd Horn/Strobe
This is where it gets nuanced. The device is listed for 75 cd under UL 1638. However, the key consideration is what type of application you're using the notification appliance in. UL 1971 (Private Mode Emergency Signaling) requires the notification appliance to be installed with a certain light distribution pattern and the coverage requirements are much more stringent than UL 1638. UL 1638 (General Visibility) focuses on the general visibility for general signaling applications such as mass notification systems or wide-area alerting.
Meeting the 60 cd Requirement
If your application falls under a general signaling environment, then
yes, a 75 cd UL 1638-listed strobe likely meets the requirement. However, If you are looking for Emergency Signaling for the hearing impaired and your application requires UL 1971 notification appliances, a device listing for 15cd might require many more notification appliances and/or be rejected by the AHJ.
Recommendation
Consult the AHJ
This is the most important step. Explain the situation to your local Authority Having Jurisdiction (AHJ) – the fire marshal, building inspector, or whoever enforces NFPA 72 in your area. Present them with the device's listing information and your intended application. Ask specifically if a UL 1638-listed device is acceptable in your scenario.2.
Document Everything
Keep a record of your conversation with the AHJ, including the date, the AHJ's name, and their response. This documentation will be vital if questions arise later.3.
Check NFPA 72 (2025)
Carefully review the sections of NFPA 72 (2025) that pertain to visual notification appliances, specifically Chapter 18. Understand the requirements for spacing, placement, and coverage based on the application type. Also, familiarize yourself with any amendments or local ordinances that may apply in your jurisdiction.
4.
Consider the Application
Again, what is the purpose of the horn/strobe? Emergency Fire Evacuation for building occupants? General Signaling for a mass notification system? The application dictates the relevant standard (UL 1971 vs. UL 1638).5.
If in Doubt, Err on the Side of Caution
If the AHJ is unsure or if you're still uncertain after reviewing the code, it's safer to use a strobe specifically listed for 60 cd under UL 1971, if your goal is compliance for emergency evacuation.6.
Consider other solutions. In many installations, the use of addressable notification appliances can change coverage requirements for the space.
In Summary:
While the trend is toward UL 1638, the applicability of your 75 cd strobe depends on the specific application and the interpretation of the AHJ. Don't assume it's automatically acceptable. Consulting with the AHJ is crucial. Flag for review