Topic: 1200A Service from transformer to main switch

User: Sqjlighting, Location: Henderson NV

Asked on: Saturday, December 7, 2024 at 9:53 pm EST
Answered on: Thursday, March 6, 2025 at 6:01 am EST

Question: If I’m running 400ft underground from transformer to 1200A 208/120V 3 Ph 4 W main switchgear, please confirm 4-3” pvc Conduits with 1-500 kcmil and 1-#3/0 ground wire in each? Las Vegas location.

Okay, let's break down the conductor sizing and conduit fill for your scenario in Las Vegas, Nevada, based on the National Electrical Code (NEC). This is an electrical engineering estimate and should be verified with a qualified electrical engineer.

Assumptions



Load

1200A continuous load at 208/120V, 3-phase, 4-wire.


Conductor Material

Copper (most common assumption, but important to specify).

Installation Method

Direct buried PVC conduit.


Ambient Temperature

Assume high, given Las Vegas. We will use 46-50°C (114.8-122°F) for our calculations.

Voltage Drop

Assuming 3% voltage drop maximum.


NEC Code

Using the latest NEC edition, typically 2023.

No other conductors in the conduit (control wires, etc.)
Calculations and Code Considerations


Ampacity Requirements

Each phase conductor needs to carry 1200A.2.

Conductor Sizing (Initial)

Based on NEC Table 310.16 (Ampacity of Insulated Conductors), a single 500 kcmil copper conductor with 75°C insulation (THHN/THWN-2, XHHW-2, etc.) has an ampacity of 380A before derating.3.

Number of Conductors

1200/380 = 3.16 so minimum 4 conductors needed.
4.


Derating



Ambient Temperature Correction

NEC Table 310.15(B)(1). For an ambient temperature of 46-50°C (114.8-122°F), the correction factor for 75°C insulation is approximately 0.
79.


Conduit Fill (Number of Conductors in Raceway)

NEC Table 310.15(C)(1). For 4 current-carrying conductors in a raceway, the derating factor is 0.
80.


Total Derating

0.79
0.80 = 0.632

Adjusted Ampacity

380A
0.632 = 240.16A5.

Number of Conductors needed
1200/240.16 = 4.99 so minimum 5 conductors needed.
6. Voltage Drop

NEC Informative Annex C provides formulas for voltage drop calculations. For a 208V system, a 3% voltage drop is about 6.24V. Voltage drop calculation requires conductor length, current, conductor size, and conductor material.7.

Grounding Conductor (Equipment Grounding Conductor - EGC)

Based on NEC Table 250.122, for a 1200A overcurrent protective device, the minimum size copper EGC is #3/0 AWG.

Analysis and Recommendations

Using four 500 kcmil conductors per phase is not adequate based on our conservative estimate for ambient temperature for ampacity.

500 kcmil conductors are not large enough to meet code.
Possible Solutions (Requires Detailed Calculation and Engineering Review)


Increase Conductor Size

Consider larger conductors (e.g., 600 kcmil or larger) to increase ampacity before derating, and recalculate everything. This might still require multiple conductors per phase.2.

Parallel Conductors

The NEC permits parallel conductors (310.10(H)) but requires they be the same length, conductor material, circular mil area, insulation type, and be terminated in the same manner. This can make installation more complex and expensive. If using parallel conductors: You must ensure proper termination methods and torqueing of all connections. You must consider magnetic fields and grouping of conductors to minimize eddy current heating in metallic enclosures (if any are used). If there are enclosures, separate conduits for each phase.3.

Reduce Ambient Temperature

If possible, improve the cooling or ventilation of the conduits to reduce the ambient temperature. This would increase the ampacity of the conductors. Difficult with direct burial.4.

Calculate Voltage Drop

Conduct a voltage drop calculation for 5 conductors per phase. If the voltage drop is greater than 3% then you need to increase conductor size further.5.

Adjust Assumptions

Review the ambient temperature assumptions. Real-world measurements may show a lower actual temperature, allowing for less derating. Be very conservative.

Revised Recommendation (Subject to Engineering Review)

Given your parameters, a preliminary recommendation for a starting point for a qualified engineer to review would be:

Number of Conduits

Determine number needed based on conductors after running voltage drop calculations.


Conductor Size

Likely requires minimum 5-500 kcmil conductors per phase.

Grounding Conductor

#3/0 AWG copper in
each conduit.

Conduit Size

3" PVC conduit is likely adequate for conductor fill with the recommended conductors, but must be verified using NEC Chapter 9, Table 1.

Crucial Steps


Hire a Qualified Electrical Engineer

This project requires a professional engineer experienced in power distribution design and familiar with the NEC, local amendments, and Las Vegas-specific regulations.2.

Detailed Load Analysis

Perform a precise load analysis to determine the actual continuous load. Oversizing significantly increases costs.3.

Voltage Drop Calculations

Perform accurate voltage drop calculations using the actual load, conductor length, conductor size, and other relevant factors.4.

Coordination Study

Ensure that the overcurrent protective devices (breakers) are properly sized and coordinated to protect the conductors and equipment.5.

Permitting and Inspection

Obtain the necessary permits and inspections from the local authorities. Compliance with local codes is essential.

Disclaimer:


This information is for general guidance only and should not be considered a substitute for professional electrical engineering advice. Always consult with a qualified engineer and comply with all applicable codes and regulations. I am not liable for any damages resulting from the use of this information. Flag for review