Topic: Simple Wall Oven Question

User: infinity, Location: New Jersey

Asked on: Tuesday, December 10, 2024 at 9:16 am EST
Answered on: Thursday, March 6, 2025 at 6:05 am EST

Question: Q. An 240 volt electric wall oven has a KW rating of 7.2 Kw. What is the minimum branch circuit size permitted when used on a 120/240 volt system?a) 25 ampsb) 30 ampsc) 50 ampsd) 35 ampse) 40 amps

Here's how to solve this problem:1. Convert kW to Watts

7.2 kW 1000 W/kW = 7200 W2.

Calculate Amps

Amps = Watts / Volts Amps = 7200 W / 240 V = 30 amps3.

Oven Branch Circuit Rating Requirements

* The oven branch circuit rating is the branch circuit size required to supply that appliance. The oven nameplate rating (7.2KW) is used to determine the correct branch circuit.

Therefore, the answer is (b) 30 amps.