Topic: Trying to reduce 2 services to 1

User: SforresterBHC, Location: Bullhead City Az

Asked on: Tuesday, December 10, 2024 at 2:23 pm EST
Answered on: Thursday, March 6, 2025 at 6:07 am EST

Question: Hello all, I work for a city utilities department, and I have a project I am working on concerning ATS.I am trying to install ATS at all water distribution sites, all is good, except for 1. The site in question is fed from 2 sources, 1) 480v 400A 3 phase service from overhead powerlines that is used to power transfer pumps and 2 well sites close to the feed site, 2) a 120v/240v single phase 125A service from the street that is used for the main site 120/240v loads(lighting, RTU Cab, 208/230v AC, 120/240V sub panel on chlorine room, and recepts with a 240v welder recept in the work shop). The 2 well sites are no longer in operation and are completely abandoned, the 2 transfer pumps used at feed site are only 30A a piece. I want to set it up to only need 1 generator to power in a black out. My question is: is it more efficient to change the site over to being fed from the 3 phase 480v source with a 3 phase step down 120/208 panel and a couple buck-boost transformers for the 240v loads, or keep the 120/240v source and install a small transformer that only gets power when generator is in use that is also tied to a manual transfer switch to power RTU, Chlorine Room and lights only. First configuration would be simpler and straight forward IMO, but second could be less work and possibly cheaper (which is what I am told is the main factor in making this change).

Okay, this is a complex but solvable problem. Let's break down the pros and cons of each approach and then recommend a path forward, keeping your city's budget in mind.

Understanding the Situation Goal

Power the entire site with a single generator during outages.


Current Configuration



480V 3-Phase (400A)

Powers transfer pumps (low load) and
potentially unused well sites.

120/240V Single-Phase (125A)

Powers essential site loads (lighting, RTU, A/C, chlorine room, receptacles, welder).

Challenge

Integrating the two voltage systems into a single generator backup solution.


Important Note

The welder receptacle (240V) is a critical load to consider and should be included in the generator setup.

Option 1: Consolidate to 480V 3-Phase with Step-Down and Buck-Boost Transformers
Description

Utilize the existing 480V 3-phase service as the primary feed for the entire site. Install a 480V 3-phase to 120/208V 3-phase step-down transformer to power most of the 120V and 208V loads. Use buck-boost transformers to provide the necessary 240V for the A/C, chlorine room sub-panel, and welder receptacle.

Pros



Simplified Generator Solution

Only one generator size needed for the entire site.

Cleaner Design

Eliminates the need for two separate services and their associated panels/switchgear.


Potential for Future Expansion

More capacity available on the 480V system if needed.

Better Power Quality

Balanced 3-phase power can improve the lifespan and efficiency of some equipment.


Cons



Higher Upfront Cost

Step-down transformer and buck-boost transformers are significant expenses.


More Complex Installation

Requires more extensive electrical work and potentially larger conduit runs.

Efficiency

Transformers have losses, leading to some efficiency loss.

Option 2: Keep 120/240V Service and Add a Small Transformer for Generator Use Only
Description

Maintain the existing 120/240V single-phase service as the primary feed. Install a small transformer (e.g., 240V to 120/240V) that is ONLY powered when the generator is running. This would provide the 120/240V for essential loads when utility power is lost. Install a manual transfer switch to select which essential loads (RTU, chlorine room, lights) get power from the existing service OR from the generator via the small transformer.

Pros



Potentially Lower Initial Cost

Smaller transformer and manual transfer switch are less expensive than a large step-down transformer and buck-boost units.


Less Extensive Electrical Work

Less re-wiring and re-routing of circuits.

Cons



More Complex Control Logic

Requires a carefully designed control system to ensure the transformer is only energized when the generator is running and the manual transfer switch is in the correct position.

Limited Capacity

The size of the small transformer will limit the amount of load you can run from the generator.


Manual Intervention Required

Someone must manually switch the transfer switch during an outage, which may not be acceptable in a critical infrastructure setting.

Welder Unaddressed

This option doesn't easily address the 240V welder receptacle. You'd need to either exclude it entirely or add a separate small generator just for it, which defeats the purpose.

Analysis and Recommendation


Given the need to power the entire site (including the welder) and the potential need for future expansion, Option 1 (consolidate to 480V 3-phase) is the
better long-term solution, despite the potential for higher upfront costs.

Here's why



Scalability

Consolidating to 480V provides ample capacity for future expansion.

Reliability

A single, well-designed system is generally more reliable than a cobbled-together system with multiple transformers and manual switching.


Automatic Operation

With proper ATS selection, the transfer to generator power can be fully automated, eliminating the need for manual intervention. This is critical for a water distribution site.

Welder Integration

Easily handles the 240V welder receptacle.


Simplification

While the initial installation is more complex, the overall system is simplified from a maintenance and troubleshooting perspective.

Cost Mitigation Strategies for Option 1



Negotiate with Suppliers

Get quotes from multiple suppliers for transformers and ATS equipment.


Consider Used Equipment

Check with reputable electrical supply companies for used but tested and certified transformers and ATS equipment. (Be cautious and get professional verification of condition and suitability.)

Phase the Project

If budget is severely constrained, consider phasing the project. Install the 480V-to-120/208V transformer
first. Run the existing 120/240V loads off this new 3-phase 208V panel using the buck-boost transformers, while still using the existing 120/240V service as the main feed. Then, in a later phase, install the ATS and generator.

Evaluate Load Requirements

Accurately assess the actual load requirements of the site. You may be able to slightly downsize the transformers if some loads are intermittent or lower than initially estimated.

Steps to Take


Detailed Load Calculation

Conduct a comprehensive load calculation for all electrical equipment on the site. Be precise. Don't overestimate.2.

Consult with a Qualified Electrical Engineer

A licensed electrical engineer should review your load calculations, design the electrical system, and ensure compliance with all applicable codes.

This is essential for safety and regulatory compliance.
3. Get Multiple Quotes

Obtain detailed quotes for both options from qualified electrical contractors. Include all materials, labor, permits, and testing.4.

Life-Cycle Cost Analysis

Perform a life-cycle cost analysis that considers the initial cost, operating costs (including electricity and maintenance), and the expected lifespan of each option.5.

Present the Findings

Prepare a clear and concise presentation of your findings for the decision-makers in your city's utilities department. Highlight the benefits of each option, the costs, and your recommendation, with justification.

Important Considerations



Code Compliance

Ensure all work complies with the National Electrical Code (NEC) and any applicable local codes.


Safety

Safety is paramount. Use qualified electricians and follow all safety procedures.

ATS Selection

Carefully select the appropriate Automatic Transfer Switch (ATS) for your application. Consider factors such as ampacity, voltage, phase, and features such as bypass isolation.


Generator Sizing:
Proper generator sizing is critical. Work with a qualified generator supplier to select a generator that can meet the site's peak load requirements.By following these steps, you can make an informed decision that provides a reliable, efficient, and cost-effective backup power solution for your city's water distribution site. Remember, while the initial cost is important, the long-term reliability, safety, and scalability of the system are even more crucial. Good luck! Flag for review