Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Feeder Sizing (80% rule)

User: RogerRoger, Location: Boise, ID

Asked on: Friday, December 13, 2024 at 12:21 pm EST
Answered on: Thursday, March 6, 2025 at 6:16 am EST

Question: I'm reviewing the electrical code to teach other engineers the rules on feeder sizing and want to verify I'm still on the right track. It seems like there's still a lot of confusion among my colleagues with the "80% breaker standard". I'm using NEC 2023.Example 1:The below table shows a feeder calculation. Per my understanding of 215.2, the feeder size would be determined by taking the noncontinuous loads plus 125% of the continuous loads. I first determine the noncontinuous load demand factors per article 220 and add those loads to 125% of the continuous load. The final demand value comes out to 284.5A. Other engineers say that breakers are 80% rated and have required that the minimum feeder size be determined by taking an additional 125% of the 284.5A, resulting in a feeder size of 400A (next size up from 355.63). Since I've already applied the 125% to the continuous loads in the calculations, that seems redundant. In this case, I would have the minimum feeder size be the next size up from the demand - 300A. Please note I'm just wanting to determine the minimum feeder size and not taking into account the good design practice of leaving 20%-25% spare capacity for future additions.Non-Continuous & Continuous Feeder (Non-Dwelling)LOAD CLASSIFICATIONCONNECTED LOADDEMAND FACTORESTIMATED DEMANDR - RECEPTACLE LOAD20000 VA0.75 (220.47)15000 VAX - LARGEST MOTOR20000 VA1.2525000 VAMN - MISC NONCONTINUOUS50000 VA150000 VAMC - MISC CONTINUOUS10000 VA1.2512500 VATOTAL (VA)100000 VA102500 VATOTAL (A @ 208V/3-ph)277.6 A284.5 A

You are absolutely correct in your understanding of the NEC and your approach to feeder sizing. Your colleagues are misinterpreting the "80% breaker standard."Here's a breakdown to clarify: Your Calculation

You correctly calculated the required feeder current as 284.5 amps after applying the appropriate demand factors for non-continuous loads and the 125% factor for continuous loads. This is the crucial step outlined in 215.2 and 210.19(A)(1) Exception No. 1.


The Misunderstanding of the "80% Breaker Standard"

The "80% breaker standard" refers to the listing requirements for circuit breakers and specifically addresses the maximum continuous load allowed on the breaker, per 210.20(A) and 215.
3. It's not about arbitrarily increasing the feeder size beyond what is required by the calculated load. It's about selecting a breaker that can handle the already calculated continuous load. The breaker must be rated not less than 125% of the continuous load. In your example, the 125% of the continuous load is already taken into account within your feeder calculation.


215.2(A)(1) & 210.19(A)(1) Exception No. 1

Explicitly states to increase the
continuous load by 125%. You've already done that.

Breaker Selection

To elaborate, this means if you have a 20A circuit breaker in a panel, and if you plan to run it at a continuous load (anything running for 3 hours or more), you cannot load it beyond 80% of its capacity (16A).

Minimum Feeder Size

Since your calculation already accounts for the 125% factor for continuous loads, the
minimum feeder size is indeed the next standard size up from the calculated demand of 284.5A, which is 300A. Note that 310.16 has to be followed for ampacity ratings.

Good Design Practice vs. Code Minimum

You're right to distinguish between meeting the minimum code requirements and good design practice. While the minimum feeder size is 300A, as calculated, adding a 20-25% buffer for future expansion is a prudent engineering decision, but it's not strictly required by the code.

In Summary

Your colleagues are incorrectly applying the 125% factor to the entire calculated load instead of only applying it to the continuous loads during the load calculation process. You are correct. You've already accounted for the continuous loads in your initial calculations.

How to Explain to Your Colleagues


Refer to 215.2(A)(1) and 210.19(A)(1) Exception No. 1

Point out that the code explicitly instructs increasing only the continuous load by 125% during the initial load calculation.2.

Explain the Purpose of the 80% Rule

Explain that the "80% rule" (or the 125% factor in code language) is about the breaker's ability to handle continuous loads and that this has already been factored into the load calculations.3.

Walk Through an Example

Use your example and clearly show how you applied the 125% factor to the continuous load only.4.

Clarify Breaker Selection vs. Feeder Sizing:
Emphasize that the minimum required ampacity of the conductors is determined by the load calculations (including the 125% factor for continuous loads), while the breaker selection must also consider the continuous load requirements.By clearly explaining these points and referring to the relevant sections of the NEC, you should be able to clear up the confusion and ensure everyone is following the correct procedures for feeder sizing. Flag for review

Previous Question Next Question