Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Cable for rental generator

User: anbm, Location: TX

Asked on: Friday, December 13, 2024 at 1:21 pm EST
Answered on: Thursday, March 6, 2025 at 6:17 am EST

Question: Looking for 480V, 400A outdoor rated cable to connect between a rental generator and 800A panel inside the building,probably will run (2) sets of this cable in parallel. Anyone knows any cable brand name that can do the job? Thank you,

Okay, let's break down the requirements and identify suitable cable options for your 480V, 400A (or effectively 200A per set when running two in parallel) outdoor-rated generator connection.

Understanding the Requirements Voltage

480V (3-phase likely, but specify for certainty).


Current

400A total (200A per parallel set).

Outdoor Rated

Must withstand weather conditions (sunlight, rain, temperature extremes). "Outdoor Rated" typically means a jacket suitable for direct burial (even if you are not burying it) or exposure to the elements.


Application

Connecting a rental generator to an 800A panel. This is a temporary or semi-permanent connection.

Installation

Likely involves some flexibility for movement and connection/disconnection.


Panel size

800A, this will determine the lugs you use to terminate the cable.

Run distance

This is critical. The longer the run, the larger the cable you will need to minimize voltage drop. Provide this and I can calculate voltage drop for you.


Cable Type

You'll need conductors for L1, L2, L3, Neutral (if required) and Ground.

Cable Options and Considerations


Given the temporary/semi-permanent nature of the connection and the need for flexibility, the best options are usually variations of portable power cable. Here are some common types and considerations:1. Type W Portable Power Cable

Description: Type W cable is a single conductor cable that is very flexible and designed for portable power applications. It has a tough jacket, and it can be used in wet or dry locations. Advantages: Extremely flexible, durable, readily available. Disadvantages: Requires individual conductors for each phase, neutral (if required), and ground. Requires proper termination with lugs and potentially color-coding/labeling. Sizing: For 200A per conductor, you will likely need a 1/0 AWG or 2/0 AWG copper conductor, or a larger aluminum conductor. The specific size depends on the temperature rating of the terminations at both ends (generator and panel). Typically terminations are rated for 75°C or 90°C. Use a 75°C ampacity rating as a conservative starting point. Consult the NEC (National Electrical Code) Table 310.16 for ampacities. Example Brand: Southwire, General Cable, Priority Wire & Cable. Search for "Type W Cable" at electrical distributors.2.

Type SC (Service Cord) or Type G-GC (Grounding Cable - Ground Check)
Description: These cables have multiple conductors within a single jacket. SC is a service cord. G-GC usually includes a ground check conductor for safety interlocks (more common in mining applications, but extremely rugged). Advantages: All conductors are in one cable, simplifying installation. Very durable. Disadvantages: Less flexible than individual Type W conductors. May be more expensive. Can be harder to find in the exact conductor count and ampacity you need. Sizing: Similar ampacity considerations as Type W. Look for cables with conductors rated for at least 200A at 75°C or 90°C. Example Brands: Similar manufacturers as Type W. Search for "Type SC Cable" or "Type G-GC Cable".3. DLO (Diesel Locomotive) Cable

Description: Very flexible, single-conductor cable, designed for harsh environments. Good for high-current applications. Advantages: Extremely flexible and durable. Disadvantages: Similar to Type W in that you need to manage individual conductors. Can be more expensive than Type W. Sizing: Same ampacity considerations as Type W and SC. Example Brands: Similar manufacturers as Type W. Search for "DLO Cable".

Important Considerations



NEC (National Electrical Code)

All installations must comply with the NEC. Article 310 covers conductor ampacity. Article 400 covers flexible cords and cables. Article 250 covers grounding and bonding. You need to consider derating factors for ambient temperature, grouping of conductors, etc.

Ampacity Derating

If the cables will be bundled together or exposed to high ambient temperatures, you will need to derate the ampacity of the conductors according to the NEC.


Voltage Drop

Calculate voltage drop based on the length of the run and the cable size. Excessive voltage drop can damage equipment. Use a voltage drop calculator. Aim for less than 3% voltage drop.

Grounding

Ensure proper grounding between the generator and the building's grounding system. This is critical for safety. The grounding conductor must be sized according to the NEC.


Overcurrent Protection

The 800A panel should have appropriate overcurrent protection (circuit breakers or fuses) to protect the cable and the equipment connected to the panel. The generator should also have its own overcurrent protection.

Terminations

Use properly rated lugs and connectors for the cable size and conductor material (copper or aluminum). Use a crimping tool designed for the lugs. Make sure the lugs are compatible with the terminals on the generator and the panel. Apply antioxidant paste to aluminum conductors. Torque all connections to the manufacturer's specifications.


Professional Installation

This type of electrical work should be performed by a qualified electrician who is familiar with the NEC and local codes.

Local Codes and Permits

Check with your local authorities for any required permits or inspections.


Rental Company Requirements

Check with the rental generator company for any specific requirements they have regarding cable type, connections, and grounding. They may even provide the cable as part of the rental.

Neutral

Determine if the generator is providing a separately derived neutral. If so, it must be properly bonded at the generator and handled correctly.

Steps to Take


Determine the exact voltage and phase configuration
of the generator (e.g., 480V 3-phase Wye, 480V 3-phase Delta).2. Measure the distance between the generator and the panel.3. Consult the generator's specifications to determine its grounding requirements.4. Consult a qualified electrician to perform the installation. They can help you select the correct cable size, terminations, and grounding methods, and ensure that the installation complies with all applicable codes.5. Obtain necessary permits from your local authorities.

Example Scenario (Illustrative)

Let's say you have a 480V, 3-phase generator and a run of 100 feet. You decide to use two parallel sets of Type W cable. You want to keep voltage drop below 3%.
You might need 1/0 AWG or 2/0 AWG copper Type W cable per phase (check ampacity at 75°C or 90°C based on terminations). You would need a separate ground conductor (sized according to NEC 250.122). You would need properly rated lugs for 1/0 AWG or 2/0 AWG copper.

Disclaimer: I am an AI chatbot and cannot provide professional electrical advice. This information is for general guidance only. Always consult with a qualified electrician for any electrical work. Flag for review

Previous Question Next Question