Topic: Residential Service and generator

User: Sandlamb, Location: Ohio

Asked on: Monday, December 16, 2024 at 11:10 am EST
Answered on: Thursday, March 6, 2025 at 6:22 am EST

Question: Hi, all. Thanks in advance for the help.Customer is wanting to upgrade their service and I’ve come across this subpanel fed off a 2 pole 100 A breaker with #2 SER feeding panel containing all circuits for generator to be operated off manual Transfer switch.Looking for some advice on tying this all back together and being code compliant. I usually just do a generator and ATS catching the entire house or a generator inlet receptacle. First time seeing this set up. Photos attached

Okay, I understand the situation. You have a customer wanting to upgrade their electrical service and they currently have a generator setup with a subpanel fed by a 100A breaker in their main panel, using #2 SER cable, and connected to a manual transfer switch. You need to figure out how to integrate this existing setup into the upgraded service while remaining code compliant.Here's a breakdown of the considerations and some approaches

Key Considerations and Code Implications:
NEC 220.87 Existing Load Calculation

Because the service is being upgraded you must perform a new load calculation to determine if the service is adequate to handle the additional loads after the upgrade. Because there is a generator installed on the property it is advantageous to use NEC 220.87 to establish the demand.


NEC 215.2(A)(1) Feeder Overcurrent Protection

The 100A breaker feeding the subpanel must be properly sized and rated for the load served by the subpanel. The 100A OCPD can not be larger than the ampacity of the #2 SER cable.

NEC 310.16 Conductor Ampacity

Check the ampacity of the #2 SER cable. Assuming it's copper, the
maximum ampacity is typically 90A (using the 75°C column in Table 310.16). If it's aluminum, it's typically 75A. This is a critical point.

The 100A breaker protecting the #2 SER cable is potentially a code violation if the conductors are not rated for 100A.
The conductors would require an overcurrent protection device to be rated at 90A or less depending on the type of conductors. NEC 250.32 Grounding of Detached Buildings

Since this appears to be a detached structure, ensure that the grounding system meets the requirements of NEC 250.32. This means:

Grounding Electrode System

The subpanel at the detached building
must have its own grounding electrode system (ground rod, etc.).

Separation of Neutrals and Grounds

The neutral and ground bars in the subpanel must be separated. The neutral conductor should not be bonded to the subpanel enclosure.

Four-Wire Feeder

The feeder to the subpanel must include a ground wire (equipment grounding conductor) in addition to the two hots and the neutral.


Transfer Switch Compliance

The manual transfer switch must be listed for its intended use. It must reliably isolate the generator power from the utility power to prevent backfeeding. Inspect the transfer switch for proper installation and labeling.

Load Calculation (Subpanel)

Perform a load calculation for the subpanel itself. Verify that the existing 100A feed is adequate for the connected loads. If the upgrade adds significant load to the subpanel, you might need to increase the feeder size and breaker.


Generator Sizing

Ensure the generator is appropriately sized for the loads connected to the subpanel. It's common for generators to be undersized, leading to problems under heavy load.

Permitting and Inspection

Don't forget to obtain the necessary permits for the service upgrade and have the work inspected by a qualified electrical inspector.

Possible Approaches and Recommendations


Address the #2 SER/100A Breaker Issue IMMEDIATELY

This is the most urgent. You
cannot leave a situation where the breaker exceeds the ampacity of the wire.

Option A: Reduce Breaker Size

Change the 100A breaker in the main panel to a 90A breaker (if #2 copper) or a 75A breaker (if #2 aluminum). This is the easiest and cheapest short-term fix if the existing loads on the subpanel allow it.

Option B: Upgrade Feeder

Replace the #2 SER cable with a larger gauge wire that is rated for 100A or more. This is the correct long-term solution, especially if the subpanel loads are close to 100A.2.

Evaluate Subpanel Load Calculation

Perform a thorough load calculation for the subpanel. This will determine if the existing 100A feed is sufficient or if you need to increase it. Consider the NEC's load calculation methods for dwellings (Article 220).3.

Detached Building Grounding

Carefully inspect the grounding at the subpanel in the detached building. Ensure: Separation of neutral and ground. Properly sized ground wire running with the feeder. Local grounding electrode system (ground rod, etc.).4.

Integration with New Service

After addressing the above issues, you'll integrate the existing subpanel feed into the new main service panel. The 90A or less breaker in the main panel that feeds the subpanel would be re-located into the new upgraded main panel. Make sure the new panel has sufficient space and is properly sized for the overall load.5.

Consider an Automatic Transfer Switch (ATS)

While the existing manual transfer switch is functional, discuss the advantages of an ATS with the customer. ATS systems provide seamless power transfer during outages, eliminating the need for manual intervention. This is generally a preferred solution for convenience and reliability. However, it also significantly increases the cost.

Important Considerations for Quoting



Be Thorough

Clearly outline
everything you are going to do to bring the system up to code. Don't just quote for the service upgrade itself. Include the necessary work on the subpanel feeder and grounding.

Include Options

Present the customer with options (e.g., reducing breaker size vs. upgrading feeder, manual vs. automatic transfer switch).*

Explain Code Requirements

Help the customer understand why these upgrades are necessary for safety and code compliance.

In summary, focus on


Addressing the undersized feeder issue immediately.
2. Verifying the grounding is correct.3. Ensuring adequate load capacity for both the subpanel and the generator.4. Proper integration of the existing setup into the new service panel.

By addressing these points, you'll ensure a safe, code-compliant, and reliable electrical system for your customer. Good luck!Disclaimer: I am an AI Chatbot. Consult with a licensed electrician for all electrical work and to ensure compliance with local codes and regulations. Never work on electrical systems unless you are qualified and have taken all necessary safety precautions. Flag for review