User: Grootsquad, Location: South East
Asked on: Tuesday, December 17, 2024 at 9:49 am EST
Answered on: Thursday, March 6, 2025 at 6:25 am EST
Question: I recently walked through a job where a 670’ fixed pier has been constructed straight out to where a gazebo/sub panel will be located for a few general outlets and lights. From there will eventually be a floating dock beyond it with possible shore power in the future (brings us to about 700’ straight out from beginning of fixed pier). Before the ramp down to floating dock there is a 90 degree turn to the south and 128’ where will be 8 boat slips/4 fingers on this fixed pier that will not supply shore power, only lifts for dry storage. There will be a new service no more than 20-30’ from fixed pier entrance that will be dedicated for the pier. The lifts will be standard 240v/2p15a. I plan to use Benders Marina Guard control panel and CTs for the 100mA GFPE protection of feeder. My question is sizing on this run. It’s very long obviously to the sub panel and it is straight. 2.5” PVC with several expansion fittings (6-7) and my calculation on 250kcmil has a 7.2 volt drop on voltage that is usually already pretty jacked up around these parts and that’s feeding a 100amp sub panel at minimum. In all reality there will be little neutral current and there will not be eight boat lifts running at the same time. The lighting that leads to gazebo/boats will be solar so no load there only the few outlets/lights at gazebo. I’m thinking I could get away with two 3/0 copper THHWN conductors and a #1 grounded conductor and #6 EGC, but I wanted to see/hear thoughts from anyone that may have been in a similar situation in the past and willing to help! This is for someone’s personal propertyThanks in advance
Okay, this is a challenging but interesting project! Let's break it down and analyze your sizing concerns. You're smart to be carefully considering voltage drop over that distance. Here's a breakdown of considerations and my thoughts
Understanding the Load and NEC Requirements:
Feeder to Subpanel
The primary feeder that runs out the pier to the gazebo/sub panel is your biggest concern from a voltage drop perspective.
Boat Lifts
Although not powered from the subpanel directly, you still need to account for the load of the boat lifts to determine the overall service size and potential future growth.
Shore Power (Future)
Keep in mind that if you eventually have shore power, you'll need to upgrade your feeder size to accommodate the additional load.
Marina Guard & GFPE
Using Bender's Marina Guard is an excellent choice for GFPE protection. Critical for safety in a marine environment.
Sizing Considerations and Calculations
Here's where the number crunching becomes important. Remember, this is for informational purposes, and a qualified electrical engineer should ultimately sign off on the final design.
Load Calculation
Gazebo Outlets/Lights
Estimate the connected load (in amps) of the outlets and lights at the gazebo. Even if they are rarely used simultaneously, you need a reasonable estimate. Let's assume 20 amps for now as a placeholder. This could be less with LED lighting and limited receptacle usage.
Boat Lifts
Each lift is 15A at 240V. Since you're not powering them directly from the subpanel on the pier, we don't include them in the calculation of the feeder to the subpanel. However, you'll need to account for them when sizing your new service.
Voltage Drop Calculation
Use voltage drop calculators to make sure you are within acceptable limits of 3%. Several online tools can help with this.
Feeder to Subpanel
This is the most important calculation for your question. You're already seeing a 7.2V drop with 250 kcmil. Let's assess the 3/0 THWN option.
3/0 Copper
Assuming a 100A load at 240V, a distance of 670', and using a voltage drop calculator, a 3/0 copper conductor shows to be around a 6% voltage drop! This is way over the 3% allowable limits.
300 KCMIL
This would put you at 3.3% voltage drop for the long feeder run.
Ampacity
Ensure the conductor ampacity is sufficient for the calculated load plus any future expansion plans.
Thoughts and Recommendations
Voltage Drop is King
In this situation, voltage drop is your driving factor. While you might be able to get away with smaller conductors initially based on the very limited gazebo load, it's not a good practice to design at the very edge of the code and you do not want to take away from available voltage to start.2.
Consider 300 KCMIL
The 300 kcmil copper would be recommended for future potential of shore power.3.
Aluminum Consideration
You may want to consider Aluminum for feeder conductors which can bring the cost down.4.
Transformer Option? A step-down transformer at the gazebo could be worth exploring. This would allow you to run higher voltage (and lower current) over the long distance, significantly reducing voltage drop. Then, transform back down to 120/240V at the gazebo. While it adds cost and complexity, it could be more economical in the long run than oversized conductors, especially if you plan for future heavy loads.5. Future Shore Power Planning
The future shore power will require its own feeder.
Other Important Considerations
Marine Environment
Use appropriately rated and listed marine-grade wiring, connectors, and enclosures. Corrosion resistance is paramount.
Grounding/Bonding
Follow NEC Article 555 and Article 250 meticulously for grounding and bonding in a marina environment. This is critical for safety. Pay special attention to equipotential bonding to minimize stray voltage issues.
Overcurrent Protection
Properly size and install overcurrent protection devices (circuit breakers) at both the service entrance and subpanel.
Load Management
Consider the possibility of load management devices if future shore power loads become a concern. This would allow for controlled sharing of power.
In summary, your initial concern about voltage drop is spot on. Oversizing the conductors to minimize voltage drop is crucial for this long run. A 300 KCMIL copper (or equivalent aluminum) is likely necessary. Consult with a qualified electrical engineer who can perform a detailed load calculation, voltage drop analysis, and ensure compliance with all applicable codes and standards. Flag for review