User: photonboy, Location: Berkeley, CA, USA
Asked on: Thursday, December 19, 2024 at 4:04 pm EST
Answered on: Thursday, March 6, 2025 at 6:31 am EST
Question: Just read a 2016 thread here on this question but it wasn't resolved. 2023 690.12 says "The PV system disconnecting means shall simultaneously disconnect the PV system conductors that are not solidly grounded from all conductors of other wiring systems" I'm not sure what is meant by that last part in bold. The neutral is the "grounded conductor" but is it "grounded from all conductors of other wiring systems? What are the other wiring systems being referred to?I have never switched the neutral in any of my installs and rarely see it now but am starting to see it a bit more often. My gut instinct, based on what I'm not sure, is that it should not be broken, but can't find any clear reasoning one way or the other.Any ideas?Thanks.
You're right, that part of 690.12 is confusing and causes a lot of debate. Let's break it down
What "other wiring systems" likely refers to:
AC Utility Grid
This is the most common and, arguably, the only "other wiring system" being considered in this context. Think of the connection point where the PV system interacts with the utility grid.
Other DC sources
While less common, this could also refer to other DC power sources within the building, such as a large battery system unrelated to the PV system.
The Intent Behind the Requirement
The intent of 690.12 is to ensure that, in the event of rapid shutdown, no voltage from the PV system can backfeed into another wiring system. This protects first responders and other personnel from potential shock hazards. By disconnecting all ungrounded conductors of the PV system from any other wiring system, you isolate the PV array during an emergency.
Why the Neutral is a Point of Confusion
Solidly Grounded Systems
The neutral, if present in an AC distribution system, is typically solidly grounded at the service entrance. Because of that single connection point, you have to make absolutely sure that you are not disconnecting it.
Referencing to other "wiring systems"
This is the problem with the wording of the code. When talking about "other wiring systems" in this context, it does not make sense to disconnect your PV system's grounded conductor from itself. So the intent of 690.12 must be with disconnecting it from other wiring systems like the grid.
So, Do You Switch the Neutral? Almost certainly not, unless specifically required by the inverter manufacturer or another section of the code. In most installations in North America, disconnecting the neutral is illegal.
Why not just make it explicitly clear? Different Philosophies
There are varying opinions on the safety benefits of switching the neutral in all scenarios, which is part of the reason for the ongoing debate and less-than-perfect code language. Some argue that it provides an extra layer of safety in certain fault conditions, especially in systems with complex grounding configurations. However, there's a general consensus that it's usually detrimental.
Complexity and Cost
Requiring neutral switching adds complexity and cost to PV systems. This is a factor that code-making panels consider when weighing the potential benefits.
In Summary
The part of 690.12 you highlighted primarily aims to isolate the ungrounded conductors of the PV system from the utility grid or other DC power sources during rapid shutdown. The language is vague, but it almost never requires breaking the neutral unless specifically instructed by the manufacturer of the equipment.
Important Considerations: Always consult with the local Authority Having Jurisdiction (AHJ) for clarification on their interpretation of this code requirement. Their interpretation is the one that matters for your project.* Double-check the manufacturer's instructions for all PV system components (inverters, disconnects, etc.). They may have specific requirements regarding grounding and disconnecting.This is a complex issue, and interpretations can vary. When in doubt, err on the side of caution and consult with a qualified electrical engineer or inspector. I hope this clarifies the situation! Flag for review