User: Fordean, Location: New Jersey
Asked on: Thursday, December 26, 2024 at 9:55 am EST
Answered on: Thursday, March 6, 2025 at 6:40 am EST
Question: Not really understanding this.'IN ORDER TO REDUCE SHORT CIRCUITCURRENT, E.C. SHALL ROUTE 30 FEET OF #12AWG WIRE FOR EACH POWER AND LIGHTINGBRANCH CIRCUIT CONNECTED TO THE LCP.RUN WIRE FROM PANEL, UP TO JOIST SPACE,LOOP AND ROUTE BACK DOWN TO LCP.Any input. Where would you loop this in. It's say 120volt circuit
Okay, let's break this down. This instruction is unusual but is specifying a specific method to limit short circuit current on 120V branch circuits connected to a Load Center Panel (LCP). Here's a more clear interpretation: The Goal
Reduce the potential short-circuit current flowing through each 120V power and lighting branch circuit connected to the LCP.
The Method
Introduce additional resistance into each circuit using 30 feet of #12 AWG wire. This resistance will lower the maximum current that can flow during a short circuit.
The Installation
Start at the LCP breaker for a particular 120V circuit. Run the #12 AWG wire up into the joist space above. "Loop" the wire in the joist space (this just means coiling or routing it back and forth to achieve the necessary length). Route the wire back down to the LCP. Connect the end of the wire back to the original circuit.
Explanation and Where to Loop
The instruction doesn't specify where to loop the wire in the joist space other than it needs to reach the 30 ft distance.
Let's illustrate with a simple example
Assume you're working with a 15-amp breaker for a 120V lighting circuit.2. At the LCP
You would disconnect the existing #12 AWG wire that runs from the breaker to the lighting circuit.3.
New #12 AWG Run
Connect the new 30ft run of #12 AWG wire to the breaker.4.
Into the Joist Space
Run the 30ft wire up into the joist space.5.
Looping
In the joist space, arrange the 30 feet of wire. You don't need to make a tight coil; simply route it back and forth or in a large loop pattern to take up the length. Ensure the wire is secured and won't be damaged.6.
Back to the LCP
Bring the other end of the 30-foot wire back down to the LCP.7.
Final Connection
Connect the end of the 30-foot wire to where the original wire had been connected to the breaker.
Why This Works (Simplified Explanation)
Resistance
All wires have resistance to the flow of current. The longer the wire, the more resistance it has. #12 AWG wire has a specific resistance per foot.
Short Circuit Current Reduction
During a short circuit, the current is limited by the total resistance in the circuit. Adding 30 feet of #12 AWG wire significantly increases the resistance, which therefore reduces the maximum short circuit current.
Important Considerations
Code Compliance
This is a very unusual requirement. Make sure this method is actually permitted by the applicable electrical codes in your jurisdiction. It's important to consult with the Authority Having Jurisdiction (AHJ) to ensure compliance. It may be a project-specific design or variance from standard code.
Voltage Drop
Adding extra wire increases the overall resistance of the circuit, thus increasing voltage drop.
Overheating If you were to put too much current on a 120V, the wire would melt and could start a fire. Alternatives
Consider alternative ways to reduce short-circuit current. The use of a current limiting device may be more effective.
Safety First
De-energize the circuit before doing any wiring. Turn off the breaker and verify with a meter that the circuit is dead. Use proper wiring techniques and make sure all connections are tight and secure.
In Summary:
The instruction describes a deliberate method to reduce short-circuit current by adding resistance to each branch circuit. However, it's vital to verify this method's code compliance and carefully consider the potential drawbacks (voltage drop, heat etc). Flag for review