Mike Dolt Enterprises Logo Mike Dolt Enterprises

Topic: Protecting GEC against physical damage

User: Pwinsor, Location: Alaska

Asked on: Thursday, January 2, 2025 at 6:13 pm EST
Answered on: Thursday, March 6, 2025 at 6:53 am EST

Question: Just finished our transformer craft certification (3rd year wireman class), and we all got scored 50% on raceway. I think it's related to protecting the grounding electrode conductor. Ran it from a knockout at the bottom of the transformer with a chase nipple. The wire runs up to the wall to lugs labelled "water pipe" and "building steel". I protected the wire with schedule 80 PVC and so did everyone else in my class. Is this correct? Was i supposed to put it in PVC under the transformer as well?Thanks!

Okay, let's break down why you likely received a 50% score on the raceway portion of your transformer craft certification related to the grounding electrode conductor (GEC) protection, and what the possible issues are.

Understanding the Grounding Electrode Conductor (GEC) and its Protection

The GEC is a critical safety component of an electrical system. It's the conductor that connects your electrical system's grounded conductor (neutral) to the earth (grounding electrode). Its purpose is to provide a low-impedance path for fault current back to the source, allowing overcurrent protective devices (breakers/fuses) to trip and clear the fault quickly, minimizing the risk of electric shock and equipment damage. NEC Requirement

The NEC (National Electrical Code)
requires that GECs be adequately protected from physical damage. This is because damage to the GEC can compromise the entire grounding system and create a serious safety hazard.

Analysis of Your Installation and Potential Issues


Here's why your installation and the installations of your classmates likely resulted in a low score:1. Unprotected GEC Inside the Transformer Enclosure

This is the most probable reason for the score. While you protected the GEC
outside the transformer enclosure with Schedule 80 PVC, the portion of the GEC inside the transformer enclosure, between the knockout and where it exits the transformer, was likely unprotected.

The Problem

Inside the transformer enclosure, the GEC could be subject to:

Mechanical Damage

From vibration, tools, or other equipment during installation or maintenance.


Abrasion

From sharp edges inside the transformer enclosure.

Corrosion

Depending on the environment.


The Solution



Yes, you were likely supposed to put the GEC in a raceway (like PVC conduit, EMT, or even flexible metal conduit [FMC] with appropriate fittings) inside the transformer enclosure, from the knockout to where it exits the transformer.
You should have used a chase nipple and a short piece of PVC conduit. You should also verify that you are bonding your PVC to the transformer as well.2. Type of Raceway Used (Possible, but Less Likely)

While Schedule 80 PVC is generally a good choice for physical protection, the NEC (National Electrical Code) may have specific requirements for the type of raceway acceptable for GEC protection in your jurisdiction. This is less likely to be the sole reason for the 50% score, but it's worth checking. The main concern here would be whether a metal raceway is required as part of the fault current path.3.

Chase Nipple Installation

While using a chase nipple is generally acceptable, make sure it's properly installed and tightened. A loose chase nipple could allow the GEC to be exposed to physical damage. This is less likely than the above two issues.4.

Grounding Electrode Connections

Ensure that the connections to the "water pipe" and "building steel" are made correctly and according to NEC requirements (NEC 250.64(F)). This includes using approved connectors and ensuring a secure and reliable connection. However, this isn't raceway related, so it shouldn't impact your raceway score.

Key NEC Sections to Review (Consult the Latest Edition of the NEC)
NEC 250.64(B): Grounding Electrode Conductor Installation. This section covers the physical protection of the GEC. It specifically mentions that GECs "shall be protected from physical damage by enclosures, raceways, or otherwise, where exposed to physical damage." Article 300: Wiring Methods

This article covers general requirements for wiring methods, including raceways.

Article 352: PVC Conduit

This article covers the proper installation and use of PVC conduit.

What You Should Do Now
1. Review the NEC

Carefully review the NEC sections mentioned above to understand the specific requirements for GEC protection in your jurisdiction.2.

Consult Your Instructor

Talk to your instructor and ask for specific feedback on
why you received a 50% score on the raceway portion. They can point out the exact deficiencies in your installation.

Ask specifically if the lack of protection
inside the transformer was the primary reason.
3. Practice

Practice proper GEC installation techniques in a lab setting to reinforce your understanding.4.

Understand Local Amendments

Be aware that your local jurisdiction may have amendments to the NEC that could affect GEC protection requirements.

In Summary


The most likely reason for your low score is the lack of a raceway protecting the GEC
inside* the transformer enclosure. Make sure to protect the GEC from the knockout to the point where it exits the transformer, typically with a short length of PVC conduit secured with a chase nipple. Review the NEC and consult with your instructor to fully understand the requirements and improve your installation techniques. Good luck! Flag for review

Previous Question Next Question