User: njose424, Location: Carmel, IN
Asked on: Friday, January 3, 2025 at 3:55 pm EST
Answered on: Thursday, March 6, 2025 at 6:55 am EST
Question: Please help!?!?My furnace stopped working today and I was able to determine it was a blown fuse. I've currently got the fuse block bypassed to keep the furnace going temporarily.The blown fuse I removed is a Eagle OK 125V 20AMP Time Delay "D" fuse. I understand this is a Type T fuse because it has an Edison style screw base. Beyond that, my available options for Type T fuses at my local hardware store are a TL (medium duty) or T (heavy duty) rated fuse.What would be the appropriate replacement fuse? TL or T rated?On a side note, the electrician at work AND the facilities HVAC engineer both separately told me a local fuse is not necessary because it's on a dedicated circuit. I looked and my breakers are Square D QO type. The breaker is a 20 amp breaker.Furnace is a Lennox m/n ML180UH090P48B-55The "Electrical Rating" sticker says the max amps is 12 and the full load amps is 8.2.Here's what I extracted from the Installation Manual on this topic:"The power supply wiring must meet Class I restrictions. Protected by either a fuse or circuit breaker, select circuit protection and wire size according to unit nameplate.NOTE − Unit nameplate states maximum current draw. Maximum over−current protection allowed is 15 AMP.Holes are on both sides of the furnace cabinet to facilitate wiring.Install a separate (properly sized) disconnect switch near the furnace so that power can be turned off for servicing."Not sure if the blown fuse was appropriately rated at 20 amps or if a 15 amp fuse is appropriate. Also, wondering if I need the fuse or can just get away with the 20 amp dedicated circuit breaker but also wondering if that's appropriate for the motor rating.
Okay, let's break this down to get your furnace running safely and correctly.
Understanding the Fuse Situation1. Fuse Purpose
The fuse in your furnace is there for a reason: to protect the internal components of the furnace from overcurrent situations. The circuit breaker protects the wiring to the furnace. A problem within the furnace (like a motor issue) might not trip the breaker fast enough to prevent damage to the furnace itself.2.
Correct Amp Rating
Your Lennox furnace nameplate and manual clearly state the
maximum overcurrent protection allowed is 15 AMP. The fact that it had a 20-amp fuse installed is a problem. It's likely why it blew; it was likely enduring too high a current draw for some time before actually blowing. Using a fuse larger than specified can create a fire hazard because the internal components will overheat and potentially start a fire before the breaker trips.3. Fuse Type: Time Delay (Type T)
You are on the right track with a "Type T" fuse. These are designed to handle the brief inrush current when a motor starts up, preventing nuisance tripping. The time delay is important for motors. Your blown fuse was a "Time Delay" fuse.4.
Fuse Rating: TL vs T There's no industry standard for the "TL" or "T" terminology with fuses, but generally speaking a "T" rating is more robust with a longer time delay. Since you're dealing with a motor that has high inrush, a "T" rated fuse would be the more appropriate choice.
Recommendation: Correcting the Fuse Issue1. Replace with a 15 AMP, Type T (Time Delay) Fuse
This is the most important thing. Get a 15 amp, Type T (Heavy Duty Time Delay) fuse. This is the correct size based on your furnace documentation.2.
Electrical Code Compliant
Because your Furnace documents state that a fuse or breaker is required, it is unsafe and against code to bypass it. DO NOT operate the furnace without a properly sized fuse installed.
Addressing the Electrician/HVAC Tech Comments
While it's true you have a dedicated circuit, their statement that a local fuse isn't necessary is
incorrect and potentially dangerous based on what you've provided. The furnace manufacturer clearly requires overcurrent protection at the unit itself. The breaker protects the house wiring, not necessarily the sensitive components within the furnace. Here's why their advice is flawed: Speed of Response
A fuse is generally faster at responding to a short circuit or overcurrent condition within the furnace than a breaker is. This can prevent damage to the furnace's components.
Specific Protection
The furnace manufacturer understands the nuances of their equipment's electrical requirements. Their specification for a 15-amp fuse is based on protecting the furnace components from damage.
Code Compliance
As noted before, Furnace documents state that a fuse or breaker is required, it is unsafe and against code to bypass it.
Next Steps
Purchase a 15 AMP Type T (Heavy Duty Time Delay) Fuse
Make sure it is 125V or 250V. Your current 125V fuse is acceptable because that is above the 120V input.2.
Install the Fuse
Turn off power to the furnace at the breaker before installing the new fuse.3.
Observe
Once you install the new fuse and turn the furnace back on, monitor its operation. If the fuse blows again, it indicates a problem within the furnace that needs to be diagnosed by a qualified HVAC technician. It could be a failing motor, a short in the wiring, or another component issue. Do not just keep replacing the fuse with the same size or, especially, a larger size.
Important Safety Notes
Never bypass a fuse permanently. This is a fire hazard. If the fuse blows repeatedly, call a qualified HVAC technician. There is an underlying problem that needs to be addressed. If you are not comfortable working with electricity, consult a qualified electrician or HVAC technician.
In summary, get the right fuse (15 AMP, Type T), install it, and monitor the furnace. If the fuse blows again, call a professional. Good luck! Flag for review