Topic: NEC 705.12(B)(3)(3) add loads and sources separately?

User: ryangittens, Location: usa

Asked on: Wednesday, January 8, 2025 at 1:10 pm EST
Answered on: Thursday, March 6, 2025 at 7:03 am EST

Question: The way this code section reads sounds like they want the loads and the sources to be added together?It would make more sense to me that if you add all the loads and you add all the soruces (excl. the main) separately and both add up to less than the bus bar rating the bus bar is still protected. For example a 200A panel with 200A worth of supply (excl. the main) and 200A worth of loads would be okay.If we have a single 50A solar breaker connected to a 200A meter main combo with no other supply breakers and one 200A on the feedthrough conductors, is this compliant per this code section? If not, what code section applies here?

You're right, the wording in many codes related to backfed breakers and busbar ratings can be confusing. Let's break down the concepts and address your specific example.

Understanding the General Principle

The core concern is preventing the busbar from being overloaded. Overloading creates excessive heat, which can damage the busbar insulation, potentially leading to short circuits and fires. The rules aim to ensure that the total current flowing through any part of the busbar never exceeds its rating.

Why It's Not Just Loads + Sources < Busbar Rating (Sometimes)

The simple "Loads + Sources < Busbar Rating" rule only works if the main breaker protects the entire busbar from both the loads and the sources. Think of the busbar as a highway. The main breaker acts as a gatekeeper. If the main breaker is sized properly, it can prevent too much "traffic" (current) from entering the busbar, regardless of whether that traffic is coming from loads or sources.However, when you have sources backfeeding onto the busbar without the main breaker providing that total protection, you need more stringent calculations. The concern is that current from the backfed source could add to the current from the loads between the main breaker and the backfed breaker, potentially exceeding the busbar rating in that section.

Your Example: 50A Solar Breaker on a 200A Meter Main Combo

Let's analyze your scenario with a 200A meter main combo, a 50A solar breaker, and a 200A feedthrough breaker. The key is where the solar breaker connects. I'm going to assume the 50A breaker connects to the bus bar within the meter main combo.The general rule being enforced by the code you're probably looking at comes from NEC 705.12(D). This section addresses backfed breakers in panelboards.

NEC 705.12(D)(2)(3) [for a 200A main breaker]> Supply connections shall be permitted at any location on the supply side of the main overcurrent device or on the load side of the main overcurrent device where the sum of all sources supplying the busbar section does not exceed the ampacity of the busbar. Where two sources of power are located on the same busbar section, the sum of the overcurrent devices supplying the busbar shall not exceed 120% of the rating of the busbar.Applying the NEC to Your Scenario


Busbar Rating

200A (given in your example)2.

Main Breaker

200A3.

Backfed Breaker (Solar)

50A4.

Applying the 120% Rule

The sum of all breakers supplying the bus bar (main and backfed) must not exceed 120% of the busbar rating. 200A (main) + 50A (solar) = 250A 120% of 200A (busbar) = 240A 250A > 240A

Therefore, in
most interpretations, your configuration is NOT compliant based on the 120% rule.
Important Considerations and Caveats



Listing and Labeling

Some meter main combos are specifically designed and listed for backfeeding with a higher allowable percentage. Always check the equipment's listing information and labeling. The manufacturer's instructions always take precedence, as they have been tested and certified. If the meter main specifically says it can accept, say, a 70A backfed breaker, follow that.

Load Calculation is Required

You still need to perform a load calculation to ensure that the total connected load on the panel,
before considering the solar, doesn't exceed the busbar rating. The solar simply offsets the loads; it doesn't increase the panel's capacity.

Feedthrough Breaker Location

If the 200A feedthrough breaker is ahead of the backfed breaker, it may affect the interpretation, but in general, the 120% rule will still likely apply.*

Interpreting "Bus Bar Section"

Sometimes there is ambiguity when talking about a "busbar section". If the 50A backfed breaker is physically separated from the busbar section that the 200A main breaker connects to (usually meaning a separate lug from the main breaker), then it's possible to calculate the capacity requirements separately for that section.

To be absolutely certain


Consult the equipment manufacturer's documentation.
The meter main combo should have instructions regarding backfeeding.2. Discuss your specific design with your local electrical inspector. They are the final authority on code compliance in your jurisdiction.3. Engage a qualified electrical engineer. They can perform a detailed analysis to ensure compliance and safety.

In summary, while the idea of sources offsetting loads is valid, the NEC imposes stricter limitations on backfed breakers to ensure busbar safety. The 120% rule is the common sticking point. Flag for review